The emergency heat light is blinking on my thermostat when…

Customer Question
The emergency heat light is...
The emergency heat light is blinking on my thermostat when it is in the cooling mode (heat pump)and the outside compressor unit shuts down while the inside fan blower keeps going. The manual for the system (Coleman Evcon 98 vintage) indicates that this light will blink if the safety lock out device opens because of either the high temperature switch or the high pressure switch opening. The tech who looked at it seemed to think that the problem is with the thermostat. The freon was within the normal operating parameters. I am leaning towards the safety lock-out device (whatever that looks like) being bad. What is your opinion?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
6/13/2015
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,043
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
hello,
The emergency heat code is for when you are heating and the heat pump fails or locks out because it cant keep up.
If this is happening in COOL mode then you have an issue with the thermostat.
The thermostat code is different than the furnace code. Basically the thermostat is thinking it is in heat and the heat pump couldnt keep up.
Looks like you will need to replace the thermostat
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I agree with your logic, but the manual does say something different: "Safety Lock-out: This device opens the circuit to the compressor contactor, stopping the compressor in response to either the High Pressure or High Temperature limit switches opening. The compressor will remain off, even though the limits close and will start up only when the Lock-out is reset. The Lock-out also illuminates the Emergency Heat Indicator. To reset the Lock-out, turn the indoor thermostat's System to "OFF" momentarily then, back to the selected mode. The system will start up after the 5 minute delay period is complete..." This is exactly what I have to do to get it back into the cool mode. However, it cycles this way maybe several times in maybe in a two hour period. So I have to constantly watch to see if the light comes on. Whenever it does, the outside unit is completely off, but the inside blower fan is still going. Nothing is coming out of the floor vents except recycle indoor air of whatever the room temperature is.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
OK...If the unit were in high pressure lockout...
either the outdoor coil would be plugged
the fan in top would not be working
it would be in a very hot spot during a portion of the day...and have a dirty coil
So it is something you would have to give input on..
when this occurs is at the same time of day....is it over 100f at condenser?
Is the outdoor coil coated or plugged?
Is the outdoor fan running reliably?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
We have had some rather hot days as of late in the lower 100 degree range, but the outside portion of the unit is in the shade after 10:00 am for the rest of the day. When it is running, everything seems fine. Got lots of cool air coming out of the floor registers and the house cools down well. The manual indicated that this Emergency Heat Light will turn on if there is not proper maintenance. Further into the manual it indicated, "If the emergency heat indicator light turns on with the system switch in the HEAT or COOL position, then the following maintenance problems could be the cause." It goes on to list a bunch of stuff regarding block ducts, dirty blower wheel, indoor and outdoor coils, dirty filter, registers not opened or blocked. I have checked all of this and cleaned everything up and the issue is the same. The outdoor fan is running good until the emergency heat light comes on at the thermostat. As soon as the emergency heat light comes on, the outside fan and compressor shut down.
Customer reply replied 2 years ago
I did not hear back regarding my last reply above regarding your questions above that. Please respond. Thanks.
Customer reply replied 2 years ago
Still waiting!
Customer reply replied 2 years ago
I went ahead and replaced the thermostat and the problem is still the same.
Customer reply replied 2 years ago
I fixed it myself. Turns out the compressor fan was not turning fast enough to get the proper flow of air through the coils. Thus, it was tripping either the high pressure or high temperature limit switch. I had my wife turn it off and on a couple of time from inside the house via the thermostat and I noticed how the fan started up really slow and the volume air didn't seem to be what I used to remember it was. It would maybe cycle three or four times before the limit switch would cut the power to the compressor and compressor fan. So I replaced the motor myself (not hard to do) and went ahead and replaced the associated capacitors just in case they were problematic too (only a little over $30 for them so worth it). Everything is working fine now and I got a new thermostat in the process which I really didn't need, but that was only another $30 too on-line.
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,043
23,043 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
do you have a trane heat pump error code chart
do you have a trane heat pump error code chart… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,043 satisfied customers
central air just started making a VERY LOUD sort of humming
central air just started making a VERY LOUD sort of humming sound - not rattling rt banging..have changed the filter...what is the problem? We have lived here for 6 years and have never had a problem … read more
Ryan V.
Ryan V.
UA Local 350 Journeyman
High School or GED
6 satisfied customers
I have a rheem prestige series furnace, that is flashing code
I have a rheem prestige series furnace, that is flashing code "66". I have replaced the filter, hosed out the A/C unit, and checked the internal blower motor fo operation, and it spins freely. What el… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have an Amana condensing unit #RCB36B2A the start
Hi I have an Amana condensing unit #RCB36B2A the start capacitor failed its 19 yrs old and I cant read the numbers to replace it can you give me the start capacitor info to replace it? … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Inside uint blowing but outside condenser not coming on.
inside uint blowing but outside condenser not coming on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE ERROR CODE I AM GETTING SAYS "EE" =compressor relay contacts welded … read more
Bill
Bill
Service Mgr
100 satisfied customers
The condensate pump on my xe90 is cycling on and off. 1st
the condensate pump on my xe90 is cycling on and off … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Condenser fan going counterclockwise. Just notice it. put a
just notice it. put a new motor in it , but has differ color wiring … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,043 satisfied customers
HVAC question I have a Carrier condenser unit that was
HVAC question I have a Carrier condenser unit that was running this morning when the heat was on in the house. The thermostat was set for heat? Model number 38TGO30300. I through the outside breaker b… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Looking to buy replac ement condenser to model nac036akc3
Looking to buy replac ement condenser to model nac036akc3 serial e040516483 … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
How do I determine the reversing valve polarity of any given
How do I determine the reversing valve polarity of any given heat pump system?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,043 satisfied customers
where do I hook the two wires from the condenser to the fu
where do I hook the two wires from the condenser to the furnace… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,043 satisfied customers
if my goodman heat/pump / air conditioner outside unit quits
if my goodman heat/pump / air conditioner outside unit quits in high heat conditions what part likely went out… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My heat pump mini-split unit has stopped producing hot or cold
My heat pump mini-split unit has stopped producing hot or cold air. The indoor fan still works, but it just blows unheated / uncooled air. It shows a P4 error code on the indoor unit. A technician che… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Fault code 179 appears on my INFINITY thermostat for
Fault code 179 appears on my INFINITY thermostat for INFINITY series condenser. Turning power on/off did not re-start system. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
How do you bypass defrost control board to test if it is reason
How do you bypass defrost control board to test if it is reason why no 24 V at contactir… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,043 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x