Hi - I have two Goodman furnaces, but Im having a problem

Hi - I have two Goodman...
Hi -

I have two Goodman furnaces, but I'm having a problem with one. I keep getting a pressure switch stuck open/closed error. We switched the control boards between the units (it was the same board) and I still get the same error. Do you have any other ideas as to why the pressure switch error keeps happening?

Thanks.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/18/2013
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,075
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Rick :

Welcome, my name is XXXXX XXXXX I will do my best to help you with your issue.

Rick :

You could have a bad pressure switch or there could be a blockage in the exhaust vent

Customer:

HI

Rick :

Or your draft inducing fan could be weak and not provinding adequate draft

Customer:

when the unit comes on we hear the click in the switch

Customer:

doesn't that mean it's working?

Rick :

I don't think your hearing the pressure switch click

Rick :

You might be able to hear it if the fan wasn't running

Rick :

but the fan makes too much noise for you to hear the switch

Customer:

yes...we do hear a click when the service panel is open and you put your ear next to the switch

Customer:

yes the fan does make some noise, but if you listen carefully i hear a small click

Customer:

is there a way to test the pressure switch?

Customer:

or to test the draft inducing fan?

Rick :

You can check for continuity through the switch with an ohm meter. You need a manometer to check the draft

Customer:

this is a Goodman high efficiency furnace

Rick :

Same procedure no matter what furnace you have

Customer:

the unit works if we replace the switches with ones that have lower gauges

Rick :

"lower gauges"?

Customer:

lower sensitivities

Customer:

there is a number on the switches

Rick :

Then that could be an indication of a draft problem

Customer:

ok...what types of draft problems should I check for?

Customer:

the exhaust vent is clear

Rick :

How do you know that? It could be a blocked vent (including any sags in horizontal vent piping runs) or could be a weak fan (only a manometer test will confirm this)

Customer:

the vent is made of 3 inch pvc piping

Rick :

sags can fill with water (condensate) restricting the air flow

Customer:

the piping is rigid so any condensation should drain

Rick :

BotXXXXX XXXXXne is you need a manometer to be sure. The fact that the unit runs with a switch that has a lower pressure rating indicates a draft issue. If you are sure there are no vent obstructions then the fan is the most likely culprit or possibly too long a vent run. A too long vent run doesn't always cause a problem at first but it can show up as the fan output weakens a bit over time

Rick :

One other possibility and it might not apply to your unit

Rick :

Some unit have a condensate drain at the beginning of the run. If the drain is (partially?) plugged this too can affect the draft. The only other possibility could be a (partial) blockage where the vac tubes connect to the furnace (not the switch)

Rick :

You can try poking a straightened paper clip into the hose port on the furnace (not the switch)

Customer:

there are two tubes...on going into the furnace and the other into the fan?

Customer:

what can clog the tubes? water?

Rick :

Water can clog the tubes but it usually shows in the tubes and you said you cleaned them. Blocked ports are rare but they do happen. They can get blocked by debris as well

Customer:

ok...I'll try cleaning the ports...if the manometer shows the fan is too weak...how much of a stronger fan would I need?

Rick :

You should replace it with the OEM (original equipment) fan. The only reason the orignal fan wouldn't do the job is because the run is too long

Customer:

if the run is too long what would be the corrective action? moving the furnace?

Customer:

the holes in the unit are for two inch pipes and we put three inch

Rick :

Take a different shorter route with the vent.

Customer:

so i though the three inch pipe would compensate for the longer run

Rick :

The size of the vent piping is determined by the furnace btu input and the length of the run. I only mentioned the length of the run as a possibility. I wasn't saying it was likely

Rick :

The vent length limits are listed in the installation manual

Customer:

ok...i'll double check the limits for the length of the run...so to recap it good be clogged ports, a weak fan or the run might be too long...any other possibilities?

Rick :

Check the vent condensate drain (if you have one) for blockages. It could also be the original switch too is faulty. Even though you hear it click doesn't mean it's making good contact. You need to check for continuity through the switch while the fan is running or check for 24 volts (to common) in and out of the switch while the fan is running.

Customer:

the unit is only two years old...do the switches go bad that often?

Rick :

These switches work on extremely low pressure so they are very sensitive. Consequently they can fail at any time. It's not common for a switch to fail in 2 years but it does happen

Customer:

if it's a switch issue, should I replace both at the same time?

Rick :

It's best to determine which one is the culprit in this case. If your unit was 20 years old I'd say replace them both.

Customer:

so since the unit works with switches with lower pressure ratings then would the more probable cause be the switch instead of the fan?

Rick :

No way to know from that alone. Could be either one

Rick :

are you still there?

Customer:

yes

Customer:

ok...the problem is recurring as well

Customer:

we were able to get the unit to work by resetting the control board, the unit works for sometime and then the problem happens again

Customer:

does this indicate anything?

Rick :

Could point to a balky pressure switch. Sometimes it works sometimes it doesn

Customer:

what do you mean by balky?

Rick :

sometimes it works sometimes it doesn't

Customer:

i see...ok...thanks for your help

Rick :

You're welcome!

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,075
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,075
23,075 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman furnace acts as if it's not getting gas. Slightly
We just went through about 2wks of extreme cold temps. For whatever reason when the furnace has a lead time that lapses the furnace shuts down.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Our goodman furnace starts to run we can see it ignite but
Our goodman furnace starts to run we can see it ignite but when the fan starts to push the air shuts off and restarts. Could this be the ignitor? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Goodman furnace where the flame goes out before the
Hi. I have a Goodman furnace where the flame goes out before the blower starts. I've cleaned and then replaced the flame sensor. The led is giving me three blinks which I think is a pressure switch co… read more
Rick
Rick
HVAC Supervisor
23,075 satisfied customers
I have a goodman furnace that does not work, its a fairly
i have a goodman furnace that does not work, its a fairly new unit(about 4 years old). … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman Furnace that won't light. It seems like the
I have a Goodman Furnace that won't light. It seems like the igniter won't get warm, but I am not sure if I need to manually light it. My guess is no! The fans will turn like the heat is starting up a… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How can I bypass thermostat at furnace. Goodman furnace
Goodman furnace won't run ran out of propane when all started propane is good now furnace can not get any codes out of … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Goodman furnace is not working properly since yesterday.
My Goodman furnace is not working properly since yesterday. It is intermittent … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Goodman furnace won't stay lit. Replaced the board with an
Replaced the board with an updated one, replaced gas valve, replaced flame sensor, replaced limit switch.… read more
Steve Peck
Steve Peck
NC
16 satisfied customers
My Goodman furnace comes on and then goes several times a
My Goodman furnace comes on and then goes several times a day with varying degrees of slightly warm air. we can not get our house to warm up at all. I documented for an hour what it does. I hear the f… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman furnace that has tripped the lockout
I have a Goodman furnace that has tripped the lockout sensors twice now … read more
Rick
Rick
HVAC Supervisor
23,075 satisfied customers
I'm trying to help a friend diagnose this Goodman furnace
Hi there. I'm trying to help a friend diagnose this Goodman furnace problem. The burner only stay lit for a few seconds then shuts off. We tried cleaning the flame sensor. Even bought a new one. Test … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Gmh950904cxad Goodman furnace Main blower that is the fan
Gmh950904cxad Goodman furnaceMain blower that is the fan the blows the air into the house is extremely low and shuts up very quickly during the cycle leaving just the gas on and I keep getting open Hi… read more
Rick
Rick
HVAC Supervisor
23,075 satisfied customers
Goodman furnace hums but won't start. It's Christmas.so yes
It's Christmas.so yes there is a red light. That goes on and starts flashing after a couple seconds on the control board mounted to the fan … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a question regarding a Goodman furnace Model
Hello all. I have a question regarding a Goodman furnace Model GMH950905DXAB with the following issue. Furnace will successfully go through a start up cycle but at some point during the heating cycle … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Goodman furnace that was put in in 2007. It stopped
Hi Pearl! I have a Goodman furnace that was put in in 2007. It stopped firing the burners and the LED was blinking 4 times. Figured high limit or aux limit. I jumped both of them to see which one was … read more
Rick
Rick
HVAC Supervisor
23,075 satisfied customers
Technicians installed a new Goodman furnace in my home
Technicians installed a new Goodman furnace in my home yesterday and it works well. The design of the HVAC system in my home has the furnace used as the air handler for the air conditioning.system. Th… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a goodman furnace and it is continuously cycling.
hello, I have a goodman furnace and it is continuously cycling. Heat is not coming on. A tech was over … read more
Rick
Rick
HVAC Supervisor
23,075 satisfied customers
I have a Goodman furnace that is not turning on when
I have a Goodman furnace that is not turning on when thermostat turned up. The light on the board is solid for "normal operation". Can you please list some steps I can take to find problem? I am not a… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x