My high pressure boiler keeps losing steam! HELP

Customer Question
my high pressure boiler keeps losing steam! HELP
Submitted: 2 years ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 26 minutes by:
5/30/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome!
http://www.columbiaboiler.com/industrial/CT/documents/CTManualnew708.pdf
copy/ paste that into your browser please and tell me if it is for your boiler or not, and what pressure you are running, what fuel you are using and if the burner is off when the steam pressure drops.
Tell me as much as you can about the application.
We can go from there.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Columbia 150 hp no gas burner on runs in gas low pressure 40 high pressure 80
Customer reply replied 2 years ago
Yes it is that link
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Thanks.
If we are lucky there is a wiring diagram glued inside the cover of this box... or you have the original manual for the boiler, there will be a diagram in that... the mfgr does not include it in their manual.
Attach it here if you find it please.
So far I suspect the boiler is going off on one of its safety controls such high temperature or low water.. or that the pressure control switch is going bad, or the connection point clogged with water scale.
Tell me as much about the water treatment it is getting, how often you blow it down, how often pressure relief valve is exercised.
These can be quite dangerous if not seen by a licensed boiler man at least every 30 days.
We can go from there.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Low water is the problem I already diagnosed thay
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Good work, be aware that this is a dangerous situation, most states require a licensed boiler man to work on these.
If you were to accidentally bypass the low water cut of, and *** if the pressure relief valve were blocked with water scale, the boiler could blow up, break that gas line, and take out a city block or two***.
Tell me how long it takes for the sight glass to fill with water so that the boiler then comes back on.... then test the pressure relief valve my lifting its manual release lever to insure that it does indeed blow off steam when manually operated.
----------
If it is running low on water repeatedly it has a steam leak, I need to know how long this has been going on. Bad steam traps or condensate return pumping systems can also cause this problem.
I need you to describe the use of the steam, radiators or heat exchangers, and condensate return provisions.
And keep this in mind... *** if the pressure relief valve were blocked with water scale, the boiler could blow up, break that gas line, and take out a city block or two***
Your building owners liability insurance might not cover such damage, it would be a nightmare for all concerned.. especially for those people and family members killed in the blast.
.
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Gas boiler is making loud rumbling and rattling noise
My gas boiler has just started making loud rumbling and rattling noises. What can I do? I have switched if off and turned tap on and this seems to have stopped it temporarily but I need to put it back… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Hi I have a Viessman Vitodens 100W WB1B 26kW Combi Boiler. In
Hi I have a Viessman Vitodens 100W WB1B 26kW Combi Boiler. In the last week or so the 'hot water' doesn't get very hot and goes from hot to cold hot to cold, which as you can imagin is prety annoiying… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
My boiler just started to make funny noises and a hissing sound,
My boiler just started to make funny noises and a hissing sound, should I be alarmed? It was rattling very loudly… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
My boiler in on but is not working. The lights on the screen
my boiler in on but is not working. The lights on the screen is on but not heat. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Peerless Boiler Series MI85 Gas Boiler installed 2015. We
Peerless Boiler Series MI85 Gas Boiler installed 2015. We have 3-zone water heat. Furnace works perfectly until outside temp goes into single digits and below. Furnace goes on and off repeatedly tryin… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have an old weil-mclain boiler for radiant heat. Old
we have an old weil-mclain boiler for radiant heat … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a recently installed oil fired burnham steam boiler.
I have a recently installed oil fired burnham steam boiler. There are three circulating pumps attached to the boiler. One is on a baseboard water radiation line that heats a portion of the house. One … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My sister has a boiler for heating. When she turns up or
My sister has a boiler for heating. When she turns up or down the thermostat a big stink comes. The stink comes at different times. She had a new chimney, sewer vents has lines checked but has not hel… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We service a munchkin boiler at a residence and have been
We service a munchkin boiler at a residence and have been routinely cleaning the heat exchanger every three years. It has ssemed to be adequate but wondering if that is a good schedule? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x