I need help troubleshooting Rheem RAHE-036JAS, Armstrong G1N80AU125D20C-1,

Customer Question
Honeywell ST9160B 1068 Board, Honeywell...
I need help troubleshooting Rheem RAHE-036JAS, Armstrong G1N80AU125D20C-1, Honeywell ST9160B 1068 Board, Honeywell SV9520H 8034 Gas Valve.
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 56 minutes by:
5/27/2015
HVAC Technician: Phil, Mechanical Engineer replied 3 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome! Your question will be answered in detail. UP to 48 hours step by step coaching on diagnosis & repairs $38 additional.
We can begin by doing a heat stress test on the printed circuit board (the one the thermostat wires are connected to... indication so far indicate a stuck fan relay or defective connection inside the board that is keeping the fan relay operating.
Stress test the printed circuit card.
Use a hair drier to slowly and gently warm the card to 120F (warm to the touch but not hot and not over 140F)... if you get any change in behavior that means the card is bad...
A micro crack has opened in the printed circuit at a solder joint, or inside its CPU in that case .... or a short circuit has developed as the card expanded when you heated it.
Constant expansion and contraction as these electronics heat and during their duty cycles over the years is what wears these cards out.
It is also a good idea to replug all of the connections in the unit, that burnishes any oxidized terminal connections and will sometimes solve the problem, especially at the printed circuit card and in any sensor molex connectors. Do that with the power off to the unit of course.
These cards are also damaged by Electrical Spikes caused by power failures and lightning. These high voltage spikes can literally explode the fine 'wire' connections inside the chip. There is also a shunt type device, often printed on to the card that allows a high voltage spike to arc across to ground harmlessly, some of these can wear out after a few times and allow the high voltage spike into the rest of the card and the CPU micro-circuits. The high end printed circuit cards use a large capacitor like device, or several in parallel, to capture and release such surges, these do not wear out.
If that fails use the 'attach files' link at the bottom left of your reply box to attach a picture of the thermostat wire connections there, I can use that to coach you on a few tests.
.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Condenser goes on then goes off for gust a second fan in
condenser goes on then goes off for gust a second fan in house stays on … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Can I ask wiring questions for my circuit board? Just
Not that I know of. I'm replacing a ST9160B 1068 control board on an Armstrong Ultra V Advantage 93 furnace with a Honeywell ST9120U. I have everything hooked up but the two wires that were on the M1 and M2 pins on the old controller. I'm not sure where they go. … read more
Bill
Bill
Service Mgr
114 satisfied customers
Armstrong Ultra V Tech 80 Gas Furnace Igniter will not glow.
Armstrong Ultra V Tech 80 Gas Furnace Igniter will not glow. I have replaced original igniter (no continuity) still no glow. Draft blower runs as should, pressure switch is ok, no restrictions in air … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing a Honeywell ST9160B 1068 controller board
Hello! I am replacing a Honeywell ST9160B 1068 controller board with a R40403-003 in my furnace. I am trying to figure out how to re-wire (needed a different Molex plug) the 6-pin plug with existing w… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Honeywell circuit board st9160b 1050 Mpls MN55422 went bad
Honeywell circuit board st9160b 1050 Mpls MN55422 went bad has melted spot on back Need to find a replacement is there any unviversal circuit boards made to replace this one as new one cost almost $30… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I have a Rheem Heat Pump Model: RPKA-036JAS with Defrost
I have a Rheem Heat Pump Model: RPKA-036JAS with Defrost Control Board:621-83-550N My unit was freezing over and not going into defrost mode. So I replaced the board. Same thing it's still freezing ov… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a question about my furnace control board, which is
I have a question about my furnace control board, which is not powering my Aprilaire Humidifier... I am pretty sure the board is not powering the white and black leads to the humidistat transformer (0… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Armstrong Ultra 5 Tech 80, and after the air shuts
I have a Armstrong Ultra 5 Tech 80, and after the air shuts off the inducer fan cycles 4 times. The heat isn't on.Any recommendations to problem?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Honeywell Chronotherm III. I replaced the batteries
I have a Honeywell Chronotherm III. I replaced the batteries and now when I turn on the Cool the fan never comes on. On the front of the panel it shows the time and the "AC". Why is my system doing th… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Honeywell 9502H2704 Smart Gas Valve. I want to know
I have a Honeywell 9502H2704 Smart Gas Valve. I want to know if there is a way to manually trigger this valve to see if it is working. What are the terminals to test to see if it is getting voltage fr… read more
hvacdave84
hvacdave84
53 satisfied customers
Hi MarkMy Armstrong Air Ultra 5 Advantage 93 furnace, which
Hi Mark My Armstrong Air Ultra 5 Advantage 93 furnace, which has a Honeywell Gas Valve, part # XXXXX is not allowing gas to enter firing chamber or it lights briefly and cuts off the gas flow 30 secon… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello- We just moved into our home. It has an older Rheem
Hello- We just moved into our home. It has an older Rheem condenser unit (RAHE-036JAS) that I had serviced. They had to add 2 lbs of R22 refrigerant and said this was normal for an older unit because … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello. Trying to replace original Honeywell ST9160B-1068
Hello. Trying to replace original Honeywell ST9160B-1068 with ST9120U-1011. Thought I had the wiring hooked up right but when I turn it on the blower turns on but the furnace does not ignite. Also on … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Armstrong Ultra V hot surface ignitor does not have voltage
Armstrong Ultra V hot surface ignitor does not have voltage during an ignition sequence. Is it controled by the gas valve or the control board? Wires come out of gas valve. A smart valve I believe? Ho… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
OK this ones really got me scratching my head. I have an Armstrong
OK this one's really got me scratching my head. I have an Armstrong ultra V tech 80. It was working fine until one day the blower fan just stopped going off. The heat and AC worked fine(compressor com… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Rheem Model RAHE-036JAS and what happens is the 1 pole
I have Rheem Model RAHE-036JAS and what happens is the 1 pole 24 Volt 25 Amp Contactor seems to stick and the system will either stay on even if you shut the power off on the thermostat or doesn't tur… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Air Ease Ultra V Tech 80 furnace with a new Honeywell
I have a Air Ease Ultra V Tech 80 furnace with a new Honeywell SV9520H valve and ST9160B control board installed. With thermostat turned down(no heat demand) the combustion fan cycles on/off every few… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an Armstrong Ultra SX 80 furnace. T-stat calls for heat,
I have an Armstrong Ultra SX 80 furnace. T-stat calls for heat, unit goes through normal sequence of events, burners fire and everything runs normally for about two minutes or so... Then the Honeywell… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less