This answer was rated:

High ref pressure message. I had the freon filled to required

6lbs after repairing a leak...
High ref pressure message. I had the freon filled to required 6lbs after repairing a leak in the system now it shuts off after a minute of running each time it recycles with the "high ref pressure" message. I made sure baskets, etc. clean. Thanks!
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 hours by:
10/9/2013
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to Just Answer!


You are basically on the right track, however there are some other issues we need to be sure of.
Did you use a vacuum pump after fixing the leak? what did the high side and low side gages read when it was evacuated.

What refrigerant is involved... did you liquid charge or vapor charge the system

Tell me if this is an AC unit, or water chiller. and the brand and model number of the unit.

We can go from there.

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago

This is a Jandy pool heat pump. model EE-2500T


410a refrigerant. The HVAC guy after welding the leak holes did a vacuum test to ensure no leaks then filled to the required 6 lb pressure.

Hello again,

From here it sounds like the HVAC guy over charged the system. If he told you that the vacuum was for a leak test, then thats not how its done. He may have left air inside the system, if he did, that would run the head pressure up, and if not corrected will damage the system.

CLICK HERE
for the specification sheet that shows the refrigerant charge as 100 ounces. If the man put 6 pounds of refrigerant into the system he would be *undercharged very slightly.

Here is the URL address in case the link above doesn't work
http://www.zodiacpoolsystems.com/~/media/Zodiac/Global/Downloads/SA/SA6407.ashx

I suspect air in the system (called a non condensible) or that he put more than 6 pounds of refrigerant in the system, or made some other charging error.

I would try removing a few ounces of refrigerant until the system runs. You may want to locate a more competent service man. If you need help doing that, tell me which direction you are from the center of the nearest city and I will take a look for you.


Phil


Ask Your Own HVAC Question
Customer reply replied 4 years ago

Thanks. He did the vacuum test and watched the gauge for about 5 mins to see if it moved. When he was satisfied he filled it. He also weighed his tank to show he injected 6lbs. At $50 a lb it was pretty pricy.


 


I have the guy coming back on Monday and will do just that. The closest bigger cities are: Springfield (1.5 hrs) Tulsa (2hrs), Little Rock (3 hrs), Kansas City (4 hrs) Unfortunately there is no one in this town (zip 72712, Northwest Arkansas), that specializes in heat pumps. The pool companies technicians will not touch these units much less refrigerants, etc. and the HVAC guys only know to do what they do with home HVAC units.

Hello again, thank you *very much for that detailed account.

The refrigerant is worth less than $30 a pound retail... a person cannot do a valid leak check on a refrigeration system by pulling a vacuum on it and waiting for the pressure to rise (for many reasons)... a person cannot detect the usual small leak that way in 5 minutes, it would take months. Leaks are detected by pressurizing the system and applying soap bubble leak detector solution to the suspect areas.

The man was using a plumbing technique used to find different sorts of leaks... he was out of his league... from that I am assuming he made other mistakes, such as using a bathroom type scale to weigh the refrigerant in (not at all accurate enough)... and not doing a proper evacuation, that left air in the system.

I will stay with you on this as long as needed...

Tell me if this man was running his own operation or came from a larger company from that I can help you determine what to do.

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago

Thanks, XXXXX XXXXX removed a few ounces of ref. yesterday morning and it apparently worked. The unit is running uninterrupted even now, for now. The man is from a larger, but small company. He does have many years of large commercial experience.


 


So what is the best way to measure refrigerant going in? He did use a scale. And how should he have done a proper evacuation? ( I understand about the soap bubble test).


 


I found a local large pool company that services Jandy heat pumps. However they can't handle the refrigerant side of it. No way to win here! what's a person to do in my situation where I'll always need two experts?

Hello again, the best way to measure the refrigerant charge is by the refrigeration service gage readings...IN CONJUCTION WITH the indoor and out door air temperatures to within 1 degreeF... in other words it is very precise way of doing things. That will get you to within 2% of a workable refrigerant charge on 85 or 90% of systems on the market. The other 10% of systems require what we call 'super heat and sub cooling" temperature measurements... those are made using a saturated temperature and pressure chart, a a very accurate electronic thermometer.

Its both an art and a skill.

___________

Over charging a system by just a few ounces can almost double the cost of running the unit... but it will still cool.

If you wish to rate my work positively so far, so that i get paid by the company, I will go beyond your original question and coach you how your system should be charged.

I need the rating... then i need the brand name and model number of the outside unit, and what refrigerant it uses... that is stated on the units name plate.

If it is a Chinese made unit with multiple wall units attached, its more difficult.. if its on of the more standard type ducted systems I can get you good information no how to charge it properly.

Let me know, we can go from there.

Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have central AC sysyem - Spacepak airhandler, York
I have central AC sysyem - Spacepak airhandler, York affinity 3s outside unit and a Honeywell TH8100U1003 thermostat. The outdoor unit has been intermittently cooling but seemed to start working again… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
We have a York furnace. We have no heat. The fan is working
We have a York furnace. We have no heat. The fan is working but the burners will not fire. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
Lighting the pilot on my Rheem updraft is no problem but
Lighting the pilot on my Rheem updraft is no problem but after holding the button for a min. or 2 and releasing, the pilot goes out???? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We just moved into our new place and a handyman bought one
Hi Pearl, we just moved into our new place and a handyman bought one of your honeywell thermostats. It's the programmable RTH221B1039/U1. unfortunately it doesn't appear to want to cooperate. Whenever… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My unit is not operating correctly. I have it set at a temp,
my unit is not operating correctly. I have it set at a temp, and it doesn't come on when the temp goes below the set heating temp. I have to manually hit the set button and it comes on, but then it do… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Nordyne,furnace, pressure switch open fault is
I have a Nordyne,furnace , pressure switch open fault is indicated. The model of furnace is KG7TC120D45D it is about 6 yrs old., had Hvac Tech come out just about 2 weeks ago. Furnace was firing up. W… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Is it unsafe to turn off the fans when using the L38DF gas
Is it unsafe to turn off the fans when using the L38DF gas fireplace for a few hours? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil-McLain CGa boiler. The pilot is lit and it
I have a Weil-McLain CGa boiler. The pilot is lit and it sounds like it is switching on and off (when the thermostat is on) but we're getting no heat. Is there something I should be checking? Thanks. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Looking for replacement blower motor for an old RUUD gas
Looking for replacement blower motor for an old RUUD gas furnace model HN-175JD blower # RL10-9DUH … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Trane TUE080A936K2 furnace isn't heating the ignitor
my Trane TUE080A936K2 furnace isn't heating the ignitor never glows, but the fan spins up … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
How can I solution a 1600 code erre, Sorry!! How can I
Sorry!! How can I solution a 1600 code error in a honeywell generator … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
The thermostat in our 1st floor circuit keeps automatically
The thermostat in our 1st floor circuit keeps automatically resetting itself to 62 deg F. Alkaline battery had corroded. I removed, cleaned the area with dry cotton and replaced the batteries. Still n… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
I have a York central heat unit. The problem is it wants to
I have a York central heat unit. The problem is it wants to turn on to give heat but shuts off after about 2 seconds and keeps on doing the same thing. Had this problem 3 weeks ago. Unplugged limit sw… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
Just inherited my grandparents house. Built in 1972. They
Just inherited my grandparents house. Built in 1972. They have a closet that is 50 by 70 inches that used to house a gas water heater and a gas furnace, below the closet is the intake air. The gas fur… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have the same problem with my code 33 I followed your
I have the same problem with my Bryant code 33 I followed your instructions as described here and it worked so I need a new limit switch, with one caveat, I let the wires touch metal and now I get not… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
90% secondary heatexchanger holding a lot of water in it,
Bryant 90% secondary heatexchanger holding a lot of water in it, not allowing the pressure switch to close. I removed the 3 hoses at the top (2 large 1 small) of the plastic trap and drained the water… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
How are you? I have a Breckwell P-2700 FSA Pellet stove and
I have a Breckwell P-2700 FSA Pellet stove and when the stove is on the auger continues to feed pellets into the pot. … read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
Do you charge a fee? just recently, tried to lite propane
just recently, tried to lite propane heat stove, pilot lites, and when I release the hold down knob to turn on burner , the pilot goes out, as long as I hold down the the lite knob , it will stay lit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x