have a disconnect box issue
Submitted: 2 years ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 8 minutes by:
6/28/2015
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Hi I'm Brian and I'm here to help! What kind of issue are you having with your disconnect?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
My fuse had burned and melted, the fan was running and stopping getting hot prior to that. I got a new disconnect and fuse same amps and volts just set up a bit different. followed the load line line load diagram. but now the ac unit just clicks one time when I turn it on, nothing else. Is it something else, is it the box, or my wiring?
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
If the disconnect was wired incorrectly, chances are you would have heard a loud pop with sparks and the breaker would have tripped or the fuses would have blown. It's possible there may be some type of power company load management device attached or even unit provided time delay. I would give it up to 10 minutes after you close the disconnect to see if your unit starts then. Of course make sure the thermostat is set properly and your breaker or fuses inside are set to on. Some power company load management delays can be up to 10 minutes long. If you can upload a picture of your disconnect wiring using the 'Attach Files' button or the Paper clip icon in your reply dialog box, I'd be happy to double check your wiring for you! Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
you just need a pic of the actual wiring I did. How will you tell which wire is which by looking at the pic?
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
I may need to ask for some clarification but chances are good I may be able to tell with just a picture.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok will do
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
A close up shot and a wide shot will help. That way I can see the conduit(s) or flexible conduit(s) are attached.
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
*how they're attached.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok, but I have the type that goes into the wall as you will see. But I took a photo of the back panel of the ac where the capacitor is. Again it clicks like its trying to come on but that's it. uploading pics now
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Ok, I'm sure we can figure this out together! btw the pics are still not posted. Are you having upload issues? It does happen occasionally. -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
yes I am
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Let me see if I can get some help for you to get the pictures uploaded. If you have an account with a third party picture site you could upload them there and share the link with me but I will try to get some help for you from customer service. Sorry for the issue and thanks for your patience.
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
That's good because when I tried to get help for you the app locked my browser up! Sorry for the delay! I'll review your pics now. Thanks for uploading them!
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
The wiring on the disconnect looks ok. If you hear a click when you turn your system on, that could be coming from the thermostat sending a signal to your unit outside and the contactor (the device with the two large line voltage wires are connected) is engaging. It's possible even though you replaced the disconnect (and I assume fuses if the new one holds them) that your are still not getting 240 volts to the outdoor unit. It would really require a volt meter to check some voltages for me to help you determine where the problem still lies. Do you have access to and knowledge of a volt meter?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
not at the moment. why would I all of a sudden not be receiving the 240 volts just from changing the disconnect.
Customer reply replied 2 years ago
I am checking with my neighbor for a meter. could it be the capacitor?
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
It could be possible that the breaker that feeds that disconnect did not fully turn back on after you replaced the disconnect. This is a common occurrence on a circuit that has been overheating like yours has. If the disconnect was wired wrong it would only do one of two things: 1) either pop the breaker that feeds it immediately and you would have known because it would have popped in your hand when you inserted the disconnect handle, or the breaker would have popped in your hand if the disconnect handle was already in when you turned the breaker on. OR 2) nothing would have happened and the unit would have power if your breaker was ok even if two of the line load wires were in the wrong side. It could be a capacitor but as long as you had the unit off chances are you would have heard the groan of the fan and/or compressor trying to start. So that is low on the list of possibilities for the moment. Let me know if you score a meter and I'll help you check some voltages and that will tell us what's going on. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok thanks. if not the capacitor is there really any other easy fix.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
If it's the breaker not resetting, sometimes you can work it off then on very firmly and it will reset. Without knowing whether it's a voltage issue or a signal issue from the thermostat It's hard to tell if there could be any other easy fix. Is the air blowing inside from the inside unit? Looking at the capacitor, it is not swollen at all and nothing else I can see within the unit jumps out at me visually. I wish I could be more help but this is a case where the right tool for the job is necessary. Let me know how I can help further. We have as much time as you need, even if it goes into tomorrow or even later. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok will get a meter tomorrow
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Sounds good, I will be in and out here tomorrow but leave a reply and I'll post back as soon as I can. Thanks and have a great night! -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
whats the first thing I need to check with the meter
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Good morning! Ok with your meter set to read ac voltage (make sure the meter leads are plugged into Com and V sockets on the meter) The ac voltage range should be left at auto or at least 400 volts ac. Now, in the disconnect, pull the handle out and measure the voltage at the two LINE terminals. You should read 240 volts nominal there. Let me know what you get and we'll go from there. Thanks, -Brian
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Sorry!!! that should have read "at the two LINE terminals" on the disconnect, NOT LOAD yet!
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok I go 240 from the line terminals
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Awesome! Now plug the disconnect handle back in and check the voltage at the LOAD terminals on the disconnect please.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
nothing at all from the load
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Ok, the 240 volts on the LINE terminals tells me your breaker is fine in the panel and you have wired your disconnect correctly. Since you have voltage on the LINE but not the LOAD, it can only mean that the fuse(s) in the handle fuse cartridge are blown. If the meter has an OHM scale (resistance) you can pull the handle and check the fuses with the meter set to its lowest resistance scale. The reading across the fuse cartridges should be close to zero ohms. If you had put new fuses in and they are already blown, you may have a deeper problem in your ac unit. Let me know what you find, thanks.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
where are the fuses?
Customer reply replied 2 years ago
nevermind that I assume there the slots the handle goes in. do we need to check the line, or load or both with the resistance
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Edit: after reading last post (was writing response below) DO NOT check resistance on the LINE or LOAD terminals! That will damage your meter! Test the fuses themselves which should be in the pull out handle if the disconnect has fuses. Pictures of the handle and the disconnect with the cover removed may be helpful to me here. Because of the readings you are getting (voltage on LINE but not LOAD with disconnect plugged in) I am assuming this is the type of disconnect that has the fuses in the disconnect handle itself. If there are no fuses in that disconnect then the disconnect is faulty. Do you still have voltage on the LINE terminals when the disconnect pull-out handle is pushed in and ON is up? and you don't have voltage on the LOAD terminals with the disconnect handle in with ON up?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok when I check the load terminals it goes to 0. when I check the line it bounces around between -110 to -130
and that's set on the resistance.
Customer reply replied 2 years ago
The voltage on the LINE have 240 whether the handle is in the off or on position. The LOAD voltage does not read anything when the handle is in the off or on position.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Edit: Thanks for that clarification! I was writing everything you see below and was about to send it when you posted your last reply ;) My response below should explain. Let me know if you have questions. It appears there are either fuses in the disconnect that are blown OR if there are no fuses in the disconnect, the disconnect is faulty. But read the post below for more clarification. Post before the edit above:Yeah, again we shouldn't be checking resistance on the terminals with the wires in them. Just voltage on those spots! Your meter probably has an auto protection in it fortunately. Let me tell you what you should and shouldn't have for voltage on the terminals in the disconnect and maybe that will be helpful for you:1) When the disconnect handle is NOT plugged in you should have 240 volts ac on between the two LINE terminals and zero voltage on the two LOAD terminals.2) When the disconnect handle IS plugged in you should have 240 volts between the two LINE terminals AND 240 volts between the two LOAD terminals. You said earlier that you had 240 volts on the line terminals and zero volts on the load terminals with the handle in and ON is up. That indicates either blown fuses in the disconnect (if there are fuses in it) OR the disconnect handle is in and in the OFF position (handle upside down) OR the handle is in and in the ON position and the new disconnect has an issue. I was just suggesting you use the resistance scale to test the fuses (if there are fuses in the disconnect). It appears there may be a problem with that disconnect. That's why I asked for the pictures. Thanks, -Brian
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Ok thanks for those pictures! This clears everything up! That handle is also a fuse holder and will hold FRN style 250 volt buss cartridge fuses! There are no fuses in it and that's why things aren't working. If you have the proper size breaker in your breaker panel that supplies that circuit you can put 60 amp fuses in the handler fuse receptacles. The LINK HERE provides an example of what the fuse looks like. Ace Hardware or a similar hardware store is probably the best place to find them. Call first, a lot of hardware stores aren't open on Sunday! Turn your breaker off inside, install the fuses in the disconnect handle, insert the disconnect handle, then turn you breaker back on. That will take care of your issue if there is no other problem in the unit! Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thanks, ***** ***** tell we are new to this, I feel real silly. I didn't see fuses in the last disconnect handle, so I just assumed the new one would be the same. Makes sense though. We will get fuses and see how that works.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
No worries. That's what we're here for! This stuff is second nature to us but can be hard to explain to the layman. Let me know how it goes and if it works! Thanks, ***** ***** If it worked before you changed the disconnect, it should work fine once you get the fuse in!
Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok that got it. Our problem now is what probably melted the last fuse box in the first place, which was the fan not turning, when we turn the unit on it will start to move slowly then stop, then the unit gets real hot. Im assuming the fan motor, it was replaced about 2 years ago.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Yeah, it sounds like the fan motor has gone bad. It may have been the disconnect that took out the fan motor and not the opposite. Even at locked rotor current, the fan motor itself will not make the disconnect burn. By the looks of the wires in your disconnect it would appear one or more of them may have been loose and caused the issue. Does the compressor run ok?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
yes it runs but the fan will not move. it sounds like the motor is getting ready to go but the fan never moves.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Yep, no real sense looking further, I would say your fan motor is shot indeed. Sorry for the bad news :( would you like me to source one online for you?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
we got one from grainer 2 years ago, is there some place better/cheaper? I don't remember off hand how much it was but I think it was over $200
Customer reply replied 2 years ago
sorry grainger
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Yeah, Grainger is historically very expensive! You can get an aftermarket one online for less than half that. I'll see what I can find. You should also replace the dual run capacitor at the same time. Can you tell me what the Mfd rating of the capacitor is please? I'll look for one of those as well, they are really cheap online! It will be something like 50+5 Mfd-370 volts ac or 45/7.5 mfd at 440 VAC or something very similar.
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Oh, and I will need the make and model number of the unit itself to source the motor! If you have the motor specs that would be helpful too. All I need it RPM, HP and rotation. I know the rest. Or a motor model will get me there too. Make and model of the unit is important though.
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Yeah I've gotta go offline for a bit too. I'll post back a little later with the info I find for you. Thanks, -Brian
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Boy, I'm having trouble locating the specs on the motor! I see the motor is 1/4 horsepower by the unit data plate but I can't get any more info! All I really need is the RPM and the rotation of the motor. You can just tell me whether the motor turns clockwise or counter-clockwise as you look down at the fan blade in your unit. I can take it from there. I believe I can find you an aftermarket motor for around $75! The capacitor size will depend on the motor I find for you. If you like, I can probably also find the OEM motor with the info above as well. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Not sure on rmp. but it turns clockwise
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Ok thanks. I will continue to try to look when I get back online tomorrow and reply with what I can find. It appears that model series could either have a standard 1100 rpm motor or a slower 850 rpm motor and that's a huge difference so I have to find that out before I can recommend a motor for you! Thanks and have a good night,Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
We will find the rpm and let you know you don't have to worry about that. Thanks though
Customer reply replied 2 years ago
Ok went ahead and got a new motor and capacitor. Everything was installed and was running fine, but now cuts of and on. It will run for a minute or two then stop, no noise at all and start up again later.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Hello again and sorry for the slow response. This sounds a bit like you may have a high or low refrigerant pressure switch tripping and cutting the unit off and on. I would check to make sure the condenser coils are clean and when the unit is running the larger of the two copper lines attached to it from the house is cool to the touch, the smaller copper line should be no higher than 20 degrees above the outdoor temperature. If the copper lines are outside of those ranges when the unit does run, then you probably have a very dirty coil (even if it doesn't look like it) or a low refrigerant condition. It would require manifold gauges to test the refrigerant level. Thanks, -Brian
Ask Your Own HVAC Question
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
953 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Condenser contractor chattering is it bad? Just notice
We had very cold weather down to 10 degrees, fan not been running until today thouzght was running's. On heat strips. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat pump condenser coil are freezing up during this
my heat pump condenser coil are freezing up during this latest cold spell, can I thall them by using my aux mode … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have aTrane XE 1200 AC and as of yesterday the condenser
I have aTrane XE 1200 AC and as of yesterday the condenser fan and compressor won't shut off. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL #702H02997 THAT THE COMPRESSOR WAS RECENTLY REPLACED BUT i STILL HAVE A ISSUE WITH IT IT CRANKS BUT IT STOPS AFTER 45 SECONDS NEED HELPWITH THIS IS… read more
R G
R G
44 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,416 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x