Hi. One of the blades on my ac condenser fan had a crack. the crack split the blade and caused the blade to lodge in the protective grill. i only discovered this after the house started to get a little warm. neither the compressor nor fan come on when the system is "ON". Cause/suggestion? BTW i did replace the 40 A fuses
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 3 years ago
(Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from yo. Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 25 minutes by:
6/11/2015
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome!
I am assuming you replaced the fan blade, got the right one that has the same blade curve and rotation as the original (and draws air across the condenser coil)
There are manual high pressure cut out switches on a majority of these systems, especially the older ones, that trip when there is no air flow.
The reset button is generally behind a 3/4" hole in the AC unit cabinet, or it is inside the electrical controls box in the unit itself.
Look for that, tell me how it goes... we can proceed from there as necessary without a time limit unless you rate negatively, that closes the question.
-----
We are on the honor system here. Please remember to rate my service before you leave today. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge.
Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
see private contact info in the section attached below please.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
"contactor
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
Hello again, that looks like a temperature sensor that with a spring loaded strap on the back for attaching to the outside oil... it seems to be removed from its proper location. It is not the contactor.
If you can take a very well focused close up of the wiring diagram glued to the inside of the electrical service panel, and post it here I can locate the high pressure cut out switch for you.
Use the 'attach files' link at the bottom left of your dialog box to attach the picture.
.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Would you mind calling me...I have a couple of questions I'd rather talk about. I paid for Live service and sent you my phone. Thx
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
Thanks.
I have not gotten your phone number yet for some reason, see my email in the box **below** this dialog box, and send me an email with your phone number in it.
----------
http://screencast.com/t/dLAWKmgSQS
Press the reset for 1 second, with the power off, tell me if the unit runs when you turn the power back on when set for cooling and down to 60F.
Next clean the outside condenser coil regardless if it looks dirty or not.
https://www.youtube.com/watch?v=vDtT6hSpV4s
thats a video on how its done, you can buy the foaming cleaner at Home Depot, Lowes or most larger hardware stores.
.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
9,880 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,880 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
After a power outage our AC is not blowing cold air. The
After a power outage our AC is not blowing cold air. The outside fan in the AC unit is operating but when the thermostat is changed to "COOL" nothing happens. … read more
canuck the pro
canuck the pro
294 satisfied customers
I have a heat pump (split unit) and my goodman condenser
I have a heat pump (split unit) and my goodman condenser make a loud noise on start up … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My furnace blower will turn on but the AC condenser wont. I
My furnace blower will turn on but the AC condenser wont … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
I just had an older Goodman mini-split installed. 20CR air
Hi, I just had an older Goodman mini-split installed. 20CR air handler & HDP 18-1A condenser (R22). Works fine in both heating & cooling but the fan runs continuously. Is this normal? Tkxxx Bob Miller… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a waiting for equipment status on my new honeywell
I have a waiting for equipment status on my new honeywell thermostat … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My central air conditioning is not working, checked circuit
My central air conditioning is not working, checked circuit breakers, changed batteries in my Honeywell thermostat, outside compressor does not turn on nor does the fan… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a AOSmith Pro Max md. ocv90 100 and we have been getting
I have a AOSmith Pro Max md. ocv90 100 and we have been getting carbon monoxide when AC runs and heater runs at same time the water heater has its own chimney and its 3" pipe its 8 years old.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
All of a sudden both of my Venstar thermostats both stopped
All of a sudden both of my Venstar thermostats both stopped working. Tried to reconnect to wifi but it does not accept the WIFI connection. Help ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We are getting error code 91. Our american standard heat pump
We are getting error code 91. Our american standard heat pump and furnace are not working - this just happened. Any ideas? I have tried resetting the breaker...… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
1200xl trane ac............loud humming noise in airhandler
1200xl trane ac............loud humming noise in airhandler and compressor unit when unit is turned on. Handler fan will turn on but compressor don't. what is your expert opinion?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
Carrier heat pump question: AC stops blowing cool air...notice
Carrier heat pump question: AC stops blowing cool air...notice that the compressor is not running. Turn off power to compressor, set all thermostats to off and unplug molex connector to circuit board … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
York Furnace model# ***** When only the fan is on,
York Furnace model# ***** When only the fan is on, the speed is normal but when turned to cooling mode, the fan speed decreased significantly, resulting in the system icing up. How to increase CFM by … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Billy, I have a 1992 Payne VCD0060. I had a full service cleaning
Billy, I have a 1992 Payne VCD0060. I had a full service cleaning done on Friday. A/C worked great. I did see initially the guys had a problem with start up but then I went back in. Today, it will not… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Having trouble wwiring from outside condenser &t-stat to
having trouble wwiring from outside condenser &t-stat to Goodman natural gas hot-air wiring to work right--I wired & bunit kept on rinning constantly for a day--need help please! *************… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Honeywell RTH 8500D. I usually shut it down (off)
I have a Honeywell RTH 8500D. I usually shut it down (off) for the summer. In past years the thermostat would still show the time and temperature, humidity etc. Now it is blank. I get to DC voltage re… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My AC just went out. I have 2 zones and 3 thermostats,
Hello my AC just went out. I have 2 zones and 3 thermostats, all thermostats are blank (no battery back up), breaker is on and fine, there seems to be no power going to the main units inside including… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
Why can't we get this 3 ton York air handler board to communicant prop
Why can't we get this 3 ton York air handler board to communicant properly with a new 3 ton lennox heat pump/ac condenser board. when we call for ac we get heat mode.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a furnance control, part mnumber..HK42FZ012 AND THE
I have a furnance control, part mnumber..HK42FZ012 AND THE MOVE THE DIAGRAM OF RUN IT's ate 3 little red bboxboxrsconectorees… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x