possibly have a nordyne 624591-d control board that is faulty

Customer Question
- purchased universal board Honeywell...
possibly have a nordyne 624591-d control board that is faulty - purchased universal board Honeywell S9200u1000
Submitted: 3 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
12/9/2014
HVAC Technician: airheatman, HVAC Technician replied 3 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,762
Experience: Furnace, A/C and heat pump specialist.
Verified
Hello. My name is ***** ***** I'll do my best to help. Let's get started and see what we can do. Do you have a volt meter ?
If so, after burners ignite put probes on terminals HEAT terminal and NEUTRAL terminal on board and see if you get 120 volts between them.(You should have the Common fan wire and Low Speed heat wire connected to these terminals)
Ask Your Own HVAC Question
Customer reply replied 3 years ago

hey Tim - here is some more detail.

OK I have a Frigidaire furnace made by Teledyne. the control boards has been flaky for past few months and is near death - the board is part number 624591-D. I just purchased a Honeywell s9200U1000 universal control board and the instructions are very straightforward. After diligent exchange of wiring and connectors the new board installed with no issues. it starts fan inducer; lights glow stick; gas turns on and fires no issues then after 30 seconds it clicks to turn on blower motor and nothing happens. it then shuts down and restarts process. Motor is only one year old. I then put old board back in and system fires up no issue but will eventually die and several cycles or so dies. the new board requires some conversion wires and dip switch settings which old board did not require - I don't have a voltmeter - is there another way to check? just wanted to provide more data - the Honeywell board is brand new just out of newly open box

HVAC Technician: airheatman, HVAC Technician replied 3 years ago

I have personally never been a fan of using these universal boards, but should be able to make it work.(By the way if you ever have issues and need assistance, make sure you mention changing board so tech will know we may get different error codes than what original board had) What concerns me here is that you say you hear it click at time fan should come on. That is why I would like to know if board is sending 120v out. I think Dip switch 2 should be in OFF position so blower starts 30 seconds after burners. It is not out of question that you received a defective board although new.I think I would obtain an inexpensive meter from Lowes for about 20 bucks and verify if board is sending 120v out of NEUTRAL and HEAT terminals since you ARE hearing board click.

Ask Your Own HVAC Question
Customer reply replied 3 years ago

let me check wiring - I have white to white; red to red; green to green and yellow to yellow - if i turn fan on rather than auto on tstat - is there a way I can get a wire and touch two of the connectors say white and green to bypass tstat to see if blower motor turns on

HVAC Technician: airheatman, HVAC Technician replied 3 years ago
To bypass thermostat remove the R and G wire and touch them together. That should activate blower.
Ask Your Own HVAC Question
Customer reply replied 3 years ago

OK - will try that -- also on old board had an orange connector on M1 and a blue connector on M2 -- there are no connectors on new board with these tags. should they be going to a connector?

HVAC Technician: airheatman, HVAC Technician replied 3 years ago
No. M1 and M2 are simply for parking unused fan speed wires.Some fan motors have 3 or four wires (low,med low,med high and high). We only use one speed for heat and one speed for cool so if you had wires to M1 and M2 just tape them off.
Ask Your Own HVAC Question
Customer reply replied 3 years ago

OK - unfortunately I need to run - but does it make sense to try these two wires on heat and cold connectors?

HVAC Technician: airheatman, HVAC Technician replied 3 years ago
You could just to make sure the issue is not with the speed winding that you have selected
Ask Your Own HVAC Question
Customer reply replied 3 years ago

Sorry but work has been crazy - now have some time to finish up - on your last comment how can I check the speed winding?

HVAC Technician: airheatman, HVAC Technician replied 3 years ago
How many speed wires do you have and what colors?
Ask Your Own HVAC Question
Customer reply replied 3 years ago

on the nordyne 624591-D board

Cool - black

Heat - Red

M1 - Orange

M2 - Blue

HVAC Technician: airheatman, HVAC Technician replied 3 years ago

OK to see if the speed winding could be the issue, swap the black and red (Black to heat and RED to cool ) to see if blower will energize on heat mode.

Ask Your Own HVAC Question
Customer reply replied 3 years ago

OK may take few minutes to test.

HVAC Technician: airheatman, HVAC Technician replied 3 years ago
Standing by
Ask Your Own HVAC Question
Customer reply replied 3 years ago

OK - tried both your recommendations and neither one work. Tried bypassing thermostat by connecting red and green wires - blower will not activate. Also tried switching cool and heat - still no luck. Not sure what is left to try other than it maybe a defective board.

HVAC Technician: airheatman, HVAC Technician replied 3 years ago
I would probably replace with an original replacement board rather than a universal. If you can give me complete mode ad serial , I will get you a factory part number.
Ask Your Own HVAC Question
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,762
8,762 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a gibson furnace and the ignitor wont turn on. I
I have a gibson furnace and the ignitor wont turn on. I checked the resistance and it was 89. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Can't get my heat to stay on. Checking filter. It comes on
It comes on than goes off it got a programmable mode… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a payne model pg8jaa/maa. It is not igniting. My wife
I have a payne model pg8jaa/maa. It is not igniting. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Raypak model 59 spa heater. It was used last night
HI pearl, I have a Raypak model 59 spa heater. It was used last night and was operating normally. About 3 hours after using the spar I heard a buzzing noise from the heater , I turned the ac power off… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Kelvinator/Klectrolux split system Model ESE21hra,
I have a Kelvinator/Klectrolux split system Model ESE21hra, which keeps switching off after about 30 minutes operation. I have it on the cool setting of 25 degrees C, fan speed medium, and I believe t… read more
Michael Ferryman
Michael Ferryman
85 satisfied customers
My thermostat on my whirlpool hot water heater allows the
My thermostat on my whirlpool hot water heater allows the water to be too hot, after I changed both elements. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Its freezing outside, my furnace is new, and I have a RT
Its freezing outside, my furnace is new, and I have a RT Honeywell. I have tried to get the heat to come on and it wont. It says the internal temp is 64. No matter how much I turn it up, it wont come … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Trying to see if old Ruud deluxe 90 furnace works. Dotted it
Trying to see if old Ruud deluxe 90 furnace works. Dotted it have a pilot light or hsi? I cant find a manual on this thing,and we hanger no idea whether to start to figure out if it works or needs rep… read more
airheatman
airheatman
HVAC Technician
8,762 satisfied customers
Thermostat will heat to set temp then kicks out only to not
Thermostat will heat to set temp then kicks out only to not kick on at the temp required but if I take cover off stat kicks back on , batteries have been replaced and connections are tight Maple chase… read more
HvacmanSean
HvacmanSean
Owner
HVAC
226 satisfied customers
Air con model AOTR09JEC- orange timer light flashing two
Air con model AOTR09JEC- orange timer light flashing two times consecutively a break then flashes twice consecutively again … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Replace one coil for BAY96X1415 assembly. American
Replace one coil for BAY96X1415 assembly. American Standard/Trane. is there a part number for that. … read more
airheatman
airheatman
HVAC Technician
8,762 satisfied customers
I would need a Honeywell thermostat AIR Conditioner
I would need a Honeywell thermostat AIR Conditioner specialist how much does it cost for questions? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Our munchkin contender heater will not ignite. Turned power
Thanks. Turned power on an d . I think it's been down since this morning. I tried … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My air conditioner keeps on cutting off after I turn it on.
My air conditioner keeps on cutting off after I turn it on. The light is green and sometimes two light in green continue to beep … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a flashing yellow light on the front of my Furnace
I have a flashing yellow light on the front of my Bryant Furnace Model CNPVP/CNPVT. Flashes 6 times. I noticed that the heat was not firing up, but could hear something running inside the furnace. I r… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an old GE combination heating and AC unit. It has a
Hello. I have an old GE combination heating and AC unit. It has a wall thermostat, a transformer, a plenum thermostat, a fan limit control, a gas valve model 36C03 type 222 and a Honeywell R8222B rela… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
We can't get our boiler started. We had a water line break
we can't get our boiler started. We had a water line break and after that we have not beeb able to get it started. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Frigidaire furnace seems to blow cool air , no matter ...
My Frigidaire furnace seems to blow cool air , no matter what I try, I changed the filter, it didn''t help, it seems like there is no part of my furnace hooked up tp the chimney.And so I see a PVC pip… read more
Edward
Edward
Retired /Self employed
High School or GED
5,933 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x