I have a 1710a model. After it runs I get 4 red

Customer Question
I have a 1710a model...
I have a 1710a model. After it runs for awhile I get 4 red light blinks error code. I have 300 high pressure side and zero on auction side. What is going on with this?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 29 minutes by:
7/18/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Hello, This should be the service manual for it. I will post it here for future reference.ftp://ftp.aprilaire.com/Fulfillment/Dehumidifiers/Aprilaire_Model_1710A_1750A_1770A_Dehumidifier_Technical_Manual.pdf Tell me please if the high pressure side maintains 300 psig, and if the suction side never goes above zero or not. We can go from there without any time limits. .
Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
http://screencast.com/t/3WyXjC4hSo far, that looks like the most suspect component. Locate its connection on the board and unplug one of the connections to it and let me know what happens. Next, locate its sensing element on the cooling coiling coil, remove it and hold it in your hand as you run the system, let me know what happens. We can go from there.
Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Tell me please if the suction line that comes back from the cooling coil to the compressor is cool, cold or frosty where it attaches at the compressor.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Pressure doesn't change and after it hits the error code it stops running. The 2 small linesctgar go to the txv valve freeze up. The auction line itself us not cool.
Customer reply replied 2 years ago
When I unplug one of the lines you asked about, the unit shurs down and I get 6 red flashes for werror code.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Thanks,
Tell me please if this system uses R-410a, or some other refrigerant and if you have added any refrigerant to the system or not, and if so what type.
If the two small tubes between the TXV and the cooling coil are frosted, then the TXV may be blocked with a tiny ball of ice *inside* the valve at the orifice... or there may be a refrigerant leak in the system.
I need to know how warm the room is surrounding the dehumidifier, and if you have cleaned its condenser coil or not.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
This is a 410 system. I have tried adding refrigerant and then took it back out when the pressure increased on high side and no change on low side. Only put 8 oz in. The room temp is about 74 with lots of humidity. This unit does this after it has sat for days. No chance of ice in txv. I got this unit uses so I have no idea if it has been worked on before.
Customer reply replied 2 years ago
Coil is clean as well
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again, just in case, make sure that *both sides if the coil are clean... sometimes the dirty side of the coil is not visible. 8 ounce is a lot of refrigerant for that unit, it most likely holds less than 2 or 3 pounds, the amount is not listed in their specs, but the law requires that it be on the model number name plate.. can you tell me what that reads? If there is moisture in the system, and the system is warm as if sitting for days or weeks, ice will still form in the TXV within minutes... if there is moisture in the system... in this case the chances of that are in the 30% range, not 100% however. If it has been worked on before, and someone put R-22 in it, that will cause the POE oil used in R410a units to clot in some cases, and that will block the refrigerant flow at the TXV. Locate the sensing element attached to the power head on the valve, remove it and hold it in your hand until it is warm, tell me if that lets the suction pressure rise or not.... if not replace the TXV.... if it does allow the suction pressure to rise, look for a nut on the back end of the valve that you can remove to reveal the superheat adjustment and turn it counter clockwise a turn or two and tell me if that runs the suction pressure up or not. We can go from there.
Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
If you are in doubt about there being a super heat adjustment on the valve, use the paper clip icon above to send me a picture of it.
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
6,022 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,022 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My condenser trap on my Potterton Combi Promax is full i
Hi Pearl my condenser trap on my Potterton Combi Promax is full i have just discovered this is the reason why i had a pool of water on my worktop , how can i deal with this please … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
73 satisfied customers
My 5 ton condenser unit located on a concrete slab outside
My 5 ton condenser unit located on a concrete slab outside my house was damaged in the Hurricane Harvey flood. It looks like I need a new condensing unit. I just received a quote of $4,000 for a new 4… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What is the best way to channel off the condensation water
What is the best way to channel off the condensation water on outside heat pump? When it is heating a lot of water is accumulating. Our lowest temp has only been 54 degrees outside so shouldn't be ove… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser fan running compressor not running or humming.
Condenser fan running compressor not running or humming. Checked capacitor it's good. Checked contact it's also good. Pills in by its self and has just over 240. Could it possibly be something in the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
The inside fan is not running, condenser will run, 3 days,
the inside fan is not running, condenser will run, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
C wire problem. A day. Condenser not turning on with
Condenser not turning on with additional wire to c terminal on fan unit … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I'm in the process of installing a Goodman 2 ton condenser
Good morning! I'm in the process of installing a Goodman 2 ton condenser (GSX140241) however I have a few questions. 1. On the name plate it states that this unit requires 15 amps. Should I connect th… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
Installed a Goodman 410a condenser on a r22 evap. Coil do i
Installed a Goodman 410a condenser on a r22 evap. Coil do i just change out the piston on txv valve. (57) … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Need a new condenser motor and capasitor for a goodman
need a new condenser motor and capasitor for a goodman cple36-1c and the charge amount of R22 … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.