Customer Question
I have a Trane UDO80R9V3K...
I have a Trane UDO80R9V3K. The gan is not going on, there is water/condensation leaking, and the LED on the control board is on indicating it needs to be replaced. The local tech hypothesized that the blower motor is bad causing condensation to build up and leak onto the control board causing it to fail. They want to replace the control board and motor $1500 in parts plus labor.
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 hours by:
6/22/2015
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Hello, a bad blower motor will not cause water to build up in the cooling coil and so that it leaks down through the furnace and onto your control board... it will cause the coil to ice over though, and when the ice melts water can drip down over the control card etc. If the blower runs it is fine and does not need to be replaced... let me know if you can get it run by setting the thermostat FAN setting to ON. The model number you gave does not compute, did it come from a sticker inside the gas valve compartment that also shows the serial number. that will be the place to get the correct model number. If the blower does not run with fan set on Fan ON, it could very likely just be a bad fan relay on the control card and not a bad motor. Tell me if this blower is variable speed (starts and stops very slowly and quietly) or if it tends to come on hard or not... that will tell me what I need to know about the pricing. We can go from there.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
The number on the sticker is TUD080R9V3K4. There is a second number 7082P161G.
The blower does not come on with the fan set to on. It is a variable speed motor. I pulled the motor and checked all the resistances. They seem fine. I'm not sure how to check the ECM. My thinking is to replace the control board and then plug in the motor and see if it works. The control board is definitely bad. Of course none of the local distributors will sell to a consumer so it doesn't look like I can fix it today.
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
Hello again, you are on the right track.Look this video over for the most common failures in these end bell speed controllershttps://www.youtube.com/watch?v=5Q5mm1Nqx9UTell me what you find on your motor. Lets do that first, and go from there. Please hold your rating until we get the situation entirely resolved.--------------We are on the honor system here. Please remember to rate my service before you leave today. If you need anything else, just let me know. You can continue asking follow-up questionst at no additional charge.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
On my Trane evaporator/air handler/furnace unit, the fan
On my Trane evaporator/air handler/furnace unit, the fan will not come on, though thethermostat/control panel in the thehouse … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Trane XE 78. Condenser works. A coil freezes. Blower won't
Trane XE 78. Condenser works. A coil freezes. Blower won't kick on. Manual blower (Fan on) works and kicks the blower on ok. As soon as A coil kicks in, blower quits. A coil keeps going and freezes. S… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
, I have a trane xt90 and the blower will not go on.
Hello, I have a trane xt90 and the blower will not go on. The flame goes on but no air movement. The red light blinks four times which tell me something about an open limit switch. I don't know what t… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i have a lennox furnace wont turn on and blinking only the
i have a lennox furnace wont turn on and blinking only the green light slowly model c50uh-48b-090-12, the induced motor is keep spinning and wont stop even its not calling for heat… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
Luxaire acclimate 9c furnace, about 4 years old Furnace
Luxaire acclimate 9c furnace, about 4 years old Furnace does not start when temperature dropped below thermostat setting Turned off power to furnace for a minute, then on again. The fan runs for about… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trane technician has serviced my A/C system including replacing
Trane technician has serviced my A/C system including replacing the thermostat and the circuit control board. However, the compressor continues to either "stick" on or off. If on, the compressor runs … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Trane unit model number 2TEC3F48A1000AA less than
I have a Trane unit model number 2TEC3F48A1000AA less than 2 years old. Initially I heard a humming sound from the unit in the garage. I went outside the house to check the fan element which was still… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi I have a trane uh2d120a9v5va (gas condensing furnace
Hi I have a trane uh2d120a9v5va (gas condensing furnace with variable speed), and my hvac tech service manger called ame and says that it was not installed properly. It is leaking water when it runs a… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
We are now required to replace both heat pump and air handler
We are now "required" to replace both heat pump and air handler on our residential system because of another change in freon. Furthermore, residential HVACs appear to be designed for obsolescence; for… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Trane model YCC036F1MOBC not coming on to heat house. Can smell
Trane model YCC036F1MOBC not coming on to heat house. Can smell "hot" something at registers but not blowing air. control panel says check filter. when put on cool also indicates fan is on but not blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My local trane dealer is fixing my TUY080R9V3A4 furnace purchased
My local trane dealer is fixing my TUY080R9V3A4 furnace purchased in August 1997 the blower fan quit working dealer says could be 3 things control, 137.22 modual 376.25 and fan motor 472.50 plus labor… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
On a an Infinity 96 system, the Infinity Control shows a Critical
On a an Infinity 96 system, the Infinity Control shows a Critical Alert Screen (Critical Malfunction Call Technician). The error code on the board is 41 (Blower Motor Fault). Aside from a dirty filter… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Ive gotten some quotes on replacing my furnace and A/C. Both
I've gotten some quotes on replacing my furnace and A/C. Both the Lennox and Carrier systems seemed pricier than the Trane options. I got a few Trane quotes since they seem to be popular in my area. 1… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
when my system is on cool, the fan will not run. Runs fine
when my system is on cool, the fan will not run. Runs fine in heat mode. Everything else cooling system wise checks out OK. Control Panel (EGC-2) led's indicate all is OK. Any thoughts?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our 4 year old Carrier system on our 2600 foot house has already
Our 4 year old Carrier system on our 2600 foot house has already had the motor replaced with one that now squeaks so loud you can hear it all over the house. Now both the inside and outside coils have… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Trane 2TTX4060 - inside blower will not come on even with fan
Trane 2TTX4060 - inside blower will not come on even with 'fan' switch on thermostat. The blower motor will cycle if the access cover is removed and the safety switch is depressed.… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hi I was told that my a/c unit--Trane 1400 series about 7
Hi I was told that my a/c unit--Trane 1400 series about 7 to 8 years old, needs a modullator for the blower motor in the air handler. Is the part (modullator ) under a 10 tear warranty ? If not can yo… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
my trane unit the blower fan is not turning on. the LED flashes
my trane unit the blower fan is not turning on. the LED flashes normal no call for heat. is this a problem with my thermostat or bad motor/starter cap? i need to fix myself because i cant afford to pa… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x