Installed a two ton Gibson heat pump
Had trouble getting proper pressures.
Got pressures to 125 and 425. Unit shut down on temp. When unit turned back on pressures dropped to 80 and 350.
Dropped charge and leak tested. No leaks found.
Tried to recharge unit but could not get suction pressures above 20 psi
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 days by:
6/30/2015
HVAC Technician: gotoman for ac, HVAC Technician replied 3 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,362
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
You have a restriction in coil or metering device. There is a screen in line just before metering device. Open up and clean screen. Russ
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Subject: heat pump system subcooling requirements for a
subject: heat pump system subcooling requirements for a downflow air handler.I have Rheem 6 ton variable speed split heat pump system. My air handler is installed in downflow position. Air handler is … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a trane package unit suction 85 psi and line temp 65
I have a trane package unit suction 85 psi and line temp 65 degree. High side 370 psi and 175 degree on r22, what happened?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
what is the best way to charge heat pump when nameplate missing.
what is the best way to charge heat pump when nameplate missing. don't know tonnage or factory charge. r-22 and 30degreees… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,362 satisfied customers
what would cause the high side and low side pressure on a 3
what would cause the high side and low side pressure on a r410a 3 ton goodman heat pump to be 400+ psi? The unit was charged in heating mode and 11lbs 1 oz of refrigerant was used. When the heat pump … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,362 satisfied customers
I an Hvac system with low performance. Suction pressure is
I an Hvac system with low performance. Suction pressure is 10 psi and 125 on the hi side. the suction line is iced over from the unit to the a-coil and the a-coil itself. please advise… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have nordyn js5bd 024kb lowside 80 highside 230 but after checking
Have nordyn js5bd 024kb lowside 80 highside 230 but after checking superheat very closely and charging reading good about (60degrees farenheit on required superheat) (- run for 10 minutes and high sid… read more
rpen7111
rpen7111
119 satisfied customers
I was recently working on a 3 ton Goodman(R22) replacing a
Hello, I was recently working on a 3 ton Goodman(R22) replacing a TXV, due to the high side having head pressures of 600 PSI , and I also changed the bi flo filter on the hide side as well. The custom… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,362 satisfied customers
I have a ultra 5 tech 80 air handler, an older carrier unit
I have a ultra 5 tech 80 air handler, an older carrier unit outside, guages reading "r-22" 50 deg on the low side and 275lbs on the high side, the condensor line is "cold" on the low side all the way … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
How to recharge Freon for HVAC 2 Ton- 3 Ton and how to measure
How to recharge Freon for HVAC 2 Ton- 3 Ton and how to measure pressure on section line & Heat line by Gauge manifold kit… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodmam 4 ton, 16 SEER, R410A, 2years old. In the summer, in cooling mode th
I have a Goodmam 4 ton, 16 SEER, R410A, 2years old. In the summer, in cooling mode the suction press is 140 and a disch of 340. When switched to heat mode the pressures are almost equal (within 25 psi… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
looking for a Freon Charging Chart in Heat Mode for a TRANE
looking for a Freon Charging Chart in Heat Mode for a TRANE HEAT PUMP Model # XXXXX The Suction Line is HOT to the touch pressure is 80 PSI The Pressure at the Service Port at the Reversing Valve was … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,362 satisfied customers
I use Atlas Frost-top with granite on top of the unit. It normally
I use Atlas Frost-top with granite on top of the unit. It normally takes about 45 minutes to freeze the granite (frost on granite) . Lately only 50% of the granite freeze up. There is water between th… read more
drcool299
drcool299
shop owner
Bachelor's Degree
22 satisfied customers
When charging a air conditioner I have seen differant methods
When charging a air conditioner I have seen differant methods used, I was always taught to use superheat if the system uses a fixed orifice metering device or subcooling if it;s a txv. now I was also … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
proper piston size for a twj7224a100a0 s/nd34521086, press.80-375.20
proper piston size for a twj7224a100a0 s/nd34521086, press.80-375.20 degree super heat,32 deg. sub-cool. no restiction rev. valve ok, coils clean, with proper air flow… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
150 head pressure 60 suction pressure. R22 Should cool right?
150 head pressure 60 suction pressure. R22 Should cool right. 78 degrees suction line 84 degrees head line. New filters. Clean coils. 70 degrees air temp at the registers. What the heck? Optional Info… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
i have a trane condensing unit (2TTB30A100A) and goodman air
i have a trane condensing unit (2TTB30A100A) and goodman air handler (ARUF303016). and honeywell pro5000 thermostat. my original air handler was trane(2TGB3F30A1000A). the problem i have right now is … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i just installed a new 2 1/2 ton heat pump 410 a with a txv
i just installed a new 2 1/2 ton heat pump 410 a with a txv airhandler. I have 30 feet of line set and my pressures are 120 suction and a 240 discharge. at 45 deg. outside ambient temp are these presu… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hey dude, somehow I got this other guy,but my suction pressure
Hey dude, somehow I got this other guy,but my suction pressure 30 seconds out is 65 psi, and discharge is 250, then 1 min out the pressures are 60 and 160. the installer claimed it was tripping out on… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x