The emergency heat light is blinking on my thermostat when

Customer Question
it is in the cooling...
The emergency heat light is blinking on my thermostat when it is in the cooling mode (heat pump)and the outside compressor unit shuts down while the inside fan blower keeps going. The manual for the system (Coleman Evcon 98 vintage) indicates that this light will blink if the safety lock out device opens because of either the high temperature switch or the high pressure switch opening. The tech who looked at it seemed to think that the problem is with the thermostat. The freon was within the normal operating parameters. I am leaning towards the safety lock-out device (whatever that looks like) being bad. What is your opinion?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
6/13/2015
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
hello,
The emergency heat code is for when you are heating and the heat pump fails or locks out because it cant keep up.
If this is happening in COOL mode then you have an issue with the thermostat.
The thermostat code is different than the furnace code. Basically the thermostat is thinking it is in heat and the heat pump couldnt keep up.
Looks like you will need to replace the thermostat
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I agree with your logic, but the manual does say something different: "Safety Lock-out: This device opens the circuit to the compressor contactor, stopping the compressor in response to either the High Pressure or High Temperature limit switches opening. The compressor will remain off, even though the limits close and will start up only when the Lock-out is reset. The Lock-out also illuminates the Emergency Heat Indicator. To reset the Lock-out, turn the indoor thermostat's System to "OFF" momentarily then, back to the selected mode. The system will start up after the 5 minute delay period is complete..." This is exactly what I have to do to get it back into the cool mode. However, it cycles this way maybe several times in maybe in a two hour period. So I have to constantly watch to see if the light comes on. Whenever it does, the outside unit is completely off, but the inside blower fan is still going. Nothing is coming out of the floor vents except recycle indoor air of whatever the room temperature is.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
OK...If the unit were in high pressure lockout...
either the outdoor coil would be plugged
the fan in top would not be working
it would be in a very hot spot during a portion of the day...and have a dirty coil
So it is something you would have to give input on..
when this occurs is at the same time of day....is it over 100f at condenser?
Is the outdoor coil coated or plugged?
Is the outdoor fan running reliably?
Ask Your Own HVAC Question
Customer reply replied 2 years ago
We have had some rather hot days as of late in the lower 100 degree range, but the outside portion of the unit is in the shade after 10:00 am for the rest of the day. When it is running, everything seems fine. Got lots of cool air coming out of the floor registers and the house cools down well. The manual indicated that this Emergency Heat Light will turn on if there is not proper maintenance. Further into the manual it indicated, "If the emergency heat indicator light turns on with the system switch in the HEAT or COOL position, then the following maintenance problems could be the cause." It goes on to list a bunch of stuff regarding block ducts, dirty blower wheel, indoor and outdoor coils, dirty filter, registers not opened or blocked. I have checked all of this and cleaned everything up and the issue is the same. The outdoor fan is running good until the emergency heat light comes on at the thermostat. As soon as the emergency heat light comes on, the outside fan and compressor shut down.
Customer reply replied 2 years ago
I did not hear back regarding my last reply above regarding your questions above that. Please respond. Thanks.
Customer reply replied 2 years ago
Still waiting!
Customer reply replied 2 years ago
I went ahead and replaced the thermostat and the problem is still the same.
Customer reply replied 2 years ago
I fixed it myself. Turns out the compressor fan was not turning fast enough to get the proper flow of air through the coils. Thus, it was tripping either the high pressure or high temperature limit switch. I had my wife turn it off and on a couple of time from inside the house via the thermostat and I noticed how the fan started up really slow and the volume air didn't seem to be what I used to remember it was. It would maybe cycle three or four times before the limit switch would cut the power to the compressor and compressor fan. So I replaced the motor myself (not hard to do) and went ahead and replaced the associated capacitors just in case they were problematic too (only a little over $30 for them so worth it). Everything is working fine now and I got a new thermostat in the process which I really didn't need, but that was only another $30 too on-line.
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
22,767 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Water found under condensate tank? Just discovered, not sure
Just discovered, not sure how bad, so far water only found under tank about 3/4 way over and about 2 inches out from wall. … read more
Chad DeYoung
Chad DeYoung
8 satisfied customers
I have a condensing furnace, MN G51MP- 48C- 090 -06 this
Hi , i have a condensing furnace, MN G51MP- 48C- 090 -06 this furnace gives trouble every year at some point. flash code says condensation is backed up or not enough combustion air or pressure switch … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My condenser trap on my Potterton Combi Promax is full i
Hi Pearl my condenser trap on my Potterton Combi Promax is full i have just discovered this is the reason why i had a pool of water on my worktop , how can i deal with this please … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,159 satisfied customers
I changed the condensation pump on my gas furnace and now
I changed the condensation pump on my gas furnace and now the furnace won't start. The old pump was direct wired through the kill switch and the new one had a plug. The new one also had a yellow wire … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My 5 ton condenser unit located on a concrete slab outside
My 5 ton condenser unit located on a concrete slab outside my house was damaged in the Hurricane Harvey flood. It looks like I need a new condensing unit. I just received a quote of $4,000 for a new 4… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
MONROVIA CA AND I NEED THE CONDENSER FAN AND THE FAN MOTOR
I'M IN MONROVIA CA AND I NEED THE CONDENSER FAN AND THE FAN MOTOR FOR THIS MODEL. NAC048AKC3 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,767 satisfied customers
What is the best way to channel off the condensation water
What is the best way to channel off the condensation water on outside heat pump? When it is heating a lot of water is accumulating. Our lowest temp has only been 54 degrees outside so shouldn't be ove… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser fan running compressor not running or humming.
Condenser fan running compressor not running or humming. Checked capacitor it's good. Checked contact it's also good. Pills in by its self and has just over 240. Could it possibly be something in the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
The inside fan is not running, condenser will run, 3 days,
the inside fan is not running, condenser will run, … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,767 satisfied customers
C wire problem. A day. Condenser not turning on with
Condenser not turning on with additional wire to c terminal on fan unit … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I'm in the process of installing a Goodman 2 ton condenser
Good morning! I'm in the process of installing a Goodman 2 ton condenser (GSX140241) however I have a few questions. 1. On the name plate it states that this unit requires 15 amps. Should I connect th… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question