Trane Heat Pump M/N XP19-048-230-05, S/N 5808B28331. Unit runs

Customer Question
fine, when running. It will...
Trane Heat Pump M/N XP19-048-230-05, S/N 5808B28331. Unit runs fine, when running. It will run and bring home down to set cooling temp. Unit appears to run for too long a time before cycling off. Then, when it kicks off, it will not restart on it's own. I pulled the condenser panel and found the motherboard red and green LED's flashing on and off together. I cannot find the code to diagnose.
At first, I suspected the contactor, so I manually pressed the contactor bar to activate unit. Compressor kicked on, so I released the contactor, compressor kicked off. I shut off power to unit, waited a bit, then powered back on. After about 3 minutes, unit comes back on, and cools as normal.
Is this a welded contactor or something else?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
7/21/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Hello,Tell me please about how hot outside it is when this happens as a rule... for instance, only on very hot days for example. Tell me how old the outside unit is, and if you have cleaned the condenser coil or not.We can go from there.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Typical Florida weather, averaging high 70's at night and getting to approximately 91-95 or so during the day. Unit appears to cool fine, but seems to run constantly during night and early morning. Seems to stop around 11 am or so. This just started about 4 days ago, so no difference in weather pattern other than stated here. We also have rain off and on most days.Unit was new about 8 years ago. I have not cleaned the condenser coils.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again, thanks for the data. So far it sounds like the system may have developed a slow refrigerant leak, and is going off on its low pressure cut out switch occasionally and that you are resetting it by cycling the thermostat on and off. The fact that it seems to be running longer than it should supports that. It is also possible that unit is going off on its high pressure safety cut out switch.... clean the condenser coil and let me know how it goes from there, You can buy 2 or 3 cans of the spray foam cleaner at Home Depot or Lowes or any larger hardware store. https://www.youtube.com/watch?v=vDtT6hSpV4sWe can go from there.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Okay, will do with the coil cleaning. And with my limited knowledge base on a/c systems, I was thinking refrigerant may be the cause of unit running so much. I will tell you, this is about 3200 heated area home, that had some lack of maintenance over the last recent years during a divorce. I have been here only 2 years, trying to bring it up, but with 20 acres and all, I'm stretched pretty thin, physically and financially. So much for retirement! Anyway, I see all kinds of 'problems' including air leaks from bad door astragals. I have not been in the attic to check insulation or ductwork/leaks. And, there is a second separate a/c for the master bedroom/bath area that is currently out of order. Overall, I know all of these situations are overworking this one unit and wearing it down prematurely. In the winter, it doesn't bring it up much over about 69-70, and just runs and runs and runs.I just thought it fair to give a complete overview on what's going on here. But, aside from this problem that I originally addressed with you, the unit has been cooling and running okay.I won't be able to check/clean the coils until Wednesday, so I'll get back to you with an update once I complete that task.Thanks so much for your input so far.John
Customer reply replied 2 years ago
P.S. I guess it could be a combination of low refrigerant activating the low pressure cut out switch, AND the high pressure cut out switch due to dirty coils/can't breath/overheat?? Or not? Is it typically just one or the other?
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again, there are dozens of possibilities, but a refrigerant leak is entirely common, and the condenser after 8 years is in serious need of cleaning. so we will look at those two first. On the 20 acres issue, you could sell all that ahead of our nations next financial fiasco and live in a country at a quarter to an eighth the cost, and plenty of free time. I am on Lago Atitlan right now. very nice. http://screencast.com/t/BYv5hhVINo heat or AC required its at 5,000 ft in the tropics, about 65 to 75F 98% of the time.Home repairs are $1 an hour.
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Condenser contractor chattering is it bad? Just notice
We had very cold weather down to 10 degrees, fan not been running until today thouzght was running's. On heat strips. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rental hot water tank - serviced and insulated pipes Oct
rental hot water tank - serviced and insulated pipes Oct 2017 by Reliance tech-ice build up at elbows on insulated outside plastic pipe - when fan comes on -can hear running water outside from inside … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,417 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x