Hi Mark
I have a four flashes Open Limit switch problem with my Concord Gas Furnace but not able to find the reset switch and unable to find the manual of the schematic for Model GC90UB075D16C.
Blower is on but no ignition is not on. No heat. 4 flashing light.
Thanks for your help.
Ly
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 44 minutes by:
5/3/2015
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Hi I'm Brian and I'm here to help. The four flash code does indeed point to a high limit switch open condition. Your limit switch should be upstream of the burners on the bulkhead separating the heat exchanger. If you follow the white wire on pin one of the 12 pin plastic plug on the control board you will find your limit switch. This is an auto reset limit control. You can try removing the power to the furnace for a few minutes but I doubt that will work. It's possible that limit switch has failed and needs to be replaced. If you can't determine which is pin 1, it is the pin on the lower right as you look at the board with the lettering right side up. The most common cause for a high limit switch trip is a dirty air filter or plugged evaporator coil. If the limit switch was cycling a lot due to those issues it's possible it stuck open. You can TEMPORARILY jump out the limit switch when you find it to confirm it's bad but NEVER EVER leave a limit switch jumped out to run the furnace!!! Click Here for an example of what a limit switch looks like. If I can answer further questions about this please reply and ask. Otherwise please remember to rate me positively before you leave tonight. Thanks, -Brian
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Click Here for another example of a high limit switch that is a different type. I'm having a hard time locating the exact switch that your furnace uses. If you find the switch and can give me the numbers off of it I may be able to help better. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi Brian,
How do you temporary jump out the limit switch to check to see if that is a problem and see if the furnace will fire up.
the filter was dirty.Thanks.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
When you find the limit switch, it will have wires connecting to its two terminals. You just jumper those wires together. This is a low voltage 24 volt circuit where they connect. There may be one of the terminals with two wires on it while the other terminal has only one wire on it. If that's the case you have to make sure all three wires connect to each other. If you have a jumper wire with alligator clips you could use that while they are still connected to the limit, you can can also use a carefully bent piece of a paperclip to jump them (with either the wires still connected OR removed). If the female spade connectors are not insulated they will slide onto each other so you could remove them and connect them that way. I must repeat myself and caution you, DO NOT leave them jumped to get heat. It is dangerous to leave the system without that protection! Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thanks
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
You're very welcome! Thanks for using Just Answer and allowing me to help you tonight.
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
For your convenience Click Here for a link to the PDF copy of the manual for your furnace. :)
Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Hello again. I'm just following up on our discussion last night to see how things turned out. Where you able to determine that is was a high limit switch issue? Is there anything else I can answer for you? If not, please remember to rate our session today. Thanks much, -Brian
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Jumping the high limit switch did not start the flame.
There was 27 volts between the two wires. I go ahead and order the new switch anyway. The red reset button seems loose hanging down when it was in upside down and not staying up when pressed
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
If there was 27 volts between the two wires while they were connected to the limit switch, that is indeed your problem and replacing it should solve your issue. Let me know if I can help further. You can continue to post on this same question for follow ups when you get your limit switch even after rating our session. I will get an email notice of your post and reply back as soon as possible. Thanks for allowing me to help and thanks for using Just Answer! Have a great day!
Ask Your Own HVAC Question
Customer reply replied 2 years ago
The 27 volts was when it was not connected to the switch, just the voltmeter.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
That is normal you would have 27 volts between the wires when not connected to the switch. If you reconnect them and no longer have 27 volts, you have zero volts, between the two wires connected to the two terminals on the switch, then that switch is closed and that is not the problem. This is how any of your safety switches would be checked when the unit is calling for heat. Let me know what you find and we might have to look elsewhere for a problem.
Ask Your Own HVAC Question
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
953 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit,
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit, Model MS-A12WA). That recently started leaking a pretty significant amount of water. The water must be building up inside the unit and then at s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Fault code 26 and 59 at same time. Evaporator frozen
Fault code 26 and 59 at same time. Evaporator frozen condensation drain was blocked now open .blower mother will not run when set to fan only… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
953 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
I have a furnace with an evaporator pump that i had to
I have a furnace with an evaporator pump that i had to repace all the relays and also the thermostat. After all is done it worked great for the winter except in order for it to work i had to put the t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.