HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC

GPH1448H41 goodman 4 ton heatpump package compressor/fan not

Customer Question
engaging, 240v at contactor input reading...
GPH1448H41 goodman 4 ton heatpump package compressor/fan not engaging, 240v at contactor input
reading 120v on each leg of contactor output but 0v nothing, natta zip whenvoltage is read across the two output terminals
contacts quite black
coil is not engaging when thermostat engaged
reading 240vac at coil
transformer 240vac input read across common and 240 terminal
24v output is reading 240vac across the 2 output terminals
blower fan is cutting on and blowing air through ducts but only hot air
Bad contactor, bad transformer or both, had plans on pulling output wires off of transformer but lost day light
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 years ago
capacitor tested good but slightly out of tolerance so change with newwhen you engage coil manually compressor and fan comes on
Answered in 33 minutes by:
7/10/2015
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Hi I'm Brian and I'm here to help! First, can you please clarify the following sentence?:"24v output is reading 240vac across the 2 output terminals" Are you actually reading 240 volts (and not possibly 24.0) between the two 24 volt terminals on the LOAD side of the transformer? There should be Red wire(s) on one terminal and Blue wire(s) on the other. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
240 volts on the input and output of the transformer....cant verify colors right now but has not been worked on until now
tested across com/240 on the top of the transformer and across the 24volt outputs on bottom.....also seeing 240 at coil
on contactor.
Customer reply replied 2 years ago
should be as it shipped from factory except the change out today of cap.....
Customer reply replied 2 years ago
if I checked each line to ground which I know is not accurate testing
I got readings of approx. 120 on each output terminal and was no decimal
had on 200 v ac setting on meter and overloaded and had to switch to 500.....
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Thanks, ***** ***** the diagram I would have to suspect the transformer did a total meltdown internally. That's a very odd and rare failure though. I just can't see where anything else on the low voltage side could net you 240 on the transformer's (or contactor coil's) 24 volt terminals. An easy way to tell would be to disconnect the load leads and ohm them out to the line leads. There should be infinite resistance between the line and load windings (between any line terminal and any load terminal). Under normal circumstances if the transformer was moist you may get a low megohm reading but that should be it. I'm shocked that the line voltage is passing all the way through to the coil on the compressor contactor! I would not put power back to that machine until the high on low voltage issue is figured out! I'd look very carefully at all the wiring in the unit to make sure nothing has melted somewhere else causing this. If it does turn out to be the transformer, I would be very surprised if there wasn't something else burnt in the low voltage circuit! I can almost guarantee the compressor contactor is also burnt! You can check that with a resistance test across the coil terminals (with one coil connection disconnected), I bet it shows OL (open). I'd be very surprised if the defrost control board isn't burnt as well. Let me know what you get for the resistance reading from line to load terminals on the transformer and we can go from here. Thanks, -Brian
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
6,022 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,022 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a jotul wood stove. f55. I want to know what are the
hi, I have a jotul wood stove. f55. I want to know what are the ideal temperatures to run it at and how to measure that. I have received many answers. … read more
eauto
eauto
self employed
High School or GED
74 satisfied customers
I have a Rheem Model No. R92PA0601317MSA. There is a
I have a Rheem Model No. R92PA0601317MSA. There is a Diversitech Condensate Pump attached. The old thermostat did not seem to be working, so we had a new one installed. It is a Honeywell RTH111. With … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
My system does not maintain heat when running shower but
my system does not maintain heat when running shower but does when heating house … read more
eauto
eauto
self employed
High School or GED
74 satisfied customers
Flashing light on Beckett oil furnace. The pump was seized,
Flashing light on Beckett oil furnace JA: Did you check the furnace's filters? Customer: Yes JA: Do you plan on doing the work yourself? Customer: The pump was seized , I installed a new one JA: Anyth… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
My thermostat screen shows vertical bands and is unreadable.
my thermostat screen shows vertical bands and is unreadable. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am having trouble. The flint glows and then click.....the
I am having trouble. The flint glows and then click.....the gas does not light. We replaced the upshot burner tubes. Everything worked when I turned it on and now...it just clicks. No fire… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Had no heat in some rooms 4 zones could here air in lines.
Hi had no heat in some rooms 4 zones could here air in lines. Dnc don't no crap. I went on u tube to bleed lines. Had pressure no pressure now. And boiler won't light. I read that sometimes they have … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I installed HRV in my home. What do i need to have the unit
I installed HRV in my home. What do i need to have the unit balanced? do i need to turn the fan on 24/7? what level of humidity should i set it up, so far i have it on 30% and its still blinking meani… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have blinking F2 error and Fault signal. 5 years old no
I have blinking F2 error and Fault signal JA: How old is the appliance? Have you gotten error messages before? Customer: 5 years old no did not JA: Do you plan on doing the work yourself? Customer: it… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
My furnace is not coming on. The external air filters. Yes.
Can I send you a model number or name of my furnace… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Rick, The thermostat terminals on the ZVC404 Zone Valve
Hi Rick,The thermostat terminals on the ZVC404 Zone Valve Control are marked as 24 VAC. Does this mean that when the terminals on the thermostat are closed, the circuit is completed and energized with… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have Weil-MclAIN GOLD CGA GAS BOILER....AND FLAME LIGHT IS
HI.I have Weil-MclAIN GOLD CGA GAS BOILER....AND FLAME LIGHT IS BLINKING. WHAT THAT MEAN ? HOW THAT FIX ? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Gibson split system a/c model js3bd-030k, condenser
I have a Gibson split system a/c model js3bd-030k, condenser fan not working replaced cap same problem label on motor faded, is there a parts list available, thanks… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I was just turning my thermostat down and it keeps showing a
I was just turning my thermostat down and it keeps showing a lock on it and won't move any of the numbers. It shows room temperature 23?? There are only 3 things on it, arrow up menu and arrow down. I… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 13 month 0ld 58cva110-122 with infinity thermostat
I have a 13 month 0ld 58cva110-122 with infinity thermostat that shows a temperature that is actually 6 degrees warmer as measured by an adjacen t thermometer.how do we adjust the thermostat to read 6… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our home is heated and ac by a 2009 friedrich ptac and it is
our home is heated and ac by a 2009 friedrich ptac and it is acting up somewhat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
Error code 59. Its 3 years old, just bought the home. Moved
its 3 years old, just bought the home. Moved family in yesterday, thermostat stopped working because it was hooked to wifi. Turned that setting off on the stat, but no hot air coming from furnace now … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The heater will burn from 20 min to sometimes up to 2 hours
The heater will burn from 20 min to sometimes up to 2 hours then it goes out to very thing has be cleaned on it twice … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question