I installed new heil 2ton heat pump 410a. flushed lines and…

Customer Question
I installed new heil 2ton...
I installed new heil 2ton heat pump 410a. flushed lines and installed new liquid line drier. neat day owner called said unit was cutting on and off. figured it was txv so i installed new one. 2 days later called back doing same thing. went back changed drier, 3 days later called back doing the same thing. i'm stuck.
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
6/15/2015
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,081
Experience: Furnace, A/C and heat pump specialist.
Verified
Hello. My name is ***** ***** I'll do my best to help. Let's get started and see what we can do.When you arrive are pressures normal and can you get it to cut off while you are there?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
High liquid line pressure. Unit cutting on and off when I arrive
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
Is suction pressure low also and is outdoor fan operating?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Suction line normal high side pressure gets in the 500 psi area
Customer reply replied 3 years ago
Outdoor fan runs when unit runs
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
Did you add any refrigerant at time of install?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Yes
Customer reply replied 3 years ago
Charged unit by sub cooling
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
My first suspicion is over charge.If the txv were an issue I would think the suction would also be low as refrigerant could not get back.R410 since it leaves the tank liquid goes in much faster than the old R22 and I myself had overcharged a couple because of this.2 to 3 lbs can go in before you know it. I would recover the refrigerant and see if maybe overcharged.May be able to pull out a lb or so and see if the suction changes drastically or not.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
When you charge using sub cooling unit shouldn't be over charged.
Customer reply replied 3 years ago
Factory sub cooling is 13
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
Was this a new complete system or swap out? If swapping out a system and ductwork not properly sized causing improper air flow, trying to get the superheat and sub cooling right can often lead to improper charge.The charts are based on system operating with designed air flow and equalized system.If this is the case, the sub cooling and superheat will also change.Are they still showing correct at this point?
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Suction side 137 liquid 339 sub cooling 14
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
Hmm. Sounds like at the moment, all is good.As long as fan is not stopping,not sure what can be changing on you.I will opt out and see if other experts may have suggestions.Good luck with this.I will follow the post to see what you find.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Thanks
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
THanks for letting me work with you.I have opted out of the question to see if perhaps other experts may have more information and can assist.Please do not rate or reply as that will send question back to my desk.Please stand by to see if another expert can assist further.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,081
9,081 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The head pressure slowly raises as the suction pressure
The head pressure slowly raises as the suction pressure stays steady in the cooling mode … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,344 satisfied customers
I have a 113 condenser and the suction pressure is only 15
I have a bryant 113 condenser and the suction pressure is only 15 psi and the liquid line is 198 #. is there a problem with the txv? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
What is the suction side pressure to be on a MR24C3F it's
What is the suction side pressure to be on a MR24C3F it's the only port and after a leak was repaired and everything vac down to 500M and new charge weighed in. It runs cool but not cold … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
1.5 ton system brand new, lineset length is 60feet,
1.5 ton coleman system brand new, lineset length is 60feet, subcooling is 3 superheat is 72, suction pressure 40 head pressure 220 factory charge is 5 ibs 11 oz, added 1 ib 6 oz for lineset length, ev… read more
hvacdave84
hvacdave84
53 satisfied customers
I am on a service call to a system that is a brand new
I am on a service call to a system that is a brand new system. It's less then a month old. I just got a call saying that the system isn't working and I figure I was going to have a leak in the system … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Refilling a unit 1YO that had a very small leak but never
Refilling a unit 1YO that had a very small leak but never found it so I vacuumed and installed ProSeal super stop leak, then I started the unit and I refill with a new 25lb R410A but after several min… read more
Bill
Bill
Service Mgr
103 satisfied customers
I have a Trane XL13xi outdoor unit that has been not keeping
I have a Trane XL13xi outdoor unit that has been not keeping up with the thermostat for the past 3-4 days. It's been unusually hot but I'm unsure if I need a charge or the compressor is going out. The… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Carrier, 9 yr old 3 ton residential heat pump (R410a)....not
Carrier, 9 yr old 3 ton residential heat pump (R410a)....not cooling. Suction pressure drops rapidly to about 10 psig when I turned it on. High side pressure only reached about 300 #. Compressor was v… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
My outside HVAC compressor is making a vibrating noise that
My outside HVAC compressor is making a vibrating noise that I need help diagnosing. Has been going on for a couple of weeks now. Unit works but the noise is concerning. I have a video recording of the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a new installation of a heil heat pump heat pump
I have a new installation of a heil heat pump heat pump model # NXH536000A air handler model # FEM4X3600A aux. heater model # EHK15AKB thermostat Honeywell RTH 2300/RTH221 SERIES when attempting to st… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
This question is for Phil only please *** It's getting ready
This question is for Phil only please ***It's getting ready to warm up here in Virginia. It is supposed to be hitting 80 degrees today. You said previously you wanted the temperature in the house to b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I installed a walk in cooler,compressor wont kick off on low
I installed a walk in cooler,compressor wont kick off on low pressure cut out,pulls down to 0 set to cut out at 10psi? … read more
ApplianceTech
ApplianceTech
President
Associate Degree
1,735 satisfied customers
Billy, I have had the Fedders (remember them) 15K Split HP
Hi Billy, I have had the Fedders (remember them) 15K Split HP for a few years. Last year I had only an 8F inside temp spred so I put a little R410a in to match the gauge outside temp. Inside temperatu… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a rheem unit. Cannot get supply duct temp below 62
I have a rheem unit. Cannot get supply duct temp below 62 degrees 410-ref? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having trouble getting more that 10 degrees of cooling between the return and the vent. I've adjusted the charge to the spec in the manual for a pi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
If the reversing valve has a internal short like you said is
if the reversing valve has a internal short like you said is that why my suction psi is ;low… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Is the head pressure & discharge pressure same thing? And
Is the head pressure & discharge pressure same thing ? And what about back pressure & suction pressure !… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x