Carrier furnace with auto ignitor. Get error #34 ignition proving failure. Ignitor lights & cleaned sensing rod. Doesn't sound like gas is flowing. How do I tell if gas is coming through?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 minutes by:
11/14/2013
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Tim H. :

Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Thanks for the opportunity to help!

Tim H. :

Hello there

Customer:

Hi, Tim

Customer:

You know anything about error #34?

Tim H. :

Yes, it is an ignition proving fault. Are burners lighting at all?

Customer:

I don't think so. The ignitor lights, but I don't think gas is flowing. I cleaned the sensor, but no change in amps across it when ignitor lights up. I'm assuming no flame.

Tim H. :

So burners do not light at all, even if only briefly?

Customer:

No

Tim H. :

Have you checked for gas flow to the furnace?

Customer:

Gas line also goes to hot water heaters and those are working fine.

Tim H. :

I would start by cracking a union close to the furnace and make sure it's getting gas. We can't assume anything.

Customer:

Ok, that will take some time. Let's assume gas is flowing. How do I check the gas switch mechanism that the gas flows into. It has an on/off switch.

Tim H. :

Make sure it has gas and that the on-off knob on top of the gas valve is in the "on" position. If everything looks good there, next step is to check for voltage at the 2 gas valve terminals around the time ignitor comes on

Tim H. :

We should have 24 volts AC

Customer:

Ok, if no 24ac then what? If we do have volts, then what?

Tim H. :

If you have voltage and good gas flow, then you have a bad gas valve. If no 24 volts anytime around the time ignitor comes on would signal a bad control board

Customer:

That's pretty much ends the troubleshooting I would assume. Is gas valve easy to replace? Just remove top & bottom connections and wires?

Tim H. :

Yes, fairly easy.

Customer:

I don't like working with gas. When I "crack" a union, what do I need to seal it back up?

Tim H. :

You just take 2 adjustable wrenches and turn the 2 halves just enough to hear if gas is coming out. Then immediately tighten them back up. You don't even need to take it totally apart.

Tim H. :

Unions are self sealing

Customer:

I'm not sure I have a union. I've got a ball valve. Out of that comes a flexible gas tube that runs into the unit and connects directly to gas valve. Can I just close ball valve and loosen connection to gas valve?

Tim H. :

Yes, you can do that and then briefly open the valve.

Customer:

Is there a special sealant, puddy I need to put in treads when reconnecting?

Tim H. :

Yes, if and when you install a new gas valve, use any standard pipe "dope"

Tim H. :

It's just to lubricate the threads

Customer:

Ok, but I don't need it if I'm just loosing connection & listening for gas?

Tim H. :

Most home improvement stores will help you with selecting a pipe dope. No, you don't need just to loosen and listen for gas

Customer:

In a nutshell, if burners don't light I've got

Customer:

1. gas blockage/no gas

Customer:

2. bad gas valve

Customer:

3. bad control board

Customer:

Anything else that I need to check?

Tim H. :

Absolutely correct! And we determine that by whther or not there is 24 volts AC to the valve or not

Customer:

got it. Thanks for your info. I'll go work on it and see. What do I need to do for you?

Tim H. :

Yes, good luck! Thank you for using Just Answer and please don't forget to rate my service. (Bonuses are always appreciated). Feel free to post back with any additional questions.

Customer:

ok

Tim H. :

Good luck

Customer:

Tim, are you there?

Tim H. :

I'm here

Customer:

Cracked union above gas valve. Gas was flowing.

Customer:

Ran unit. At rest, valve was reading 15V ac. When ignitor lit, valve read 28v ac. Assume bad gas valve.

Customer:

It's a white-rogers, but no marking on it. How do I know part #?

Tim H. :

Yes, if gas to valve and valve receives voltage and doesn't let gas come through, that would be a bad gas valve

Customer:

I took it off, btw. There is a gas manifold attached to bottom. Not sure how to take that off without bending it.

Customer:

I called local supply house. They won't sell to me...said I'd blow up my house.

Tim H. :

It should just unscrew from valve

Customer:

Any idea how to find PN?

Tim H. :

If you give me full model number, series number and serial number of furnace, I can locate a part

Customer:

ok, got to go look. hold, please...

Tim H. :

OK

Customer:

Bryant

Customer:

Model 373LAV048095

Customer:

Series G

Customer:

Serial 469A11644

Tim H. :

hang on....

Tim H. :

This should be the part you need, part# XXXXX

Customer:

Ok, thanks again for the help.

Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified
Tim H. and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
3,971 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My carrier furnace is not igniting, no error code. Last
My carrier furnace is not igniting, no error code. Last night it was glowing like it was trying to ignit, but it's not glowing anymore. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have 2 Carrier furnaces that are a few months old but are
I have 2 Carrier furnaces that are a few months old but are not coming on … read more
Jarrett Baker
Jarrett Baker
Building Analyst and Home Inspector
BPI license
11 satisfied customers
My carrier furnace is blinking 33 and I don't know how to
Hi my carrier furnace is blinking 33 and I don't know how to fix it … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 1983 Carrier furnace 294gaw00100. There is not
I have a 1983 Carrier furnace 294gaw00100. There is not pilot ignition. I've checked blower, theromstat, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im getting an error code of 12 on my carrier furnace, trying
im getting an error code of 12 on my carrier furnace, trying to figure out how to fix it … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Getting a code 33 on my carrier furnace intermittently. And
getting a code 33 on my carrier furnace intermittently … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have an 18 month old Carrier furnace and infinity touch
I have an 18 month old Carrier furnace and infinity touch control thermostat, in the last 2 weeks a pop up screen shows "SYSTEM FAULT 13-LIMIT LOCKOUT and the furnace will not heat. The service tech c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier furnace 58mca120 16-120 error code 33
I have a carrier furnace 58mca120 16-120 error code 33 followed by error code 13. replaced both the high limit and roll out switch and still have the error code. There are no other switches in the cir… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Got an carrier furnace 58mxa080112 new air filter burner
got an carrier furnace 58mxa080112 new air filter burner goes out when big fan kicks on … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a carrier furnace model 58 PAV090-14 the 3amp fuse
I have a carrier furnace model 58 PAV090-14 the 3amp fuse keeps blowing. I changed motor speeds and it's running ok now. Could it be something in the motor or did I not do anything and it could happen… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier pad needs to be changed. Is that something easy to do? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My carrier furnace says secondary voltage fuse is open. I
My carrier furnace says secondary voltage fuse is open … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Furnace not working. Carrier Furnace Model 58PAV070-16112
Furnace not working. Carrier Furnace Model 58PAV070-16112 Blinking code is 2 short and 4 long - 24.Code 24 reads SECONDARY VOLTAGE FUSE IS OPEN Check for short circuit in secondary voltage (24VAC) wir… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier furnace 58mcb080-20 gas valve will not open... i
carrier furnace 58mcb080-20 gas valve will not open... i confirmed 24 volts going to valve... replaced the valve and same problem... i jumped 24 volts from the transformer and it opens no problem... n… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier furnace from the 80s. In which the blower
in which the blower won't turn off. but the heat does turn on/off depending on the thermostat control … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier furnace model 58sta070 I am getting code
I have a Carrier furnace model 58sta070 I am getting code 34 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have carrier furnace model CK5BXA048021AAAA that is not
I have carrier furnace model CK5BXA048021AAAA that is not heating up. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x