Tempstar Heat Pump, Fan on the Heat pump continues to run when in defrost mode.

This morning I was in the house and the heat was running, The heat pump then suddenly got louder (its been doing this for a few days when its been in heat), I happened to have my clothes on ready to go to work, so I went outside and looked, the frost was melting as it is supposed to, I watched it go from cloudy to clear and start falling away. However the fan was still running.

After I went back inside I heard it go quiet again (assuming it went out of defrost), and then a few minutes later the entire system shut off (by the thermostat, it had hit proper temperature to turn off).

So the system is definitely working, defrosting et al, however I am unsure if the fan should be running when defrosting, and should I have it checked out or leave it alone?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
11/12/2013
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,889
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,

so in short the fan is not stopping in the outdoor unit when defrosting? It continues to run even though the defrost kicks?

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Yes, that is what seems to be happening.

Thank you.

This will become an issue as it gets colder outside.

You have a bad defrost board that is not turning the fan off during defrost. The board with installation and service call should be around $150-$200.

This is not critical in medium temps, but will be as it gets colder.

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,889
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

I have a followup, the board was replaced yesterday afternoon. When testing the new board it has the exact same symptom of the old one.


 


I did a little testing myself and after the unit had shut off I still heard a buzzing, I pulled the reversing valve lead off the defrost board and sure enough the buzzing stopped.


 


I reconnected it, went inside and kicked on another heat cycle, the unit did a proper defrost, fan didnt start, compressor ran, about 45 seconds later the fan kicked, a blast of warm air (from the coils) then i heard the reversing valve go back to heat mode.


 


I shorted the test pins after 5-10 minutes and the unit went into defrost, the reversing valve hit, and the unit got really loud, the fan still running.


 


Is it possible that my unit isnt supposed to kick off the fan if it goes into defrost mid cycle?


 


The Model is: NHP036AKC2


 


As I sit here typing this I heard the unit get quiet again, probably went out of defrost.

Can you please tell me how the unit is wired?

Thermostat wire colors to the outdoor unit?

The reverse valve should not be energized while the unit is off.

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Its wired correctly best I can tell.


 


The reverse valve was only energized when the board was calling for defrost or in cooling mode, in cooling mode the valve stays energized the entire time.


 


At least thats what the Electrician who came out said (for background he is the one who installed it 8 years ago)


 


 


I called him again this morning, he thinks we may have gotten a bad board and/or the sensor is bad. I suspect something more.


 


Regardless if the thermostat initiates a cooling cycle then O is energized (I think) and the defrost board reverses the valve and keeps that energized regardless of whether the thermostat is calling for cooling or not.


 


When the board is in defrost mode it was energized as well, to me it seemed like this morning it started a defrost cycle just as the thermostat was satisfied, so when i realized the RV was energized I went inside and forced the thermostat to kick another heating cycle, which made it run what seemed like a normal defrost.


 


So it seems like the reversing valve is good (when he was out yesterday he manually reversed it mid cycle, by energizing the orange wire to the board) The sensor seems good by the fact that when it defrosted normally as soon as it hit the temp it un-reversed and the fan kicked on, The contactor seems normal since things are turning on and off (I dont know much about this)


 


So could I have just gotten a bad board with the exact same symptoms as the first one?


 


My system does not have pressure switches, and as such has a jumper wire between the pins.


 


I cant think of any more detail to give, it befuddles me that it could be that the replacement board was bad, but it has the exact same symptoms...


 


What else could fail that would cause everything to operate normally except the defrost cycle when the unit is mid cycle?


 


If the unit is wired correctly:

O terminal is reverse valve and ONLY has power during cooling or defrost.
Defrost is actually just a cooling cycle to move heat out to coil...the only difference is the fan shuts down so as not to circulate cold air through the coil while we are trying to melt it.

Thus defrost is cooling just without the outdoor unit fan running.

In heat...the reverse valve has NO power.

The only thing that can turn the fan on is a defrost board. The compressor is turned on separately by the contactor.

The fan motor gets power straight from the defrost board. So if the fan gets power or not is because of the defrost board.

Really the only intent of the defrost board is to shut the fan down in defrost.

I would have hime try another board in case....but if the result is the same there is another issue.

Billy

Ask Your Own HVAC Question
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,889
22,889 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am replacing an old Weatertron thermostat on a heat pump
I am replacing an old Weatertron thermostat on a heat pump with a new Honeywell wife thermostat. The User Guide for the RTH6500 has an alternate diagram on page 7 for heat pumps with different wiring … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,889 satisfied customers
I'm trying to wire a new thermostat but cant seem to get my
I'm trying to wire a new thermostat but cant seem to get my colors to make heat and air work properly … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,889 satisfied customers
I am about to replace a York Q674l 1272 / 2TH11702224A
Hello, I am about to replace a York Q674l 1272 / 2TH11702224A thermostat with a Honeywell FocusPRO 5000 TH5110D1006. I am studying the wiring at the moment before touching anything. I've photocopied t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Two extra wires on thermastat (black and white) not labeled
two extra wires on thermastat (black and white) not labeled but not sure where to put on my new thermastat … read more
HvacmanSean
HvacmanSean
Owner
HVAC
229 satisfied customers
I have a goodman heat pump PGBQ36075-1A....trying to wire up
Hello...I have a goodman heat pump PGBQ36075-1A....trying to wire up a Honeywell Thermostat RTH6500WF… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to install a nest thermostat and there are two
I'm trying to install a nest thermostat and there are two wires going into the aux/e / w2 port (for a honeywell thermostat) and I'm wondering if both should (or can) be installed for the nest... I hav… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have a roof ac/heater that was installed in 2006-7.
Have a roof ac/heater that was installed in 2006-7. Yesterday found that even though it sounds like the thermostat is clicking The heater is not coming on . I believe this is a America Standard unit, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have installed a Honeywell rth6350/rth6450 thermostat and
I have installed a Honeywell rth6350/rth6450 thermostat and followed the instructions to the T. However, whenever the heat kicks on, only cool air blows out. We have a heat pump. The wires on the old … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
HiI have an american standard heat pump 1 of 2 on my roof
Hi I have an american standard heat pump 1 of 2 on my roof in AZ. They are both about 15+ years old. I changed out the thermostat with out turning off the power. Yes I know it was stupid, but most of … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
my old thermostat wires G-C-R-Y-W2-E, I attached all wires
my old thermostat wires G-C-R-Y-W2-E, I attached all wires y to yellow G to green and so on I attache W2 to Aux everything matched I did not put a jumper between E and Aux other then that what else wo… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
Im trying to replace a very old Lennox (model 72F1301) with
I'm trying to replace a very old Lennox (model 72F1301) with a new Lux programmable thermostat. None of the wiring letters are the same on the old one as on the new one. The old thermostat has wires l… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have an old honwell round(dial) thermostat that I am replacing
I have an old honwell round(dial) thermostat that I am replacing but the terminals are not mark with letters. How do i determine the hook up of my new thermostat?… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
Bought a FocusPRO TH6000 series programmable thermostat. Have
Bought a FocusPRO TH6000 series programmable thermostat. Have a split unit heat pump. Thermostat wire colors are as follows red,green, yellow, white, and orange. Black wasn't used on the old thermosta… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an older bryant heat pump model 655A the fan for the
I have an older bryant heat pump model 655A the fan for the e-heat mode will not turn on. I have no wiring diagrams or diagnostic information for this unit, if anyone could provide a diagnostic tree o… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Where does the contactor from the a/c unit hook into the furnace
Where does the contactor from the a/c unit hook into the furnace system. Working with a Nordyne Intertherm furnace Model #M1GB070ABW and Nordyne Intertherm A/C unit Model #S3QA-030K need to wire to Ho… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,889 satisfied customers
i have a line voltage heating system and want to replace the
i have a line voltage heating system and want to replace the thermostat with a programmable one. I have a honeywell TL8230 but there are 2 black wires and 2 red wires. The old king version I had had a… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Rheem heat pump RQPMA049JK Can someone give me the thermostat
Rheem heat pump RQPMA049JK Can someone give me the thermostat wiring color codes I have a Hunter programmable thermostat.The heat pump wants to heat in cool mode.What wires on the thermostat do I need… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Old Westinghouse thermocouple gas valve had three terminals
My Old Westinghouse thermocouple gas valve had three terminals my new universal has two, I was told it will work and the third turminal is a dummy terminal on the old one. I have tried every combinati… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.