I have a carrier 48pgem06 4 ton roof top unit the cooling wont…

Customer Question
i have a carrier 48pgem06...
i have a carrier 48pgem06 4 ton roof top unit the cooling wont engage the fan comes on but the contactor wont pull in for the compressor i changed the batterys in stat transformer is working . could it be in the economizer?
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 43 minutes by:
6/18/2015
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to 2 hours help.

Up to 48 hours trouble shooting and coaching on repairs $38 additional if you approve it at that time.

If you can take a well focused, close up photo of the wiring diagram glued to inside of the units service panel, I can mark it up with ongoing trouble shooting directions.
You will need a $30 type class II multi meter.
Use the 'attach files' link at the bottom left your reply box for that.
.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Sorry thats not helping me
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
So far I am 100% sure that I have not helped you at all. We are at the information collections stage of the diagnosis aspect.
I need data on your system in order to assist you in trouble shooting.
I can modify the approach to suit your capabilities as you wish, the limits are your skill with the test instrument required and ability to take photo's and attach them here.
Tell me what aspect of any of that is outside of you capability range and we can go more appropriately from there.
.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a rooftop unit the tstat is calling for cool the
I have a rooftop unit the tstat is calling for cool the compressor is running the condenser fan is running but the blower fan is not I manually pushed the contactor down and the blower fan kicks on I … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
GPH1448H41 goodman 4 ton heatpump package compressor/fan not
GPH1448H41 goodman 4 ton heatpump package compressor/fan not engaging, 240v at contactor input reading 120v on each leg of contactor output but 0v nothing, natta zip whenvoltage is read across the two… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
What would make a rheem rbhc24j21sfb model blower work on On/cool
What would make a rheem rbhc24j21sfb model blower work on On/cool but nothing else engage and blower doesn't work or anything else on Auto/cool or heat/auto no contactor pulls in compressor or fan wor… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
working on a roof top carrier 4 TON A/C split unit. Model No.
working on a roof top carrier 4 TON A/C split unit. Model No. 38ARZ008. The condenser fan /compressor motor contactor keeps drropping out. however, when I jump R terminal to G, the contactor stays ene… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an older Carrier central air unit. My issue is that
I have an older Carrier central air unit. My issue is that when I turn the cool air switch on the 24 Volt wires that go out to the compressor that power the contactor switch on the compressor ground o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 18 tear old carrier gas furnace w 3 ton AC. When
I have a 18 tear old carrier gas furnace w 3 ton AC. When I call for the AC via the thermostat the indoor fan blower doesn't come on, and the outside condenser compressor unit doesn't work either. Whe… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a 17 y.o Carrier gas furnace w 3 ton AC. When I call
I have a 17 y.o Carrier gas furnace w 3 ton AC. When I call for AC thru the 'stat the indoor fan blower doesn't work and neither does the outdoor compressor/fan. When I open the indoor service panel a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Can a certified TRANE tech help me? 5V fuse keeps blowing
Can a certified TRANE tech help me? 5V fuse keeps blowing on Trane XR80 Setup: -Trane XR80 model DD1C120A9541A Furnace -Trane 2TXCC049AC3HCAA sitting on top of the XR80 (49,000 btu?) -Carrier 38TKB048… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 20Ton goodman hvac unit on my roof cooling our data
I have a 20Ton goodman hvac unit on my roof cooling our data center room. We have an economizer attached to the device. Its so cold outside all we need is to keep the fan on and it brings the temperat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello i am having a problem with a Mcquay spit unit. The
Hello i am having a problem with a Mcquay spit unit. The compressor is a CLJ18 and the interior unit is mwm020FkFAC. The a/c stop cooling, but the evaporator was working. I check the compressor that i… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
good morning , I talked with you before about a carrier 48tc
good morning , I talked with you before about a carrier 48tc 4 ton hvac unit , I thought I found the problem and fix it ... wrong. it is back to it 's old tricks, runs good on the heat cycle but as so… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Im working on a 3 phase, 7.5 ton, 2-stage Trane Condenser.
I'm working on a 3 phase, 7.5 ton, 2-stage Trane Condenser. It is a 2006 system-not too old. When in cooling mode condenser fan will come on, but not compressor. I've checked all electrical connection… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Bryant 6 ton rooftop unit model 580cpv072074 that
I have a Bryant 6 ton rooftop unit model 580cpv072074 that does not blow cold. The main blower [squirrel cage] cycles ok however no compessor. The contactor [s] seems to be ok as they move up & down. … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
i have a trane voyager roof top that keeps burning out num
i have a trane voyager roof top that keeps burning out num 2 contactor every once in a while constantly and doesnt seem to be getting enough powe to it because it chatters and wont close sometimes tes… read more
freon
freon
Owner
High School or GED
214 satisfied customers
I did a service call today on a Goodman gmnt080-4. It had errattic
I did a service call today on a Goodman gmnt080-4. It had errattic low voltage readings and I don't understand why. 24V coming out of the board and only 5V at the AC condenser outside. Sometimes the v… read more
Mr. Jeff Pearson
Mr. Jeff Pearson
Refrigeration Systems
Associate Degree
145 satisfied customers
Need help with Carrier package unit troubleshooting.
I have a rooftop Carrier package unit and cant get compressor(s) to run except when pushing contactors. Fan and blower come on and contactor makes about one second contact then releases. Checked limit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I replaced my contactor on my unit,it worked fine for three
I replaced my contactor on my unit,it worked fine for three weeks,now when the T-stat calls for cooling the contactor is clicking and will not engage, could this be the 24 volt transformer. The unit i… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
would like to replace roof top cooling unit 25 ton capacity
would like to replace roof top cooling unit 25 ton capacity higher efficiency with energy saving economizer. compare carrier ,trane american standard or any you recommend.this will be a cooling unit f… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x