I have the same No power (display) on my thermostat problem…

Customer Question
I have the same No...
I have the same No power (display) on my thermostat problem as the thread I was just reading. My downstairs thermostat works fine. Upstairs thermostat is blank. They are identical, so I switched them and the upstairs thermostat works fine downstairs. I have checked all breakers I can find. What else can I look for?
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 41 minutes by:
6/9/2015
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,077
Experience: Furnace, A/C and heat pump specialist.
Verified
Hello. My name is ***** ***** I'll do my best to help. Let's get started and see what we can do.
1. Do you have 2 separate systems for upstairs and down?
2.What is model on indoor unit upstairs?.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
Yes we have 2 separate systems. 2 furnaces in the attic and 2 air conditioners outside. Not sure what indoor unit upstairs means. Do you mean the thermostat?
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
The model on the furnace that the thermostat controls. I want to pull a manual and see if maybe there is a small 3 or 5 amp auto type fuse in furnace that could be the problem.If we are not getting a display, we probably are not getting power from the furnace.
Ask Your Own HVAC Question
Customer reply replied 3 years ago
I will have to pick this up later. I am not at home and do not know the model of the furnace. No one is home to go in the attic and check the model.
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
THat is fine.Just come back to the question and we can go from here. While in attic go ahead and remove blower panel and see if there is a small auto type fuse plugged onto furnace control board and check to see if it is blown. See links below:
http://i.imgur.com/kYe4Epz.png
http://i.imgur.com/zOpm9aP.png
Ask Your Own HVAC Question
Customer reply replied 3 years ago
ok thank you. talk later.
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
Look forward to hearing back
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,077
9,077 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a lp gas control (thermostat control? that was in my
I have a lp gas control (thermostat control? that was in my water heater that I installed in 2003 for my vacation home. I use it only during the summer. The only numbers on the unit are 75 0r 76164007… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I, I installed a furnace control Board part # 62-24084-82.
I, I installed a furnace control Board part # 62-24084-82. It cycled once and will will not cycle again. all the controls are ok after checking them. any Ideas? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a line volt thermostat controlling 1/2 of a 120 v.
I have a line volt thermostat controlling 1/2 of a 120 v. outlet that runs a pump on my heating system. What do I need to change it to a low volt stat for more accurate control and possible setback op… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I'm tried to install a new Eecho 4 thermostat controller and
Hi. I'm tried to install a new Eecho 4 thermostat controller and now I have no power coming from the furnace. I think it should be 24V. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My carrier thermostat control 's display just went blank. I
My carrier thermostat control 's display just went blank … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gas boiler thermostat controles circulating pump hot water
gas boiler thermostat controles circulating pump hot water remains hot and is distributed by convection, how correct … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a -Rodgers model 1F97-371 thermostat controller. How
I have a White -Rodgers model 1F97-371 thermostat controller. How do I get it out of the lock mode?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Is there a zigbee thermostat controller for a gree ptac? I'm
is there a zigbee thermostat controller for a gree ptac? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Where is the fuse in my hvac unit. The thermostat control
Yes. The thermostat control shorted out. I suspect a blown fuse.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I need to replace a Zone Perfect Plus thermostat controlling
Hi, I need to replace a Bryant Zone Perfect Plus thermostat controlling two zones. My contractor is quoting $1300 plus to replace it and says there are no cheaper alternatives. Is there any simpler af… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
What is the best attic exsaust fan thermostat controlled for
What is the best attic exsaust fan thermostat controlled for an 1800 sf house? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My honeywell thermostat control panel displays only 5 empty
My honeywell thermostat control panel displays only 5 empty boxes on the bottom of the display screen … read more
airheatman
airheatman
HVAC Technician
9,077 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently replaced my furnace control board. The furnace is
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Boar… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an amana furnace control board with an led flashing 3
I have an amana furnace control board with an led flashing 3 times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need help with my -Rodgers furnace control board 50e47-060
I need help with my White-Rodgers furnace control board 50e47-060 on a Trane furnace. It has a blinking red light. On the unit it says " steady red light- replace control, blinking red light-referred … read more
type2technician
type2technician
253 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.