I have a 3 ton goodman unit that is having a hard time starting when the unit is in the afternoon sun. Last night i measured the pressures at 125 low and 470 high with outside temp at 90 deg. Trying to find out why the outside unit is cycling in the afternoon sun?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 hours by:
6/17/2015
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified
Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Please provide all information I request as it makes it more difficult to troubleshoot something when I'm not there onsite. Essentially, you become my eyes and ears. Thanks for the opportunity to help. At the end of our dialog, you will have a chance to rate my service, but please wait until we are finished and you're satisfied you have all the information you need.
I'm sorry to hear about your problems with your unit. What kind of refrigerant is this? When you say it is having a hard time starting, what do you mean by that?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
The system is 410a. The outside unit tries to start then kicks out, I suspect on the high switch. If I mist the unit with water it will start. It starts fine in the morning and late afternoon. Just not in the heat of the day.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Let's try putting a spray attachment on your hose and thoroughly rinsing out the condenser fins. Start from the top and work downward all the way around the unit.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Did that with spray and comb yesterday
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
That pressure of 470 on the high side is way too high. Condenser fan running ok, blowing out the top?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Yes
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Was system ever low on charge? Charge added?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I had the coil replaced in Jan and the system was recharged and 410 was weighed in liquid. This is a TXV system bye the way.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
OK, whoever replaced the coil did not get all the air and moisture out of the system, hence the higher than normal head pressure. And this can cause all sorts of problems including compressor kicking out on O/L.
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
When a compressor gets head pressures that high it can cause it to go on on internal overload. It can also cause system not to work right. I would expect to see pressures more like under 300 on the high side.
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
For example, on an 80 degree day, head pressure with R410A should be around 235 PSI.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
The system was pressure tested with nitrogen and vacuumed down prior to charging. Would the air not affect the low pressure
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
No, it affects head pressure (high side pressure).
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
When they pulled a vacuum on it, did they use a micron guage?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Yes, but I do not remember what it read.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
OK< because even though the system was vacuumed, if the vacuum pump was defective or a hose had a leak, and no micron guage was used, it could still have air in the system.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
So what do you recommend?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
You have to get that air out of the system for your high side pressure to come back down to normal. If a shop did this repair, I would call them back and show them our conversation. This has to be corrected so that your system will run normally.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
So would I just pump the 410 into the compressor then pull a vacum down to what microns? Then release the 410 and check the pressures?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
we usually try to get to at least 100 microns, but at a bare minimum, 250 microns. I would also make sure a filter drier is installed in the liquid line.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
There was a new filter drier installed when we replaced the coil. So how would I complete the service I have pump, gauges and freon
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Pump the refrigerant into condenser, pull a vacuum to at least 250 microns, release refrigerant and recheck pressures. If the high side is still high, then you have other issues such as a bad condenser. But I suspect air was left in the system.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok, can I let you know if the pressures are still high to continue trouble shooting?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Yeah, if the pressures are still high, and a proper vacuum was pulled, then you have a bad condenser.
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Yes, good luck! Thanks for using Just Answer and please don't forget to rate my service as that's how experts get paid (thanks in advance for any bonus left). Feel free to post back with any additional questions.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Is condenser and compressor the same?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
No, the compressor is the black thing in the bottom of the unit. Condenser is the fins surrounding this compressor, although frequently the whole outside unit is called the condenser.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
So, how is it bad. Would it be leaking or what?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
If pressures were still high with a proper vacuum, then it could be plugged. If this is the case, it would need replacement.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
What if the wrong size orifice was installed?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
That would cause very low low side pressure (which you don't have).
Ask Your Own HVAC Question
Customer reply replied 2 years ago
How would I pump the 410 into the condenser?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
I'm going to opt out as I have to do some service calls. Please do not reply back or rate the question as this will slow things down. I will open up to other experts. Thanks.
Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to 2 hours help.

Up to 48 hours trouble shooting and coaching on repairs $38 additional if you approve it at that time.

Tim was looking at the wrong chart.
http://screencast.com/t/vaykE44ItK
That shows an example if the outside air is 95F, if its higher or lower temperature outside just adjust accordingly. On an 80F day the head pressure should be 340 psig for SEER 14 and 15 rated units.
---------
The cure for hard starting, is called a 'hard start kit'
https://www.youtube.com/watch?v=Sd1577g0A0I
That is a video on the topic. copy/ paste it into your browswer. You would use a kit rated for a 3 ton unit.
...........
We are on the honor system here. Please remember to rate my service before you leave today. If you need anything else, just let me know. You can continue asking follow-up questions within your agreed on limit at no additional charge.
.
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Thanks for your assistance here, Phil, but I have worked with R410A systems for years and have never seen head pressure of 470!!!
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
And, by the way, I also know how to read a temperature-pressure chart.
Ask Your Own HVAC Question
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
3,971 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,168 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Condenser contractor chattering is it bad? Just notice
We had very cold weather down to 10 degrees, fan not been running until today thouzght was running's. On heat strips. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat pump condenser coil are freezing up during this
my heat pump condenser coil are freezing up during this latest cold spell, can I thall them by using my aux mode … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have aTrane XE 1200 AC and as of yesterday the condenser
I have aTrane XE 1200 AC and as of yesterday the condenser fan and compressor won't shut off. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL #702H02997 THAT THE COMPRESSOR WAS RECENTLY REPLACED BUT i STILL HAVE A ISSUE WITH IT IT CRANKS BUT IT STOPS AFTER 45 SECONDS NEED HELPWITH THIS IS… read more
R G
R G
44 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,417 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x