I have an error condition "C2A1537" on a 13ACX unit.

Customer Question
I have an error condition "C2A1537" on a 13ACX unit.
Submitted: 2 years ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 9 minutes by:
5/27/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,377
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome!
That is unusual for a Lennox error code, tell me please where it is showing up.
So far it looks like the outside unit off on its high pressure cut out switch... the button is hidden behind a 1/2" hole in the cabinet in the area where the wiring attaches in most cases.... or its out of refrigerant or is not getting 24v control power, or 240v line power.
Tell me a bit about your trouble shooting skills and if you have a multi meter or not. We can go from there.
.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
There is a small display that scrolls the letters/numbers. We were able to reset the coolant on the outdoor unit.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Hello again,
It sounds like you pressed a reset button on the outside unit and the unit began working again, is that correct?
That happens if you turn the AC on in the spring without removing its weather cover if you had on it.... if you had no weather cover protecting the outside unit in the winter..... then the condenser needs cleaning... that is the aluminum finned heat exchanger that surrounds the unit on 2 or 3 sides.
To clean that, go to Lowes or Home Depot or any large hardware store and ask for 'foam coil cleaner' and use that to clean the coil.
I am posting two video's below, copy/paste each one to your browser to view them. this will give you an overview of the entire situation.
https://www.youtube.com/watch?v=XLN28ZcV4L0
https://www.youtube.com/watch?v=vDtT6hSpV4s
https://www.youtube.com/watch?v=-6xmokKNxNg
If you do not want to do this yourself, tell me which direction you are from the center of the nearest city and I will located a few well rated companies that will do the job for you.
-------------
We are on the honor system here. Please remember to rate my service before you leave today. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge.
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thanks
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Let me know if that solves the problem or not, we can go from there as needed without any time limits.
.Please do not forget to rate once we have solved the problem, it is how I earn a living and does not increase your charges.
Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,377
9,377 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,377 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Why is the furnace leaking a lot of water?
Lots of water is leaking from my furnace. Please help! I have an Amana 90 Air Command GUCA090AX50. The water is seeping out all along the bottom of the big black rectangular plastic collector with the… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a question about tranquility 27 climate master, not
Hello, I have a question about tranquility 27 climate master … read more
Phil
Phil
Mechanical Engineer
9,377 satisfied customers
I have three water cooled chillers with R22 using Copeland
I have three water cooled chillers with R22 using Copeland 5HP scroll compressors. They chill water for a chilled water a/c system. A unit working well gives high and low side pressures of 250 and 66p… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Inside uint blowing but outside condenser not coming on.
inside uint blowing but outside condenser not coming on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE ERROR CODE I AM GETTING SAYS "EE" =compressor relay contacts welded … read more
Bill
Bill
Service Mgr
100 satisfied customers
The condensate pump on my xe90 is cycling on and off. 1st
the condensate pump on my xe90 is cycling on and off … read more
Phil
Phil
Mechanical Engineer
9,377 satisfied customers
How to clean heat exchanger coils, filters have been clean
filters have been clean recently and I am getting an airflow alarm on the thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,796 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
278 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
9,377 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a Heil 9mvx 95% 2 stage heating unit. It started to
I have a Heil 9mvx 95% 2 stage heating unit. It started to act up last season (would run and heat for partial cycle without bringing the thermastat up to the temp I set it to.,etc. so I cleaned out th… read more
Phil
Phil
Mechanical Engineer
9,377 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.