My Rheem Classic Super Quiet 80 is giving me problems. The…

Customer Question
My Rheem Classic Super Quiet...
My Rheem Classic Super Quiet 80 is giving me problems. The contactor (outdoor relay) is clicking on and off rapidly. The air conditioning seems to work during high demand. The problem seems to happen when the temerature inside the house gets close to the set temperature or when the air is on for a while. When it is in the clicking mode, it clicks even when the outdoor fuses are pulled and no power to the outdoor unit.
The ari conditioning tech changed the control board, the wifi thermostat to a manual one, and now the contactor. The problem is still there.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
7/1/2015
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,041
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
What is the voltage value at the contactor when this occurs?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
The AS tech said the voltages are normal, but he used an AC meter rather than an o-scope to see any spikes. This was the reason he decided to change the Control Board.
Customer reply replied 2 years ago
Serviz Tech
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
is there a water safety switch on a drain or pan in series with the low voltage
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Outside or inside the house? The tech is not here now, but I could check but I need a hint of where to look
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
the issue is strictly in the 24v circuit. from the time it leaves terminal R in thermostat to the time it gets to contactor.
If you find circuit board in furnace and the terminal R with a red thermostst wire...then follow that red wire...does it go straight to thermostat or to a switch in a drain pipe or pump?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
yes it goes to the switch in the PVC like you say and then up into the attic...somewhere
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
That water switch in the drain is a very common cause of the chattering.
If the drain is slow it pulses the switch..
Do you mind a test?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I'm ready
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
Now first...how often is the unit chattering?...if we do a test will we know fairly soon or is this just an occasional thing?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ill check right now
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
standing by
Ask Your Own HVAC Question
Customer reply replied 2 years ago
i put it back together and started it . it takes a few minutes. is the test bypassing the switch?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
correct....usually this happens when the unit has run a long cycle....the condensate is running more and a slow drain throttles the switch...you can also take a shop vacuum to the drain and purge the line.
Bypassing it generally tells us pretty quick
Ask Your Own HVAC Question
Customer reply replied 2 years ago
How do I use the vacuum? suck out the water from the overflow?
Customer reply replied 2 years ago
sorry, I'm unfamiliar
Customer reply replied 2 years ago
it is still clicking
Customer reply replied 2 years ago
it was off for about 1/2 hour so the drain must be really slow or the switch is bad
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
thank you nest is in the outdoor unit...the 2 wires go outside and attach to 2 wires at outdoor unit...then one of those 2 wires goes through low pressure, high pressure and maybe a delay board...what is make model of outdoor unit?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ill go look
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
ok
Ask Your Own HVAC Question
Customer reply replied 2 years ago
13AJA48A01
Customer reply replied 2 years ago
I PULLED THE FUSES AND IT IS STILL CLICKING
Customer reply replied 2 years ago
I forgot the brand name, something King
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
wow you got everything...inside the outdoor unit...where the 2 wires attach,,,one is yellow and one is brown...do you see these?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
yes they are on the outside of the contactor
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
correct....but before they go to contactor...the yellow makes some first.
your brown and yellow.....where they wire nut to the wires from house...do you see that junction point?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
on each side of the contactor
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
correct....but before they go to contactor...the yellow makes some stops first.
your brown and yellow.....where they wire nut to the wires from house...do you see that junction point?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
the wire from the house are insulated and goes into a grommet hole, not sure which panel i need to take off to see where they go. The yellow and brown come from a different hole
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
correct...it is the yellow and brown we are talking about...if you can post pics I can direct you quickly
Ask Your Own HVAC Question
Customer reply replied 2 years ago
i found the right angle bracket to take off. they are tied directly to the yell and brown, the wire nuts seem ok.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
what we want to do is remove the wire nut from the yellow.....and take the wire from the house and hold it directly to the terminal the yellow is on at the contactor,
This will bypass 2 pressure controls and a delay timer.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
this will deduce quickly which way the issue is
Ask Your Own HVAC Question
Customer reply replied 2 years ago
i'm waiting for the clicking problem. It sure looks like the red wire is going directly to the yelloiw. Same for the brown. All I'm doimng is makeing the yellow wire shorter, there are no other connections to bypass. Maybe I don't understand.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
your wires go direct to contactor?....not through any switches before the contactor?
The diagram shows a couple pressure switches and a time delay relay and then contactor
Ask Your Own HVAC Question
Customer reply replied 2 years ago
There are other wires (besides the heavy gauge wire) on the contactor coming from the outdoor unit.
Customer reply replied 2 years ago
at least four wires on a push on terminal that goes to the contactor bottom
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
you see there is 220v (which you have turned off)...the 24 comes from thermostat and closes the contactor...this allows 24v to cross.
That is why it chatters even when power off outside is because that 24v comes from indoors.
If the unit still chatters with the bypass direct to contactor then you your last culprit is transformer in the furnace that generates the 24v.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
i'll check the 24VAC when it starts to dhatter, its not doing it now. I think the transformer is mounted above the control board.
All i have is a VOM, but he tarnsformer can't be too expensive.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
transformer is very affordable.
That will be the last item that can cause this...If you need anything else just return to this thread
Billy
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thanks, ***** ***** i understand the system now. We think its an electrical problem and I can work that out. Thanks again.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
you are very welcome.
just rate service and I will move from active list
Billy
Ask Your Own HVAC Question
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,041
23,041 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What terminal on a trane xl80 is the common terminal as I am
What terminal on a trane xl80 is the common terminal as I am attempting to hook up a Honeywell wifi thermostat using a free blue wire in the thermostat wire bundle… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have a WiFi Thermostat RTH6500WF installed in our vacation
I have a WiFi Thermostat RTH6500WF installed in our vacation home. I setup the WiFi without a problem and was able to connect via Honeywell's website when I got home. And then I couldn't. I have been … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Need to connect c wire in Rheem RRKA-A030JK08E, but I'm not sure what to connect it t
Need to connect c wire in Rheem RRKA-A030JK08E, but I'm not sure what to connect it to so it gets power. You can see pictures at this link: http://www.justanswer.com/hvac/2louh-rheem-rrka-a030jk08e-un… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I purchase a honeywell wifi thermostat, but I have a heat
I purchase a honeywell wifi thermostat, but I have a heat pump. trying to figure out the wiring. it seems that the W wire now goes to O/B, but not sure where the W2 wire goes. When the new thermostat … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Do I need an app to my wifi thermostat. Linksys. I can
Do I need an app to my wifi thermostat JA: Who makes your router? Customer: linksys JA: What have you tried so far? Customer: I can connect but not control or program JA: Anything else you want the Ne… read more
Sheri
Sheri
Bachelor\u0027s Degree
533 satisfied customers
My TRane xL824 wifi thermostat screen is blank can you help?
my TRane xL824 wifi thermostat screen is blank can you help? … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,041 satisfied customers
I just installed a Honeywell RTH9585 wifi thermostat for my
I just installed a Honeywell RTH9585 wifi thermostat for my heat pump. I can get the fan to work but not the heat and cooling… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I installed a new honeywell wifi thermostat and it's blowing
I installed a new honeywell wifi thermostat and it's blowing cold aid in heat mode … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
I lost power to my WiFi thermostat and the furnace will not
I lost power to my WiFi thermostat and the furnace will not turn in … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
452 satisfied customers
Want to purchase Carrier Cor 7 Wifi thermostat, how do I
Want to purchase Carrier Cor 7 Wifi thermostat, how do I know if it's compatible with my Carrier HVAC system? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I HAVE THE TH6320R WIFI THERMOSTAT AND I SET IT UP WITH AT
i HAVE THE TH6320R WIFI THERMOSTAT AND I SET IT UP WITH AT THE THM5320R AND THE REDLINK … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to install a Honeywell WiFi Thermostat, but I
Hi, I'm trying to install a Honeywell WiFi Thermostat, but I have no blue common wire available in the existing wiring supplied between the furnace and the thermostat. I have a White-Rodgers-50t35-730… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Trying to connect a WiFi thermostat to an older Lennox G11
Trying to connect a WiFi thermostat to an older Lennox G11 furnace that does not have a C terminal. Furnace has R W Y G T. Is it possible to install this thermostat ? Thermostat is a Honeywell RTH8580… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I purchased a lyric T5 hooked up the wires and I can't get
I purchased a lyric T5 hooked up the wires and I can't get the ac compressor to kick in … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a York Diamond 90 Furnace P3URB10N05501C - I recently
I have a York Diamond 90 Furnace P3URB10N05501C - I recently purchased a Honeywell WiFi thermostat and I need a 24v supply wire to the thermostat. There are five wires running to my thermostat now, al… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a ducane 2hp13l30p-1b unit out side that is not running
I have a ducane 2hp13l30p-1b unit out side that is not running it does have the proper voltage coming in, last year I replaced the board and cap.… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
trying to replace an auomag thermostat that has R W connections with a honeywell wifi th
trying to replace an auomag thermostat that has R W B connections with a honeywell wifi thermostat ; I need a "C" wire and need to which wires to use… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
want to replace Honeywell T87F thermostat with Q539 base,
want to replace Honeywell T87F thermostat with Q539 base, with a Honeywell rth9580 wifi thermostat. I don't have a "C" wire and their option is to use the G wire at the loss of the fan in manual mode.… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,041 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x