New furnace, tech wired air conditioner lennox mod:hs16-211u-8p . Outside unit won't run. I think wiring in new furnace isn't right. Do you have a wiring diagram that shows correct connections?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 16 minutes by:
6/15/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to 2 hours help.

Up to 48 hours trouble shooting and coaching on repairs $38 additional if you approve it at that time.

The wiring diagram is glued to the inside of the blower cabinet cover.
The symptoms so far do not point to a thermostat or thermostat wiring problem but an ignition or flame sensing problem... there are various cause for that.
I am wondering what kind of an HVAC contractor would sell you a new furnace and wire it up, and leave it in not working condition. Are they licensed?
Tell me about that please, so that I can assist you in approaching this problem in the most effective manner.
We can go from there.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
The furnace runs for heat but will not run for air
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again, thanks for that.
Earlier you said that the furnace blower runs for 30 seconds then shuts off. .. that is not a thermostat wiring problem, *something else* is wrong.
Our options here are for me to catch a plane, and rent a car and then drive to your place and look at the unit.. and solve the problem in seconds, or ask you the questions I have and save the trip.
Only the latter approach works given the modest charge involved.
--------------
I need those questions answered... and I need to know if you have a multi meter or not and some skill with it do come tests at my direction.
----------------
In order to avoid wasting hours or days of your time and my time I need answers to the question of what the installing contractor has to say... verbatim. That tells me a lot about his character and what sort of other mistakes he may have made, such as venting the new furnace incorrectly (and unsafely).
------------
That will lead me to the most cost effective approach here... so I do need that data.
I also need a very well lit and well focused photo of the wiring diagram glued to the inside of the blower service door... taken from straight on, and up close...
and I need a photo of the printed circuit card inside that shows where there thermostat wires attach, behind the same blower service panel.
And I need to know if the unit that sits outside is a straight cooling unit, or a heat pump.
-----------------
You can use the 'attach files' link at the lower left of your reply box to attach those photos.
I need all of that data, without that I have no idea at all of what might be going on, or what mistakes might have been mad or how to help you resolve this.
Get all of that for me, please.
We can go from there, at that point.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I don't have a camera that i can down load to my p.c. I guess we are at a dead end. Thanks for trying to help. Have a good day. Clark
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,040
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,
If this is a gas furnace we should be able to get narrowed down.
Is red wire to r
white to w
yellow to y
green to g
and ac unit is to y and c?
Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Replaced batteries in my Honeywell TH5220D thermostat and now
Replaced batteries in my Honeywell TH5220D thermostat and now i cannot get anything (heat, cooling, or fan) to come back on. Checked the breakers and everything seems to be fine there.… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My goodman a/c is not working. There is no power to the thermostat
My goodman a/c is not working. There is no power to the thermostat either. Already checked the breakers and the power outlet for the fernace is working.… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,040 satisfied customers
I have a Lennox C33-60D-2F furnance. It is not producing heat.
I have a Lennox C33-60D-2F furnance. It is not producing heat. When there is demand for heat, the furnance blower starts, but there is never any demand for gas. The left LED blinks slowly and the righ… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
My furnace blower will not turn off. I removed the
My furnace blower will not turn off. I removed the thermostat but it continued to run. I had to run it off st the unit, is this a fan switch issue? Or could it be resolved with a new thermostat? … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,040 satisfied customers
Furnace blower will kick on for a minute or two then stop.
Furnace blower will kick on for a minute or two then stop. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
HVAC, 30 year old natural gas furnace, blower starts and
HVAC, 30 year old natural gas furnace, blower starts and heater relay on circuit board immediately clicks off. Does not trip circuit breaker. Thinking bad relay or over amp load condition, maybe dead … read more
Bill
Bill
Service Mgr
100 satisfied customers
Rheem furnace blower runs on low but will not run on high
rheem furnace blower runs on low but will not run on high furnace goes off on high heat limit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,804 satisfied customers
My Rudd furnace blower vibrates the entire house. Research
My Rudd furnace blower vibrates the entire house. Research indicates a motor/fan set screw may need tightening, but I can't see one. Where is it found? Can it be adjusted without removing the motor?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem furnace wont light with doors on
Rheem furnace won't light with doors on… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Goodman dependable ninety two furnace model number
I have a Goodman dependable ninety two furnace model number GMPN080-4. The other day the blower stopped working. My air conditioner turns on, I can hear the R22 flowing through the line to the furnace… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
FURNACE BLOWER FAN DOES NOT WORK. WHAT MAY BE THE PROBLEM
FURNACE BLOWER FAN DOES NOT WORK. WHAT MAY BE THE PROBLEM?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
furnace blower will not turn on. It sounds as if it want to
furnace blower will not turn on. It sounds as if it wan't to start but doesn't.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Why is Bryant gas furnace not igniting after power outage?
Why wont the Bryant gas furnace ignite after a power outage?… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
How many Flame Sensors are there on a ruud silhouette ii plus
How many Flame Sensors are there on a ruud silhouette ii plus 2 lxe? I know the one one left side is the Flame Sensor, but is the one on the right side also a Flame Sensor.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.