Help i just crash my carrier comfort zone control. it was

Customer Question
working fine till then....
help i just crash my carrier comfort zone control. it was working fine till then.
Submitted: 2 years ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 1 minute by:
8/30/2015
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 15,834
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello, thanks for using this service I will be assisting you today. When you respond to me sometimes it may take me a bit to respond back as I am researching your issue and it takes time to type so please be patient.

When you say it crashed what has happened exactly?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
can you call my cell xxxxxxxxxx
Customer reply replied 2 years ago
system was working till i played with the sensors and now no fan or cool. had a hf 41 failure.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Ok that is a ZONE 2 temp sensor error, the sensor is reading shorted or open. You need to check the sensor and the wiring to the sensor you may have knocked something loos or created a bad connection to the controller. Check that and hopefully the sensor is still fine it may just be a loose connection.

We are on the honor system for our time, all I ask is please use the star rating link on your page to rate my service. This will allow you to get directly back to me for FREE followup questions anytime and tips are greatly appreciated thank you!

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Nothing was open to short just the control on wall. and the code is a dx cool
Customer reply replied 2 years ago
coil
Customer reply replied 2 years ago
but it still was working
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

So what code do you have on it now?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
hf 41 and i have no dx coil sensor
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Do you have a volt meter?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i have 10v to panel as well as 24 volts to stat
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

OK and it is saying DX coil sensor? Also can you shut the power off to the system for 1 full minute...maybe you just need to reboot it.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have gon e thru all factory setting and i must be missing something I did that too thanks
Customer reply replied 2 years ago
I think it has something to do with 1-9 on control
Customer reply replied 2 years ago
also 2 zone downstairs has fs o7 that is zone 2 ducting sensor but it has work like that for years.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

What were you exactly doing when all this started?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
1-9 on the control s and t also Help;
Customer reply replied 2 years ago
trying to find out what code it was
Customer reply replied 2 years ago
No thanks
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Ok no problem, I fully understand thanks for trying this service

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I just got a call from my bank one of 37.00 is ok but not the 18.00 one. Please cancel my service. Tom
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 15,834
15,834 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier furnace from the 80s. In which the blower
in which the blower won't turn off. but the heat does turn on/off depending on the thermostat control … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier Programmable Thermostat and the AC keeps
I have a Carrier Programmable Thermostat and the AC keeps running. Can I reset it somehow or could there be another problem? … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,834 satisfied customers
We just had a new carrier package unit installed on the roof
We just had a new carrier package unit installed on the roof of our townhome. Model 50VLC3630TP. The unit remove was a carrier 50GX036301. The new unit works great but there is a very noticeable low f… read more
hvacdave84
hvacdave84
53 satisfied customers
Question for you regarding wiring a carrier infinity with a
Question for you regarding wiring a carrier infinity with a Honeywell lyric. I have a gas furnace and an AC condenser. Today the terminal with the abcd wires connected in the furnace has 2 sets of wir… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier 58MCA080 gas furnace with continuing
I have a Carrier 58MCA080 gas furnace with continuing issues. Need some help diagnosing current problem.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to identify thermostat wires from an old Carrier
Trying to identify thermostat wires from an old Carrier Comfort Zone to review options for upgrading the thermostat. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I live in a rental home with a Carrier system Model
I live in a rental home with a Carrier system Model CD5BXA030000AAA, serial #1896X41060. I have A LOT of questions; however, right now, I'd like to know why I am seeing a steady RED light through the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have carrier c48175d. changed thermostat to honeywell.
i have carrier c48175d. changed thermostat to honeywell. carrier shows green to A yellow to B white to C and red to D. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just moved into a house and it has the infinity carrier
I just moved into a house and it has the infinity carrier thermostat but no matter how many times I tape on it-it doesn't power up for me to set the temperature … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Just bought a Nest, but it's incompatible with my Carrier
Hi Hi. Just bought a Nest, but it's incompatible with my Carrier Infinity system. what to do? Rewire? Or find a different thermostat? If so, which one? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH NEEDS TO BE REPLACED. DO YOU RECOMMEMD A ONLINE PART. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Have a Carrier FB4CNF042 electric furnace, the blower will
Have a Carrier FB4CNF042 electric furnace, the blower will run but the elements will not heat up. The blower motor is a Genteq. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Is there a battery on my carrier infinity thermostat? The
Is there a battery on my carrier infinity thermostat? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Carrier TP-PRH01-A programmable thermostat but it
I have a Carrier TP-PRH01-A programmable thermostat but it is not WiFi capable. I would like to replace it with a Honeywell WiFi programmable thermostat. Can you tell me which model(s) you would recom… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Transformer (90-T40F3) replacement on a Carrier HVAC. 120VAC
Transformer (90-T40F3) replacement on a Carrier HVAC. 120VAC input White to common Black to power (208-240 capped) Secondary 24V blue/yellow. From the units circuit board connection "C" is brown and c… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to see what my options are to replace a carrier
Trying to see what my options are to replace a carrier infinity stat that is out of warranty and not functioning properly. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x