Hooking up a 10458 condensor fan motor to older condensor. Got a 7.5 cap. New motor has 2 brown one yellow and one black. Old motor just has black, yellow and brown. How to hook up wires?
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
7/7/2015
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,150
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
do you have a new capacitor?
Are you using a cap with 3 sets of terminals on top...or 2 sets of terminals on top?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
I have a new cap with 2 terminals on top 7.5 for new motor. Compressor will run off old cap
Customer reply replied 3 years ago
Old cap has 3 terminals
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
thank you...the 2 browns go to new cap..one on each side...no other wires to cap except the 2 browns.
Then the yellow and black go straight to contactor..one on each side.
Follow so far?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
So the yellow goes to the ground side on the power and the black goes to the black " hot power side?
Customer reply replied 3 years ago
Is that what you are calling the contractor?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
not ground..
at your contactor...there are 2 sides....2 hot legs come in one end...and then go out other end.
Are you familiar with the contactor?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
No
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
ok...do you see where main power comes into the ac unit from the house?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Yes and sorry, have to think 220v yes the 2 hots come to the bottom from house
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
great...now those 2 hots end up connecting to relay/contactor...do you see that?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Yes then have terminals on top. That's where I connect the yellow and black?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
correct...you should see black wires mainly one side...and red or yellow on the other.
So black to one side and yellow to other...can you try this now?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Can do. Thanks.
Customer reply replied 3 years ago
Gonna take me a few, didn't want to remove old motor until I had clear direction!!
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
I will stand by for result>
Billy
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Works great!! Thank you!
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
Excellent...just rate service and I will move from active list.
Thank you!
Billy
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,150
23,150 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I just replaced the fan condenser motor and capacitor and
I just replaced the fan condenser motor and capacitor and now the motor shuts off after an hour. It's very hot. It appears that the system works for awhile… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I replaced my heat pump condensor fan motore with a new Mars
I replaced my heat pump condensor fan motore with a new Mars # ***** The old fan had 3 wires ,Black to the circuit board orange to the common of my cap and blue to the fan term of the cap .also a red … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I replaced the OEM condenser fan motor with a 4 wire
I replaced the OEM condenser fan motor with a 4 wire universal motor. The unit will run for 30min and the fan will stop, but the compressor is still running Modle # ***** plus MIA 42-13. I replace the… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,150 satisfied customers
where does the yellow wire from outdoor fan motor connect to?
where does the yellow wire from outdoor fan motor connect to? Does it connect to the capacitor (C terminal) same as yellow wire going to relay/bridge?… read more
spivco
spivco
153 satisfied customers
i just replaced condensor fan motor they gave me new run capacitor
i just replaced condensor fan motor they gave me new run capacitor rotom oval 7.5 mfd dual 370/440 v the new motor has two small guage leads instead of one on original motor that ran to old capacitor … read more
spivco
spivco
153 satisfied customers
REEPLACED FAN MOTOR WITH NEW ONE BUT THE WIRES R DIFFERENT
REEPLACED FAN MOTOR WITH NEW ONE BUT THE WIRES R DIFFERENT COLORS. NEW MOTOR BLACK RED YELLOW BROWN BROWN/WHITE OLD MOTOR BLACK RED BROWN ORANGE PURPLE THE CAPACITOR IS DUAL CAP WITH 3 POSTS. HOW DO I… read more
cmcdonald51206
cmcdonald51206
MANAGER
High School or GED
14 satisfied customers
Hey, I have a pretty old Coleman Evcon Cooler X heat pump outside.
Hey, I have a pretty old Coleman Evcon Cooler X heat pump outside. I just moved into the home so I know absolutely nothing about it. The other day the fan motor went out and I got a "rescue" motor bei… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,150 satisfied customers
Hi, I am trying to replace a GE fan motor model 5KCP39HG9433S
Hi, I am trying to replace a GE fan motor model 5KCP39HG9433S with an AOS DL1026, the specs seems to me identical, however I am having a hard time with wiring, the old motor have 3 wires(black, yellow… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,150 satisfied customers
I just replaced my old condenser fan motor with an new unit
I just replaced my old condenser fan motor with an new unit that has wires a extra brown with white stripe. i connected both brown wires to the new capacitor. the other 2 wires white and black i attac… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a goodman phk036-1 an the blower was burnt out so we
I have a goodman phk036-1 an the blower was burnt out so we got a universal ao smith the old motor was a ge and had 5 wires two brown that went to the cap one red that was caped off black was coneted … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a carrier package unit model # XXXXX I install a emerson
I have a carrier package unit model # XXXXX I install a emerson model k55hxstm-9563 condensor motor 2 days ago. I wired the black to the contactor, brown to point on existing dual capacator and white … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,150 satisfied customers
I am installing a mars 10469 condenser fan motor. I have two
I am installing a mars 10469 condenser fan motor. I have two caps connected via red wire that goes to red on a circuit board. I have brown and brown/white going to small cap. Red going to red circuit … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,150 satisfied customers
when replacing capacitor on a ruud seer 10 unit does it matter
when replacing capacitor on a ruud seer 10 unit does it matter how the wires are configured on the cap as long as they are grouped orange orange on one terminal , brown on one and prurple on one?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,150 satisfied customers
I am replacing the fan motor and capacitor on an older carrier
I am replacing the fan motor and capacitor on an older carrier AC unit. The Old fan had three wires, but the new fan motor is a multi horse power unit that has five. Red, Blk, Wht, Brn and Brn w/ wht … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,150 satisfied customers
I took your advice and replaced the fan control board, That
I took your advice and replaced the fan control board, That did allow the contacter to pull in and yhe o d fan to come on.The unit will run about 5 min. the the motors starts making noise and stops ru… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Replaced capacitor and fan motor in Ruud heater. Fan problem
I just replaced the capacitor and fan motor in my Ruud heat pump outdoor unit. The original motor had three wires and the replacement motor has five. I reconnected everything exactly as it was (I drew… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
the m# XXXXX XXXXX s# XXXXX XXXXX and it is a rudd
the m# XXXXX XXXXX s# XXXXX XXXXX i have a ruud 10 seer heat pump and the condenser fan motor went out the old motor is a 3 wire i wire going to circut board and 2 wires going to the dual cap. the new… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
I am replacing the fan motor on my goodman ck24-18 HVAC unit.
I am replacing the fan motor on my goodman ck24-18 HVAC unit. the old motor has 3 wires, purple, black, brown. the universal motor that I bought has 4 wires. white, black, brown, brown with a stripe. … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.