My inside blower will not turn off. only if i t emergency

Customer Question
my inside blower will not...
my inside blower will not turn off. only if i hit emergency turn off switch. but also my condenser fan is not working
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call. Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 44 minutes by:
8/4/2015
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,516
Experience: Furnace, A/C and heat pump specialist.
Verified
Hello. My name is ***** ***** I'll do my best to help. Let's get started and see what we can do.You may have more than one issue,but lets start with thermostat. Disconnect all wires from thermostat and tell me if blower goes off.Next let me know if you have a volt meter for troubleshooting.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
i'm not home at this time. am at work.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
If you have internet access at home, we can do some step by step troubleshooting when you are on site.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok. but i paid 45 dollars already. and i thought i was to get a answer to my ?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
You are correct.The initial payment is all you will have to pay as long as we work here on the website by typing back and forth.WE can work on this with no time limit until we get the problem solved.
The only additional fees that will come into play is if you choose the phone call "additional service" where I dedicate my time soley to you on the phone.WE can continue working here as long as it takes with no additional fees .If at any time you decide you would rather work by phone, then you can accept the additional service offer. Some people just prefer not to have to do all the typing back and forth.
Lets start when you get home by removing wires from thermostat and see if blower stops. Then we will go to next step.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok
Customer reply replied 2 years ago
it will not be after 4 pm
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
No problem just come back to question when ready and we will go from here.
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
6,022 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,022 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My condenser trap on my Potterton Combi Promax is full i
Hi Pearl my condenser trap on my Potterton Combi Promax is full i have just discovered this is the reason why i had a pool of water on my worktop , how can i deal with this please … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
77 satisfied customers
I changed the condensation pump on my gas furnace and now
I changed the condensation pump on my gas furnace and now the furnace won't start. The old pump was direct wired through the kill switch and the new one had a plug. The new one also had a yellow wire … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My 5 ton condenser unit located on a concrete slab outside
My 5 ton condenser unit located on a concrete slab outside my house was damaged in the Hurricane Harvey flood. It looks like I need a new condensing unit. I just received a quote of $4,000 for a new 4… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
MONROVIA CA AND I NEED THE CONDENSER FAN AND THE FAN MOTOR
I'M IN MONROVIA CA AND I NEED THE CONDENSER FAN AND THE FAN MOTOR FOR THIS MODEL. NAC048AKC3 … read more
airheatman
airheatman
HVAC Technician
8,516 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
I have an Ultra 105 Series 3. Condensation appears on the
Condensation appears on the inside at the top and by the exhaust. It then drips down and fills the bottom of the unit. Is an exhaust leak? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What is the best way to channel off the condensation water
What is the best way to channel off the condensation water on outside heat pump? When it is heating a lot of water is accumulating. Our lowest temp has only been 54 degrees outside so shouldn't be ove… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser fan running compressor not running or humming.
Condenser fan running compressor not running or humming. Checked capacitor it's good. Checked contact it's also good. Pills in by its self and has just over 240. Could it possibly be something in the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
airheatman
airheatman
HVAC Technician
8,516 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
The inside fan is not running, condenser will run, 3 days,
the inside fan is not running, condenser will run, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My refrigerador compressor is running so is the condenser
My refrigerador compressor is running so is the condenser and evaporator fan and all the lights but it wont cool at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,082 satisfied customers
C wire problem. A day. Condenser not turning on with
Condenser not turning on with additional wire to c terminal on fan unit … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I'm in the process of installing a Goodman 2 ton condenser
Good morning! I'm in the process of installing a Goodman 2 ton condenser (GSX140241) however I have a few questions. 1. On the name plate it states that this unit requires 15 amps. Should I connect th… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,082 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x