My a/c unit isn't cooling. Inside the fan is working but…

Customer Question
Hi, my a/c unit isn't...
Hi, my a/c unit isn't cooling. Inside the fan is working but not blowing out cold air. Outside the compressor and fan are not working. I've checked the contactor and it's working and the capacitor looks OK. What else could it be?
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 20 minutes by:
6/29/2015
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
Experience: Furnace, A/C and heat pump specialist.
Verified
Hello. My name is ***** ***** I'll do my best to help. Let's get started and see what we can do.Troubleshooting often requires meters and test equipment.Do you have a multi meter for testing voltage? If not you can get an inexpensive one at Walmart for about 15 bucks, if you have or would like to obtain a meter to troubleshoot , I will be happy to guide you.Without a meter , there are a limited number of things we can check if you are able to do a visual inspection and can do some hands on troubleshooting.Please let me know and we can go from here.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
I have a multi-meter
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
OK. First step is to locate the contactors in the outdoor unit. Then we want to see if we have 24 volts ac to the contactor coil .Next 230v to the contactor and then 230v out of contactor. See below:
http://i.imgur.com/8UHOZPo.png
Ask Your Own HVAC Question
Customer reply replied 3 years ago
sorry Tim, this isn't going to work. My PC is on one side of the house and the A/C on the other. I think I'll just call an HVAC engineer...thanks.
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings now. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
Leaving a poor service rating will not automatically refund your money,but reflects poorly on your expert. You have to request a refund if not satisfied with the information provided being accurate.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
So if I give you a rating will it cost me. We haven't done anything?
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
You have already paid when you asked the question.If you rate, the question is considered closed.If you do not rate, your money just sits there until you rate.If unsatisfied with my answer and have decided you no longer want help or to continue you may request a refund.You should see a drop down list to select refund.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
9,367 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My old ac fan motor had purple, black, and wires. The new
My old ac fan motor had purple, black, and brown wires. The new fan motor has black, white, brown, and brown/white. Im trying to figure out how to wire to a capacitor with fan, c , and herm post. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Rheem Mod #RQNJ-a048JK-000 is only blowing cold air. The
My Rheem Mod #RQNJ-a048JK-000 is only blowing cold air. The heater was working 2 days ago. Is there anything I can do before I call a tech? … read more
airheatman
airheatman
HVAC Technician
6 years college
9,367 satisfied customers
My a/c will not blow cold. Air is coming through the vents
my a/c will not blow cold. Air is coming through the vents but it is not cold. the unit is only 3 years old, what can I do?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My 3amp fuse on my contro, unit keeps blowing. I've traced
Hi, my 3amp fuse on my contro, unit keeps blowing. I've traced the issue to the low voltage wiring coming from the outside A/C unit. Now I'm not sure if it is the wire itself shorting or something on … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Have a totaline thermostat P474-1050. Ever since my outside
Have a totaline thermostat P474-1050. Ever since my outside unit was replaced it hasnt cooled correctly it seemed. It would cool down to 76 and shut off, but it still felt like it was 80. I went into … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
We have a Goodman AC unit.. The outdoor compressor isnt turning
We have a Goodman AC unit.. The outdoor compressor isn't turning on?.. Fan works, but is clicking off every few minutes than back on... not cooling the house.....… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have an Armstrong Ultra SX 80 furnace and A/c. It is about
I have an Armstrong Ultra SX 80 furnace and A/c. It is about 12 yrs old,never any problems until now .Set the thermostat to cool last night and the compressor will not come on. The thermostat call for… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have a Trane AC unit and dont have cold air blowing inside
I have a Trane AC unit and don't have cold air blowing inside the home, air is blowing but not cold air. I have cleaned/pressure washed the coils, checked the battery on the inside thermostat (which I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a ComfortStar Plus Model CHH012CD-13 Split Unit; the
I have a ComfortStar Plus Model CHH012CD-13 Split Unit; the fans are working fine on it, but yesterday, the air coming out just stopped being cool, and now it's just warm air. We have it set on COOL o… read more
Will
Will
President
Vocational, Technical or Trade Scho
131 satisfied customers
We have a York gas dual zone hvac system. Starting yesterday,
We have a York gas dual zone hvac system. Starting yesterday, our upstairs is not cooling at all. (The downstairs unit is blowing cold). We can feel air coming out of the upstairs ducts but it is warm… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My lennow AC unit for the upsatirs just quit blowing cold air.
My lennow AC unit for the upsatirs just quit blowing cold air. The fan is running. Fan and capacitor were replaced last July. Is it out of freon? I can't tell if the compressor is running. Please help… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Goodman Package unit model PGB024075-1 purchased new
I have a Goodman Package unit model PGB024075-1 purchased new in 1993. A good unit and not used that much. Ran good last year but this year she wont cool. I set the thermostat to cool and lowered the … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Goodman Hvac-The air handler is running, the outside fan is
Goodman Hvac-The air handler is running, the outside fan is running but the unit is blowing hot air through the vents. The fan outside is blowing cool air. I don't think the compressor is coming on. I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Everything in my Lennox unit is working but it is not blowing
Everything in my Lennox unit is working but it is not blowing cool air. I have checked freon(130pounds on the static side) changed out the contactes, checked the capacitor,changed out the thermostat t… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Have an older RUUD unit-inside fan turns on when set to cool,
Have an older RUUD unit-inside fan turns on when set to cool, but outside unit will not start. Contactor has no voltage to engage either fan or compressor; if I manually press down contactor everythin… read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
my air conditioner quit working. the air is blowing thru my
my air conditioner quit working. the air is blowing thru my vents but isnt cold. the fan on my outside unit isnt turning but can be moved easily with a stick. it is a trane xr11… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Trane XL1200 and the air is not blowing cold. I switched
I have a Trane XL1200 and the air is not blowing cold. I switched from A/C to heater for a week or so and when I switched back to A/C, it's no longer cold. Any suggestions?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Trane XL1400 compressor does not cool. Fan on compressor only
Trane XL1400 compressor does not cool. Fan on compressor only slowly turns back and forth (1/4 turn). Heating works well, air is blown around but not cooled.… read more
HVAC DOCTOR
HVAC DOCTOR
President
Vocational, Technical or Trade Scho
74 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x