I just installed a zr42k5epfv800 comp. in a customers heat

Customer Question
pump on Friday. After the...
I just installed a zr42k5epfv800 comp. in a customers heat pump on Friday. After the vaccuume held for four hours I weighted the charge in. The comp. did not sound right and it would not pump. The charge leveled out on my gages and did not move. This is the second comp. I have installed in this same unit in a week. The first one shorted to ground in three days. I have installed a lot of comp. in my life time, this is the first time I have had this kind of problem. Am I over looking something. Does copland ship their comp with oil in them.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
5/31/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,152
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome! Your question will be answered in detail. UP to 48 hours step by step coaching on diagnosis & repairs $38 additional.
Copeland and all other mfgr ship their compressors with oil in them..
Tell me what you use for a vacuum gauge, we can go from there.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I used my standard vacuum pump and my standard a/c gages.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again,
you really need a micron gauge to check vacuum and leaks properly by the pressure method. however what you are doing has worked for the previous 50 years. (soap bubbles combined with an electronic leak detector is best or a halide torch on refrigerants with chlorine atoms in them).
Minor leaks would not cause the problems you have seeing.
It is rare that a compressor is bad out of the box... however if you have been in the business a long time and you say the compressor didn't sound right, there very well may be a problem with it.... unless it is a 3 phase unit and it was running backwards. (those make very loud racheting noise in that case)
Lets make sure you are on 230v single phase or 230v 3 phase... and what phase the compressor is rated for.
We can go from there.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
The data sheet that came with the comp. states that It is a 230 volt single phase comp.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again,
You have quite an unusual situation there.... when you checked the grounded compressor, was that done with all of the wires disconnected from it? tell me where each probe of your meter was when you did that check... and if the read was the same as touching two test probes together or no, Please be as overly specific as you can.
tell me in great detail what you mean by 'the charge leveled out on my gages and did not move' please.
We can go from there.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
The first comp. tripped the breaker after the second night, however there were storms in the area and the power to the house went off and on several times during the night. I placed my leads on each terminal to make sure there was not a short between the windings. I then checked each terminal to ground. I found the short between common and ground. After weighing in the charge and starting the unit my gages showed 100 psi on the high and low side.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Thanks, ***** ***** to be sure that when you did the electrical checks on the compressor, that all of the wires on the compressor were **removed..
if they were removed, then the compressor is burned out. Lightning strikes can cause such damage and also blow the run capacitor up.
-----------
If the 100 psig low and high side reads, occurred when the compressor was actually running, and you verified that by measuring amperage on the Common wire that runs to the compressor...then the compressor valves are bad ....or the reversing valve is stuck half way between heating and cooling mode... or you had left one or both of gauge valves open on your service gages when reading the gages (that bypasses the low side to the high side.)
-----------
Try operating the reversing valve by having someone else change the thermostat settings between heat and cool and setting the temperature to extremes in each case ..... as you stand by the unit and listen for the characteristic gushing sound as the 4 way valve reverses.
let the system run for 60 seconds before the thermostat is switched between heat and cool.
Tell me if there is a 5 minute time delay or not.
We can go from there.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
There is a delay in starting, the comp. plug was removed and I took my readings from the comp. terminals. ON the second comp. my gages were closed. The comp will only run for about 30 seconds before turning off. I'm getting 223.6 volts to the comp. Its like the internal over load in opening. This may be a new problem. Yesterday it was not doing that.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Thanks
Use a clamp around type amp meter to check the amps on common to the compressor first, then start, then run... do that in the 30 seconds before it shuts off. There could be a failed connection at the plug in on the compressor.
I need the amp readings and the full load amp number from the unit name plate for the compressor (FLA or RLA, not LRA)
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
It's drawing 64.3 amp at start up on common and start, 5.1 on run. I checked the plug and it checked out all right. I ohm out the comp. and it shows a short between the windings. I wired the plug that attaches to the comp as follows start to l2, common to l1, and run to the herm side of cap. as it shows in the diagram. Did I do something to short this comp.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Thanks.
64 amps is locked rotor amps, indicating the compressor is mechanically frozen, or that its run capacitor is bad not connected.
I want to tell you something about brain function...if you use abreviations of any sort, even known abreviations. it causes the brain to abandon its linear thought process, a process needed, as it tries to decide what among many options an abreviation stands for.
It has to decide if 'comp' is short for compressor, or compare, or comprehensive or whatever... the more abreviations the more muddled it gets, even though you and I are fully aware of what 'comp' means here... it gets exponentially worse with the more abreviations used.
Compressor motor terminals are C, S and R... (common, start and run) I do not know what you mean be the |2, and |1 terms. I have not seen that so far in 51 years working on these units.
---------
For now to avoid confusion, I need the amperage reads on all three wires that run to the compressor when it tries to start, if there is no amp read on the start (S) terminal wire running to the run capacitor, we have a bad run capacitor.
Let me know, we can go from there.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
start on the compressor is drawing 64.3 amps, common on the compressor is drawing 64.3 amps, run on the compressor is drawing 5.1 amps. The three wires coming from the compressor is wired as follows, start is wired to the line 2 side of the contactor, common is wired to the line 1 side of the contactor, and run is wired to the hermetic side of a dual capacitor. The capacitor has a rating of 55uf for the hermetic side and 5uf for the fan side. I have checked the capacitor and it is fine. Above you stated that start went to the run capacitor please verify this. The diagram shows run winding to go to the capacitor. The capacitor is also rated for 370 volts.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Thanks for the excellent detail.
The compressor is wired incorrectly.... the condenser fan may be wired incorrectly at this point also.
Line 1 runs directly to C on the compressor and also to the C terminal on the run capacitor.(not the herm terminal on the capacitor... C is the middle terminal on the capacitor.) Let that soak in for a while.
The Herm terminal on the capacitor runs to S on the compressor (that is the start winding in the compressor.
Line 2 on the contactor runs to R (run winding) on the compressor.
---------------
Attach a well focused, well lit photo of units wiring diagram, taken close up and straight on... using the 'attach files' link at the bottom left of your reply box, so that I can verify that.
We can go from there.
----------
Please rate my work so far, so that I can justify spending time above and beyond what is allowed for by a simple answer.
We are on the honor system here. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Phil, I think you are right, I wired the run wire to the capacitor, I did so because of the color coded wiring diagram that is on the back of the plug. I believe that is why the first compressor shorted out. I will notify Emerson and let them know of the error. Thank you so much for all of your help and I will give you an excellent rating.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
You are welcome, here is the ratings box!
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Phil is the type of a/c tech we all strive to be. He helped me solve a problem that was a brain twister. Thank you just answer for having Phil as one of you experts.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Thanks, ***** ***** however you should still send me a photo of the wiring diagram so that I can mark it up if necessary.
When you replace the compressor capacitor or any other part you should always have an amp meter on it in order to detect any failure to start properly before it burns something up, it takes compressor 30 to 60 seconds to burn. so a 5 or 10 second trial (that we call a smoke test as an old joke) is what we do.
I begin any new part change with a one second smoke test, then if nothing blows up, a 5 second test, if that seems fine, then I turn it and run amperage and refrigerant pressure tests.
If you have any doubts about the correct wiring, send me the diagram, and I help you review it.
.
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,152
9,152 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,152 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Need to confirm Air filter direction. Thermostat settings
Thermostat settings are irrelevant ? My question is about the filters … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat pump condenser coil are freezing up during this
my heat pump condenser coil are freezing up during this latest cold spell, can I thall them by using my aux mode … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Nest Learning Thermostat set for 80 but temp is 63. Gas
Nest Learning Thermostat set for 80 but temp is 63. Gas forced hot water boiler working fine. Other zones in my apartment are 70. Working fine yesterday. What's up? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Honeywell thermostat set at 74 (Heat on, Fan
I have a Honeywell thermostat set at 74 (Heat on, Fan automatic). But the house temp is 61. What do I do to get the heat up? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a new Payne Gas furnace. I have my thermostat set at
I have a new Payne Gas furnace. I have my thermostat set at 66 degree. It will cycle to that termperature, kick off but not come back on unless I reset the switch behind the panel or turn the breaker … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Heat won't come up to thermostat setting. New furnace and
Heat won't come up to thermostat setting JA: Did you double-check the thermostat's settings? And what about the filters? Customer: New furnace and a.c. installed this year JA: Do you plan on doing the… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gasfurnace has pilot light but no flame thermostat set on
gasfurnace has pilot light but no flame thermostat set on heat … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Can you answer a question about a thermostat setting on a.
Can you answer a question about a thermostat setting on a. Vive Box? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,408 satisfied customers
With my thermostat set to auto for heating it will not come
With my thermostat set to auto for heating it will not come on nor will it get warm. It Will come on if I place to the fan position but again will not get warm. If i set it to cooling the thermostat w… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Came in yesterday ho temp 93 degress gibsob thermostat set
came in yesterday ho temp 93 degress gibsob thermostat set at 72 turned unit off then this morning turned heat on came on and was heating could this be bad thermostat … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Heat not working. Thermostat set correctly. I can't find a
thermostat set correctly. I can't find a location where a filter would even go. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
How do I re-program my thermostat settings? I pushed the
i pushed the wrong buttons and now I do not know how to reset it … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x