I have a Goodman Mini Split ductless system. It runs minutes

Customer Question
I have a Goodman Mini...
I have a Goodman Mini Split ductless system. It runs for 25 minutes producing 60 degree air and then shuts dow with the LED flashing in 7 flash bursts. Any ideas?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 hours by:
8/15/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, tell me please about how old the system is, and if you have every cleaned the condenser coil on the unit outside or not.

We can go from there.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The system was installed last fall.The system has never functioned. It is at a cottage closed for the winter.The condenser and evaporator coils are brand new and shiny clean. The outside unit is located below a deck with all recommended clearances in place.The lines are both insulated. 15' as supplied with pre-charged system. They were vacuum evacuated three time before the charge was released.There was an initial issue with the amount of power being delivered. The power company was delivering 248 volts and the unit specifies 208-230 volts.A transformer was custom made to reduce the 248 volts to 224 volts and installed. It made no difference.After six 30 minute runs to auto shutdown the unit now runs for about an hour and a half to autoshutdown.Whether through the transformer or not when the unit shuts down it emits a status code of (7) led flashes when it auto shuts down. Can't find status code index.Unit is GOODMAN MSC183E15MC (Outdoor unit) with MSC183E15AX (Indoor Unit) wall mounted.Temperature differential while operating 20 degrees F. ie 80 degrees ambient with 60 degree airflow (but not really cold).The high pressure line and the low pressure lines at the outside unit fittings are equal temperature and are cool. (ie: not much cooling going on because no heat being returned to condenser unit outside to be dissipated).The outside unit runs when the inside unit is on.Doesn't sound like compressor is engaging but I have another of these units and it is also quiet and you don't hear the compressor over the fan and it works just perfectly.(also a cottage installation).
Customer reply replied 2 years ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call. Let me know if you need more information, or send me the service offer(s) so we can proceed.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again, If you can attach a few photo's of the unit situated under the deck taken from about 20 feet away that will help me sort this out for you.
I will submit an additional services offer for a phone call that you may accept or not, if not, we can continue here after I get the photo's.
Use the 'attach files' link at the bottom left corner of your reply box for that.
We can go from there.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I am three hours away from the place right now and it must be reached by boat. I was there yesterday.I do not have photos of the installed unit under the deck but here is the description:Location:
Customer reply replied 2 years ago
Location: Under 2 X 6 deck
Clearance over unit 18"
Clearance end of unit with electrical and lines to cottage 30"
Clearance front and rear of coils for air flow 20' (unlimited airflow)
likewise opposite closed end away from power and lines
unit is located level on stone foundation screwed down with TApCon screws and fender washers
wiring is outside tech cable and waterproof electrical fittings.lines insulated with foam insulation supplied with unit and wrapped with weatherproof tape supplied with unit for wrapping the lines.
lines run inside an insulated wall behind dry wall to inside unit.No water (dehumidification) is being produced while the unit runs (when it runs 1 1/2 hours to auto shutdown) in 80% relative humidity conditions at 85 degrees F outside (and inside) produces a gentle cooler air.20 Amp tandem breaker on 120/240 V Edison panelI was told that if L1 and L2 were reversed between the outside and the inside that the unit would shut down after a period with a two flash status code so I switched L1 and L2 between the inside (L1/L2/S/G) and the outside. Two flash status code now (7) flash status code.I would be happy to do the live voice thing but first I want to hear what the (7) flash status code means.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again, Goodman is not listing the flash codes for that model, a good sign that it is Chinese made and short on paper work.
http://mobile.goodmanmfg.com/mobileapp/faultcodes/
So far I have not found it on line elsewhere.
There might be a code list printed on the outside units wiring diagram or on a sticker next to it.
There are hundreds of thousands of these ductless AC systems imported annually, from 6 or 8 different chinese manufacturers, and with all of them making changes and with different models frequently.
The chances of any one of us here having seen that particular model are in the range of one in ten thousand, or something like that.
Meantime if you like we can continue without the flash code, and look for an installation error.
Your description of the under deck installation indicates that it is getting plenty of air flow.
The next suspect is that it is over charged with refrigerant...or undercharged with refrigerant possibly due to a refrigerant leak.
An over charge of refrigerant will cause the unit to run hot, and trip the compressors heat sensitive overload... it will reset itself once the compressor cools off.
Chances of that being an accurate assessment are in the 70% range, I would need to know the low side and high side pressures to know if that is accurate or not.
The key indicator of an over charged system is demonstrated incompetence by the installer... those will say 'it has the proper charge in it'.
A competent technician will not say that... he will say 'the suction pressure is 107 psig with the room at 75F, and the compressor fully loaded, and the head pressure is 397 psig with the outside air at 102F, system uses R 410a refrigerant"
This is regardless that these systems come pre-charged with refrigerant.
That is the only correct way of describing the refrigerant charge (my numbers here are arbitrary to demonstrate the point).
Call the installer on the phone and ask 'how the system was charged'
That will tell us a lot about might be going on.
We can go from there.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Obviously I will have to go there and get some measurements taken I will get back to you then.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
That will work.
You need to be alert to errors many inexperienced techs make... these will give you the pressures you ask for but *without* the inside and outside air temperatures at the same instant.
That is because they do not realize that in these systems temperature and pressure are in absolute lock step... when the compressor is running fully loaded.
That brings up the second issue, on these variable speed systems they will give you the temperatures and pressures correctly... but with the compressor not fully loaded... that amounts to useless information.
These techs will not know how to get the compressor to its fully loaded condition.. they will assume it is fully loaded, and give you temperatures and pressures without knowing if the compressor is fully loaded or not.
To get the compressor to its fully loaded condition it has to be over 80F outside, and temperature control has be set at least 3 degrees F cooler than the room temperature read out.
------------
These will charge a system so that it looks good them at a partial load situation, and in fact it IS good under partial load... but then when the weather warms up, the compressor goes to full speed and if the system is over charged for that situation you will get the high temperature safety cut out situation.
Installing these systems is best done by long experienced specialist in these systems... if the seller is not sufficiently experienced with this equipment... that will be the root of the problem.
Talk to the technician while he does these tests, if he is familiar with all these factors he will discuss then easily and at length with you... if not he will be brief and say "I am charging it to factory specifications".
Watch for that. Let me know which direction you are from the center of the nearest city if you need me to locate a specialist in these inverter driven ductless systems.
We can go from there.
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
78 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Evaporator water flow too low alarm keeps happening.
Evaporator water flow too low alarm keeps happening. Recently cleaned coils now this. The pumps are running fine. The pressures are good on the approach. The water strainer is clean. What is this a ca… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I have a furnace with an evaporator pump that i had to
I have a furnace with an evaporator pump that i had to repace all the relays and also the thermostat. After all is done it worked great for the winter except in order for it to work i had to put the t… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x