My Rheem Classic Super Quiet 80 is giving me problems. The contactor (outdoor relay) is clicking on and off rapidly. The air conditioning seems to work during high demand. The problem seems to happen when the temerature inside the house gets close to the set temperature or when the air is on for a while. When it is in the clicking mode, it clicks even when the outdoor fuses are pulled and no power to the outdoor unit.
The ari conditioning tech changed the control board, the wifi thermostat to a manual one, and now the contactor. The problem is still there.
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
7/1/2015
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
What is the voltage value at the contactor when this occurs?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
The AS tech said the voltages are normal, but he used an AC meter rather than an o-scope to see any spikes. This was the reason he decided to change the Control Board.
Customer reply replied 3 years ago
Serviz Tech
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
is there a water safety switch on a drain or pan in series with the low voltage
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Outside or inside the house? The tech is not here now, but I could check but I need a hint of where to look
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
the issue is strictly in the 24v circuit. from the time it leaves terminal R in thermostat to the time it gets to contactor.
If you find circuit board in furnace and the terminal R with a red thermostst wire...then follow that red wire...does it go straight to thermostat or to a switch in a drain pipe or pump?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
yes it goes to the switch in the PVC like you say and then up into the attic...somewhere
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
That water switch in the drain is a very common cause of the chattering.
If the drain is slow it pulses the switch..
Do you mind a test?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
I'm ready
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
Now first...how often is the unit chattering?...if we do a test will we know fairly soon or is this just an occasional thing?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Ill check right now
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
standing by
Ask Your Own HVAC Question
Customer reply replied 3 years ago
i put it back together and started it . it takes a few minutes. is the test bypassing the switch?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
correct....usually this happens when the unit has run a long cycle....the condensate is running more and a slow drain throttles the switch...you can also take a shop vacuum to the drain and purge the line.
Bypassing it generally tells us pretty quick
Ask Your Own HVAC Question
Customer reply replied 3 years ago
How do I use the vacuum? suck out the water from the overflow?
Customer reply replied 3 years ago
sorry, I'm unfamiliar
Customer reply replied 3 years ago
it is still clicking
Customer reply replied 3 years ago
it was off for about 1/2 hour so the drain must be really slow or the switch is bad
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
thank you nest is in the outdoor unit...the 2 wires go outside and attach to 2 wires at outdoor unit...then one of those 2 wires goes through low pressure, high pressure and maybe a delay board...what is make model of outdoor unit?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
ill go look
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
ok
Ask Your Own HVAC Question
Customer reply replied 3 years ago
13AJA48A01
Customer reply replied 3 years ago
I PULLED THE FUSES AND IT IS STILL CLICKING
Customer reply replied 3 years ago
I forgot the brand name, something King
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
wow you got everything...inside the outdoor unit...where the 2 wires attach,,,one is yellow and one is brown...do you see these?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
yes they are on the outside of the contactor
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
correct....but before they go to contactor...the yellow makes some first.
your brown and yellow.....where they wire nut to the wires from house...do you see that junction point?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
on each side of the contactor
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
correct....but before they go to contactor...the yellow makes some stops first.
your brown and yellow.....where they wire nut to the wires from house...do you see that junction point?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
the wire from the house are insulated and goes into a grommet hole, not sure which panel i need to take off to see where they go. The yellow and brown come from a different hole
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
correct...it is the yellow and brown we are talking about...if you can post pics I can direct you quickly
Ask Your Own HVAC Question
Customer reply replied 3 years ago
i found the right angle bracket to take off. they are tied directly to the yell and brown, the wire nuts seem ok.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
what we want to do is remove the wire nut from the yellow.....and take the wire from the house and hold it directly to the terminal the yellow is on at the contactor,
This will bypass 2 pressure controls and a delay timer.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
ok
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
this will deduce quickly which way the issue is
Ask Your Own HVAC Question
Customer reply replied 3 years ago
i'm waiting for the clicking problem. It sure looks like the red wire is going directly to the yelloiw. Same for the brown. All I'm doimng is makeing the yellow wire shorter, there are no other connections to bypass. Maybe I don't understand.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
your wires go direct to contactor?....not through any switches before the contactor?
The diagram shows a couple pressure switches and a time delay relay and then contactor
Ask Your Own HVAC Question
Customer reply replied 3 years ago
There are other wires (besides the heavy gauge wire) on the contactor coming from the outdoor unit.
Customer reply replied 3 years ago
at least four wires on a push on terminal that goes to the contactor bottom
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
you see there is 220v (which you have turned off)...the 24 comes from thermostat and closes the contactor...this allows 24v to cross.
That is why it chatters even when power off outside is because that 24v comes from indoors.
If the unit still chatters with the bypass direct to contactor then you your last culprit is transformer in the furnace that generates the 24v.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
i'll check the 24VAC when it starts to dhatter, its not doing it now. I think the transformer is mounted above the control board.
All i have is a VOM, but he tarnsformer can't be too expensive.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
transformer is very affordable.
That will be the last item that can cause this...If you need anything else just return to this thread
Billy
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Thanks, ***** ***** i understand the system now. We think its an electrical problem and I can work that out. Thanks again.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 3 years ago
you are very welcome.
just rate service and I will move from active list
Billy
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
23,151 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a rheem air handler RHSL_HM3617CU that is blowing the
i have a rheem air handler RHSL_HM3617CU that is blowing the 5amp fuse on the handler board. This is after a tech came out and replaced the 3amp with a 5 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Having a problem with my unit not blowing hot air. All
Having a problem with my unit not blowing hot air JA: Did you double-check the thermostat's settings? And what about the filters? Customer: all checked JA: Do you plan on doing the work yourself? Cust… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Rheem RGPT-07EBRQR furnace and a Rheem central air.
I have a Rheem RGPT-07EBRQR furnace and a Rheem central air. Starting today the furnace control borad transformer blows the fuse if you put the thermostat in the cooling mode. The furnace board is a 6… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
I have trouble with my furnace. It's a Rheem Classic Super
I have trouble with my furnace. It's a Rheem Classic Super Quiet 80. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Amp draw while heat pump is in cooling mode is below rla.
Amp draw while heat pump is in cooling mode is below rla. Switch to heat mode and after a few minutes top of compressor starts getting hot and amp draw start going up until draw gets 3 amps over rla t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a rheem rhllhm4821ja air handler and a rheem prestige
I have a rheem rhllhm4821ja air handler and a rheem prestige compressor. The fuse blows on the ah circuit board frequently and now is doing it every few minutes. The fan in the air handler sounds smoo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Rheem Classic 80, It was installing in 2007. The AC
Hello, I have a Rheem Classic 80, It was installing in 2007. The AC Unit outside won't turn off.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi guys. I have a Rheem Classic Series- Super Quiet 80. I
Hi guys. I have a Rheem Classic Series- Super Quiet 80. I just had to reset the furnace -twice- by shutting off the furnace service switch, waiting, then turning it back on. After the 2nd power up, it… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Rheem Classic Plus Super Quiet 80 two -stage furnace.
I have a Rheem Classic Plus Super Quiet 80 two -stage furnace. It blows out cold air 90% of the time. I cut it off for 30 minutes and it worked for one heating cycle then back to cold air. I opened th… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
New humming noise coming from outdoor air conditioning condenser
New humming noise coming from outdoor air conditioning condenser -- Reason for concern? This condenser is less than 3 years old but has recently begun to emit an electronic humming noise when on which… read more
Jason
Jason
Lead Service Technician
Associate Degree
110 satisfied customers
I own a rheem super quiet classic 80; whereby, all the components
I own a rheem super quiet classic 80; whereby, all the components have been replaced due the a non-firing condition on the burner. The burner flames out continuosly; thereby, blowing insufficiently he… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
Trane XR-12 Heat pump blows the 5amp control fuse when switched
Trane XR-12 Heat pump blows the 5amp control fuse when switched to the heater mode, works fine in AC mode, what would cause this.… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Rheem Classic Super Quiet 80 furnace. Model # XXXXX
I have a Rheem Classic Super Quiet 80 furnace. Model # XXXXX that blows air, but will not light up to give heat. I tried bringing up thermostat and nothing. It had the same problem a year ago and the … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My Ruud Achiever super quiet 80 will not turn on in heat or
My Ruud Achiever super quiet 80 will not turn on in heat or AC mode. Not even the fan will turn on and the board lights are all off. The unit is receiving power as I hear a dull humming sound when I d… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I can not get the air handler to kick on by setting the thermostat
I can not get the air handler to kick on by setting the thermostat to the on position and setting the temperature. It will not kick on in Heat or Cool mode. I am assuming there is no power to the air … read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
My rheem air handler fan will not shut off even when I adjust
My rheem air handler fan will not shut off even when I adjust the thermostat setting to 'off' for both fan and unit. I disconnected entire thermostat and also replaced with a new thermost but the prob… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
Hi my name is greg, I purchased a house and the cetral
Hi my name is greg, I purchased a house and the cetral air would not work?I oened the air handler and found that the 5amp 24volt fuse was blown in the board. I replaced the fuse and ran system aprox 3… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My wife just called me from home and told me that the furnace
My wife just called me from home and told me that the furnace is blowing cold air. she checked the all the thermostate setting and everything is in order. I was wondering if when i go home is some che… read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x