This is very strange. So, I have a Trane XE80. My current

This is very strange. So, I...
This is very strange.

So, I have a Trane XE80. My current problem is: There is no gas ignition (or furnace appears to shut down) unless I jump the R/W in the furnace control board.

The story:
A couple of days ago I noticed the furnace did not start in the morning. I checked the breaker and reset it and it came on… no issues. Later that day in the evening, the same problem but this time resetting the breaker did not do the trick. The furnace appeared to start but it was shutting down after a while. This is what I did:

1. Reset the breaker and checked the firing process. The thermostat called for heat, the induce draft motor came on, the igniter glowed, the flame came on but the furnace shutdown 1-2 secs afterwards.

1.1. - I found the flame sensor could potentially be the problem. I cleaned it without removing it with a soft rug and tried again. It worked, once.

1.2. - I read in the forum using sand paper is the way to go to clean the sensor. I removed it, cleaned with sand paper being careful to not damage anything… Put it back on, it did not work. BUT NOW it stops right after the ignitor glows. There is a click, it seems like a call to shut the system down and that’s it

2. The red led blinks normal. 1 blink per second and 2 per second when get a call for heat.
3. Checked the igniter and it was white in the middle. I figured based on some notes from other users this could be the problem. I bought a new igniter and installed it. Same problem. It stops right after the igniter glows. The furnace tried to start twice or three times but that was it. Checked the led for a diagnosis code and same as before. Steady 1 sec blinking.
4. Decided to jump R/W just to cover all basis and it came on… works without problem.
5. Removed the jumper cable and tried again using the thermostat to call for heat. Same PROBLEM again.
6. Jumped the board once again, it works, no problem.
7. Removed the jumper cable, SAME problem. It stalls right after the igniter glows.

My questions:

1. If the problem is the thermostat, why is it able to send the signal for heat? Cables does not seems to be the problem…
2. Is there a problem running the furnace with a jumper in the meantime?

Appreciate your help,

FA
Show More
Show Less
Ask Your Own HVAC Question
Answered in 22 minutes by:
10/31/2013
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,807
Experience: Furnace, A/C and heat pump specialist.
Verified
Hello. My name is XXXXX XXXXX I'll do my best to help. Troubleshooting often requires meters and test equipment. Let's get started and see what we can do.
If you can jump the R and W at the board and furnace works fine, the issue is in the thermostat. If this is a battery thermostat, start by installing new batteries as there could be a bleed down from low batteries.
You can leave jumped for a short time , but remember we have no temperature control to shut it down.
Ask Your Own HVAC Question
Customer reply replied 4 years ago

Hi Tim,


 


I believe I figured out the problem, I was asking customer support to cancel my request but I see you went a ahead and replied and I thank you for that.


 


The problem was a flimsy connection, still testing it... will wait for the furnace to cycle a few times but that seemed to be the issue.


 


With that said, I have another question and it relates to the motor inducer assmebly, replacement part number and advice on how to get that done. Someone was telling me it needs to be replaced as there is some clicking noise when it starts and it might indicate water corrosion...


 


Thanks again,

This is the motor you will need. You can also Google and possibly find a better price MOT473AB
http://www.bestbuyheatingandairconditioning.com/Merchant2/merchant.mvc?Screen=PROD&Product_Code=MOT473AB&Category_Code=m-trane
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,807
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,807
8,807 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
display backlite not working on honeywell thermostat #TH6220D.
display backlite not working on honeywell thermostat #TH6220D. can this be fixed?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
LUX XT500E thermostat is flashing "FAN" and heater won't turn on
My LUX XT500E thermostat has been flashing the word "FAN" and my heater won't turn on because of it. I have tried online suggestions of restarting it and taking out the batteries, then putting them ba… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My furnace (Rheem Classic 90 Plus) runs only if the panel is
My furnace (Rheem Classic 90 Plus) runs only if the panel is off. When the panel is replaced, the flame on the burners goes out and the system cycles every few minutes. when I re-set the system and op… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Xrv95 trane furnace. Power to unit, fuse ok, transformer ok,
xrv95 trane furnace. Power to unit, fuse ok, transformer ok, Circuit breaker ok. Power to furnace. Changed thermostat batteries. Problem is fan will not run even in on position. No heat. No codes, no … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Both of my TH8321WF1001 Honeywell thermostats have gone
Both of my TH8321WF1001 Honeywell thermostats have gone dark? Seems like no power is going to it but I checked circuits and none are tripped.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Have an t8411r thermostat. After several failed attempts to
have an t8411r thermostat. After several failed attempts to change temp. I turned off circuit breaker ---now screen is blank … read more
airheatman
airheatman
HVAC Technician
8,807 satisfied customers
I wanted to replace a T8112D Thermostat with an RTH 111B and
I wanted to replace a T8112D Thermostat with an RTH 111B and in removing the T8112D, I accidentally touched the red and white wires. The system went on. I relaced the thermostat and the Air Cond came … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a honeywell chromorjem 111 but all it says is hold.
I have a honeywell chromorjem 111 but all it says is hold … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I am having heating issues with what I believe is my
Hi Pearl... my name is ***** ***** I am having heating issues with what I believe is my thermostat … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently replaced my furnace control board. The furnace is
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Boar… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an amana furnace control board with an led flashing 3
I have an amana furnace control board with an led flashing 3 times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need help with my -Rodgers furnace control board 50e47-060
I need help with my White-Rodgers furnace control board 50e47-060 on a Trane furnace. It has a blinking red light. On the unit it says " steady red light- replace control, blinking red light-referred … read more
type2technician
type2technician
253 satisfied customers
I have a nordyne KG7TC-080D, with a furnace control board
I have a nordyne KG7TC-080D, with a furnace control board #624790/920916. this is a 2-stage upflow unit. Furnace ignites but goes out wihin seconds. flame sensor replaced, still the same issue. Has in… read more
airheatman
airheatman
HVAC Technician
8,807 satisfied customers
I think that I may have a bad furnace control board. Trouble
Hello I think that I may have a bad furnace control board. Trouble shooting so far. Two different thermostats with the same behavior. Direct connection of the R&W&G wires make the furnace run continuo… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace control board light is not coming on. Yes, the
My furnace control board light is not coming on. JA: Did you check the furnace's filters? Customer: Yes, the furnace filter is new. JA: Do you plan on doing the work yourself? Customer: Yes. JA: Anyth… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x