I have a carrier furnace model 58GS that burners will not ignite. I am an electrician so I checked all the voltage outputs-I have 120volts to the furnace and 24 volts coming to the circuit board via the transformer. The pilot light ignites and I can see it sparking/hear it clicking to light the burners but they just don't come on. Any ideas? My furnace manual says replace the gas valve assembly? Thank you
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
10/20/2013
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,386
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Rick :

Welcome, my name is XXXXX XXXXX I will do my best to help you with your issue.

Rick :

What are the terminal designations on your gas control valve? MV, PV, MV/PV?

Customer:

I have to go look at the furnace. I will be right back

Rick :

ok

Customer:

Where would this be located?

Rick :

Inside the burner compartment. The burner manifold is connected to the valve outlet and your gas supply line is connected to the inlet. One more question. Does the pilot electrode continue to arc even after the pilot is lit?

Customer:

Yes it keeps arcing after pilot is lit. It continually arcs and makes that "clicking" noise as if its constantly trying to light the burners.

Rick :

That's usually an indication that the pilot flame is not being sensed. On most versions of this model the electrode is also the flame sensor. You can try carefully cleaning off the oxidation on the electrode with fine sandpaper. With any luck this will solve the problem. If not you may need to replace the pilot burner assembly. I was asking about the gas valve terminals to determine if the board is sending 24 volts to open the main valve (24v across MV & MV/PV on many valves) if the pilot is lit the board is sending 24v to the pilot valve (PV & MV/PV).

Rick :

If the pilot flame is not being sensed there should not be 24 volts to energize the main valve which will let gas into the main burners so they can ignite

Customer:

Last night I did clean the electrode with sandpaper and no luck. My manifold has designations of 1 and 2 and 3 and 4 at the terminal connections. I dont see a MV or PV on the manifold. You are saying these letters would be on the manifold which is the same part where you can turn the dial to turn gas on and off-It is the part that has the gas supply in and out to the burners, correct?

Rick :

The terminal designation I mentioned is the most common current designation. But I don't know what you valve terminals are. There are at least a dozen different versions of your model furnace. If you have 24 volts across both pairs of terminals on you valve then that would indicate the valve (sounds like you found it, yes it has an On& Off dial) is faulty since it's being energized but given that the electrode is still arcing should be an indication that the pilot flame is not being sensed and therefore the main valve (which will let the burners fire up) should not be energized

Customer:

So I will check for 24v across the terminals on my manifold and if I have that then it still would not light because the pilot assembly is not sensing? Or my manifold could be faulty if I don't have 24 volts across the terminals? So I would replace the pilot assembly then?

Rick :

If you have 24 volts to both pairs of terminals then that's an indication the gas valve is faulty because it should open to let the burner fire up. You should now only have 24 v to one pair which is the pilot valve that opens to send gas to the pilot. Once the pilot lights the electrode should sense the pilot flame which should stop the arcing and energize the main valve. Since the pilot flame is apparently not being sensed there should not be 24 v to the main valve.

Customer:

Ok it will take me a while to check all this. Can I sign out and come back on later if I have more questions and it will still be included in the $30 fee or should i leave this page open and come back when I'm done?

Rick :

Since you cleaned the electrode and you still don't have the pilot flame sensed that's an indication that the pilot burner may be the problem. We would change the pilot burner when this happens. It's also possible the board is faulty but since the pilot burner is much less money than the board it gets changed first.

Rick :

This thread won't go away even after you rate me favorably. I will answer related follow up questions even after you rate me. You will only be charged when you rate me.

Customer:

So obviously I have to have the pilot light lit to test the 24v connections. Is it okay to be poking around with my tester while the gas and electricity is on to the unit? Sounds like a dumb question-being an electrician I know what I can and can't touch with electricity but when you add gas I get nervous.

Rick :

The only way you can trouble shoot this is with the unit powered up. Don't sweat the gas, your problem is that the gas isn't flowing. And unless you have a gas leak there's nothing to be concerned about. Can you tell me how many terminals on the gas valve again? I thought you said 4. Is that correct?

Customer:

Yes there are 4

Rick :

OK

Customer:

Oh wait there were 5 4 of them were the same size and the 5th one was "smaller" and was between 3 and 4 but let me go double check

Rick :

Ok, I'm going to hand this off to one of my colleagues who is more familiar with this gas valve than I am. He's online now and I'll send him a message to pick this up. Please be patient it may take a little while

Rick :

Please don't post again until you hear from hime

Ask Your Own HVAC Question
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,

Is this the 3 wire pilot with green, yellow and white wires?

And gas valve is numbered 1-5?

Billy
Ask Your Own HVAC Question
Customer reply replied 4 years ago

1 and 2 are on the right side of the manifold #1 has a white wire and #2 black wire- 3,4,5 are on the front of the manifold #3 is black-#4 is a smaller pronged connector than the others and is yellow- #5 is green

Thank you.

Get a short wire and shape in a U or use a jumper...

while pilot is lit.....jump gas valve terminal 1 to terminal 5 and tell me if burner lights.

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

ok be right back


Standing by

Ask Your Own HVAC Question
Customer reply replied 4 years ago

ok so the burners did light but only for a short period and then went out

Ok,

May be a domio effect or poor connection...but one thing is sure...the pilot assembly warp switch is bad.

Before moving on you will need to replace the pilot assembly.

EXAMPLE

1 to 5 bypassed the warp switch in the pilot. This was a common failure as the assembly aged.

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

ok so the pilot assembly is the piece that has the "sparking" electrode in it-correct? I will just have to find a place in madison thats open to sell parts today which is not likely.


Now that addresses the pilot warp switch...the constant sparking can be fixed by replacing the spark electrode in the pilot



It shuts down when it senses flame activity. Yours is older and just keeps sparking...it is not harmful just a nuisance

Ask Your Own HVAC Question
Customer reply replied 4 years ago

to remove the pilot assembly should i remove the gas tube that runs from the manifold from the part itself or from the manifold? I believe somewhere in my manual it says to remove it from the manifold but I can't find where i read that

With this unit there will be (2) 1/4" screws that hold a bracket (which holds the pilot) from the burner.

Unhook the 1/4" aluminum tube from the gas valve. Then the whole assembly comes out.

From that point you easily see how the unit is held to the bracket.

Remove tube from pilot. Pilot from bracket. Reassemble with new...

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

sounds good- you have been so very helpful-Thanks again!!

You are very welcome.

I am available for 30 days after answer is rated so feel free to reply with any updates or questions.

Billy

Ask Your Own HVAC Question
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
22,767 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier furnace 58mcb080-20 gas valve will not open... i
carrier furnace 58mcb080-20 gas valve will not open... i confirmed 24 volts going to valve... replaced the valve and same problem... i jumped 24 volts from the transformer and it opens no problem... n… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,767 satisfied customers
I have a Carrier furnace from the 80s. In which the blower
in which the blower won't turn off. but the heat does turn on/off depending on the thermostat control … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,767 satisfied customers
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick
Rick
HVAC Supervisor
22,386 satisfied customers
I have a Carrier furnace model 58sta070 I am getting code
I have a Carrier furnace model 58sta070 I am getting code 34 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am having trouble with my Carrier furnace. It was heating
I am having trouble with my Carrier furnace. It was heating last night, but when I woke up this morning it was 60 degrees...brrr. I have turned the fan on and it works. I have checked the circuit brea… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have this Carrier Furnace Model 58PAV070-18112 and last
Hello I have this Carrier Furnace Model 58PAV070-18112 and last year and now this year the igniter comes up glows and first burner kicks on then shuts off. This is intermittant. Othertimes it goes thr… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Carrier furnace WeatherMaker 9200 and Ac. This fall
I have a Carrier furnace WeatherMaker 9200 and Ac. This fall when the tenant turns on the furnace, first the blower motor will run for a few minutes and then shut off. Then the induced motor will come… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace 58MCA080-13112. Got home from
I have a Carrier furnace 58MCA080-13112. Got home from vacation and my furnace won't work. The inducer motor comes on and you can see the flame thru the window, so it heats heats up but the blower nev… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have carrier furnace model CK5BXA048021AAAA that is not
I have carrier furnace model CK5BXA048021AAAA that is not heating up. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a carrier furnace and I need to change the filter. I
I have a carrier furnace and I need to change the filter. I don't see an easy way to get to the old filter to change. Can you help. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Having error 22 on my carrier furnace. according to the
having error 22 on my carrier furnace. according to the panel error 23 . Check for obstructing error tubing. Pressure switch stuck close … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace that won't let the fan run. It
Hi. I have a Carrier furnace that won't let the fan run. It starts up just fine then cuts out.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I am having a problem with my carrier furnace. The fan motor
I am having a problem with my carrier furnace. The fan motor is stuck on. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My older carrier furnace a/c unit just started running the
My older carrier furnace a/c unit just started running the blower no matter what settings are on the thermostat. The only way to turn off the blower is to shut off the power switch.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace model 58MCB100---1116, I need an
I need an electrical schematic. it there one available on line or via PDF … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a carrier furnace (1990') with a Heil Condenser. The
I have a carrier furnace (1990') with a Heil Condenser. The furnace blower doesn't shut off and the thermostat appears to be inoperative meaning the controls don't seem to have any effect on the syste… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Carrier furnace model 58gs075-8a. Initial problem
I have a Carrier furnace model 58gs075-8a. Initial problem Nest thermostat telsl that there is no out / in connection to furnace. I measured no voltage between green, blue, white, and red. Nest says n… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Get a code 34 on my carrier furnace. Cleaned the flame
Get a code 34 on my carrier furnace. Cleaned the flame sensor, but still get no ignition. Igniter seems perfect, it glows till it gets almost white in color. Any ideas?… read more
Rick
Rick
HVAC Supervisor
22,386 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.