Hi,

I'm having issues with my furnace. It is a Trane Furnace TUD120C960J0. In summer, I saw the Blower in the furnace was not working on a hot day. I went into the basement and found basement flooded with water. The water was coming from the furnace. Suspected that the condencer drain could have been blocked. I removed the dirt at end of the drain to make sure there was no dirt that was blocking the drain. I called HVAC technician, who said the control board is blown and that is the reason for blower not working, and replaced the board. The blower worked for a month and another hot day, same problem. The second technician came and tried to put a new board, however said the new board is not working because there is some short in the furnace that is causing the control boards to fail. Their recommendation is to replace the entire furnace, which I feel may not be required.

The current state of my furnace (the way the 2nd technician left it)
1)the thermostat wires are not connected to the control board.
2)the main power wires seems to be swaped (When I compare with my neighbor's furnace connections)
3)When I close the furnace door the blower starts, which they say it should not happen while thermostat is not connected, could be the control board is not working right. However, since the blower is working, I feel I don't have to replace the entire furnace. Even if I replace the furnace, the issue with te condenser and water leaking into the furnace may comback and cause the issue again with the new furnace.

I'm trying to figure out the real issue. And how I should go about solving it that shelling out lot of money for no reason. Thanks a lot for your help. The days are getting cold, and I need my furnace fixed before it gets really cold.

Thanks
Sur
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 minutes by:
9/30/2013
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to Just Answer!

If you can give me 30 minutes or so I can see if I can find the service manual for that unit in my files. Meantime tell me how deep the water got in the basement and how high up it got into the furnace.

We can go from there

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago
The condenser sits on top of furnace. The water leaked into the furnace, the filter was all wet and there was water in the furnace underneath the blower. Water was 1/4 inch high on the basement floor. The level never reached the furnace base, it is just that the water leaked through furnace because condenser sits on top.
Hello again, thank you for the explanation.

That was condensate water from the cooling coil, leaking because the drain was clogged as you suspect ....and that damaged the electronics in the furnace.

Some furnace types have a condensing section down inside the furnace, your is not that type however.

----------

If the furnace is over 10 years old, replacing it will not be a bad idea... its only worth an attempt at fixing it if it is less than 5 years old.

The second technician should be avoided.

A common ploy when a company is trying to sell you a new furnace is to leave it taken apart or worse sabotaged so that other technicians will have a hard time fixing it.

If these techs are from the same company I would tend to avoid the company...leaving the furnace apart is an unethical practice.

Tell me how old the furnace is, and tell me please which direction you are from the center of the nearest city... I will look around and see if there is an HVAC service company with good reviews in your area.

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago

The furnace is 13 year old. I live in Collegeville PA-19426. I've American Home shield insurance. The 1st and second technicians are through American Home Shield. They say it costs $4500 to replace a furnace. And the insurance says I've have to pay $1000 out of my pocket and if I get it fixed through someone outside, the insurance is void on the furnace.

Hello again, replacing the furnace that old is warranted in this case, and $1,000 out of pocket is not bad at all.

If you choose to rate my answer positively, I get paid part of your deposit...and will keep the question open for any follow up questions.

Thanks!

Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

I got my furnace replaced. It is a Payne PG8JAA/MAA model. The warrenty company replaced my original Trane 120 BTU one with 110 BTU model of payne. They say it is a good one and is more efficient.


Any thoughts about the furnace I got?

Hello again,

That Payne furnace is made by Carrier corporation, a good company, the furnace itself is their bottom of the line unit...it is 80% efficient. If it is more efficient than your old Trane furnace it is only marginally more efficient.

It is however a reasonable and equal replacement for your old trane furnace if it has a 4" sheet metal flue pipe and is over 10 years old.

I recommend those types of low efficiency furnaces for all but very cold climates because they are easy to repair and require drastically less maintenance that the 90% and 95% efficient furnaces which I am generally cautious about recommending.

They paid about $600 wholesale for the Payne furnace. It should last you 15 or 20 years with only minor repairs required.

Phil



Ask Your Own HVAC Question
Customer reply replied 4 years ago

Thank you. We live suburbs of Philadelphia. Do you think it is okay for the climate here. Also the warranty company replaced 120BTU trane funace with 110BTU Payne one. Will this be a problem for me? My house is 3000 sqft area.

Hello again, the new 110,000 BTU Payne furnace will output about as much as heat as the old Trane furnace..thats not a difference you will notice in your area. You should be fine with the Payne unit.

 

Engaging the insurance company in a debate on quality and the relatively minor details is a fight you are unlikely to win because of their use of words like "or available equivalent" in their contract... its fuzzy wording.

 

These contracts are weasel worded by attorneys specializing in that activity.

 

Such wording is common on all major engineering and construction contracts and is upheld...when in fact there is seldom ever an *exact equivalent in all aspects. and in many cases a cheaper 'equivalent' is chosen, when in fact it is of lesser quality than what was specified.

 

Having said that, many Trane units use ball bearing motors, the Payne furnace does not, The ball bearing motors last longer.

 

If you have air conditioning attached then there is an air volume issue. The Payne unit will have very *slightly less air flow capability than the Trane unit in some cases, enough to *possibly make a difference in air conditioning performance but that would remain to be seen

 

Summary: You could hassle them, but are not likely to prevail, and will most likely not notice any difference in performance.

 

Tell me what the temperatures have been in your area lately, and if you have AC attached to the furnace or not. and how the new furnace seems be operating.



Phil

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Thanks for the information. Winter least is 21-37 F and Summer peaks are 64-84 F. The AC is outside, but the furnace fan blows the air through the condenser that is inside the house, and sits on top of furnace.


 


Sur

Hello again, that furnaces should work really well for you, especially in such a mild climate during the summer. Heating is very seldom a problem... and in your case with that relatively mild climate cooling should be fine as well.

Feel free to stay in touch, even months later if you like.

Phil
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Ducane high efficiency furnace and the draft
Hi I have a Ducane high efficiency furnace and the draft inducer fan will not go on. It just hums. I also have no LED light blinking at all. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Payne furnace model #PG8MAA that seems to have lost
I have a Payne furnace model #PG8MAA that seems to have lost power. The blinking light is off, and auto pilot light does not light the pilot light. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Payne furnace that won't light. I'm pretty sure it
I have a Payne furnace that won't light. I'm pretty sure it has a pilotless system. It has a window with a red blinking light that will blink twice with a short pause then 4 blinks. Do you by any chan… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Have a weather maker infinity ultra high efficiency furnace
have a weather maker infinity ultra high efficiency furnace 1/2 hp electric motor kgmp 2001all fan seperated from shaft disk fan 9 inchs in diameter … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a 90 Plus high efficiency furnace with error code 31.
Have a Bryant 90 Plus high efficiency furnace with error code 31. Yearly I seem to get this due to birds building nest in the intake. I the use shop vac to clear it out and I am back in business. Howe… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Have a payne furnace model pg8maa036110 series e input
have a payne furnace model pg8maa036110 series e input 110,000 output 89,000 in Virginia bch 23462 zip on a slab 13,000 sq ft. is this to big for house? installed in 2011 & worked until end of heating… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier 58SX gas fired condensing furnace that will
I have a Carrier 58SX gas fired condensing furnace that will not start. The pilot flame comes up upon the thermostat calling for heat but the flame is a bit lazy and it goes out after about 5-7 second… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I have a Payne furnace that i purchased to heat an area of
I have a Payne furnace that i purchased to heat an area of about 1500 square feet. My electric bill was running $400.00 or more a month when I used it on just some day of the month since it has not go… read more
Expert
Expert
I have a 96% efficient furnace. It was properly installed
I have a Bryant 96% efficient furnace. It was properly installed and we've used it for the past 5 years. I turned up the thermostat to start it up this morning for the first time this year. Within a f… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a lennox high efficiency furnace, it's not blowing
I have a lennox high efficiency furnace, it's not blowing hot air … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
My high efficiency furnace is showing 3 flashes on the code
My coleman high efficiency furnace is showing 3 flashes on the code - says pressure switch stuck open - which switch is that? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My payne furnace turns on fan works right away but don't
my payne furnace turns on fan works right away but don't ignite. I changed the igniter and igniter senser it turned on igniter worked 1st time but did not after that … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,086 satisfied customers
I just instaled a new Payne furnace and a/c condensor. The
I just instaled a new Payne furnace and a/c condensor. … read more
David Bowden
David Bowden
Owner
331 satisfied customers
My Carrier is 4 years old. My problem is the condensate
Hi my name is Dave. My Carrier is 4 years old. My problem is the condensate drain is stopped up. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Payne furnace, during a fault code 13 or 33 is the 24v to
Payne furnace, during a fault code 13 or 33 is the 24v to the thermostat still active? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier condenser Model#: 38HDC060321. Relay opens after
Carrier condenser Model#: 38HDC060321. Relay opens after about 1 minute of running. I've replaced the capacitor (usually burns out about every two years) and the main fuses (1 blew, replaced both). Go… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I have a carrier furnace (1990') with a Heil Condenser. The
I have a carrier furnace (1990') with a Heil Condenser. The furnace blower doesn't shut off and the thermostat appears to be inoperative meaning the controls don't seem to have any effect on the syste… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x