Hi there, I have a Trane XE90 furnace/AC unit. While changing the filter last night, I had some trouble getting the front panel off, and the unit seemed to die.

Thinking the issue could be the door switch, I replaced that, but I still have no power to the unit, and my LCD thermostat won't come on either.

Could it be a blown fuse that's causing this? The breaker did not trip when the unit failed.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
9/12/2013
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Tim H. :

I will need to gather some more information before I can answer your question(s). Please provide all information I ask for as I am not on site and you, essentially, become my "eyes and ears". In some cases, I may require some readings such as voltage before I can provide you with a satisfactory answer. If you are not equipped to perform these tests, the ability to work through to a solution may not be possible. We always recommend all work be performed by a licensed professional. At the end of our dialog, you will have a chance to rate my service, but please wait until we are done and you have your answer(s).

Hi, I'm Tim and I'm an HVAC expert here to help answer your question(s). Please provide all the information I ask for since I'm not onsite. At the end of our dialog you will be asked to rate my service, but please wait until then and all your question(s) have been answered satisfactorily. Thanks for your business!

Tim H. :

Good morning

Customer:

Hi there

Tim H. :

Have you checked the switch on the side of the furnace? The breaker? If you push in the switch with lower panel off, are there any LED lights on?

Customer:

No lights at all.

Customer:

and I've checked the breaker

Customer:

the switch is just a plain old light switch, right?

Tim H. :

Yes

Customer:

I'll check it again, hold on

Tim H. :

OK

Customer:

OK, switch was in off position, and the condensate pump came on, but still no power to the thermostat display, and no movement in the unit

Customer:

pump came on when I turned it on (though for some reason it was wired to be in the "off" position)

Customer:

as on

Tim H. :

Did you check to make sure blower door is on tight? If it is, try taking the lower panel door off and seeing if the fuse on the control board is blown. Many furnaces have a blade type fuse.

Customer:

I think the fuse MAY be blown, but where would I find it on the control board?

Customer:

it's not apparent

Tim H. :

Many furnaces have a fuse like this on the control board. I don't have a model number or specifics on your furnace, but check and see if it has this type of fuse.

Customer:

OK.

Customer:

just trying to figure out where that might be on the board

Tim H. :

It may not have one. It would be sticking out and apparent (on the board) if you had one.

Customer:

OK

Customer:

doesn't appear to have one

Customer:

AND there was a red LED blinking

Customer:

and the thermostat seems to have power all of a sudden

Customer:

but when I depress the door panel switch, the LED goes out

Tim H. :

Are you there?

Customer:

Sorry, just ran down to see what it was doing

Customer:

so no fuse

Tim H. :

No fuse in the furnace?

Customer:

and when the switch is depressed by the door panel, it shuts down the thermostat which, when the red LED on the bottom of the unit is blinking and the switch is NOT depressed, has power

Customer:

no switch on the control board, no

Tim H. :

How did you hook up this new blower door switch?

Customer:

I cut the old leads and replaced them with smaller ones that fit the switch in question

Customer:

Gosh, i wish I could show you how things look via FaceTime or skype or something

Tim H. :

OK, there should be two leads that attach to the switch. Can you turn the power off and take those leads off and jumper (tie) them together thereby bypassing the switch?

Customer:

I can do that, yeah. Just a second

Tim H. :

OK

Customer:

OK that's done

Customer:

still just a blinking red LED at the bottom of the control unit

Tim H. :

Now turn power on and see if it works

Customer:

power is on

Customer:

that's why the LED is blinking

Tim H. :

Is there a code legend somewhere around that control that tells what that blinking means?

Customer:

I'll go down to the basement and take a look

Tim H. :

OK

Customer:

it's flashing, though without a previous point of reference, I can't say if it's "fast" or "slow"

Customer:

and the codes are "normal, no call for heat" if slow

Customer:

which I guess is the case

Customer:

and "normal, call for heat" if fast

Customer:

which I don't think is the case

Customer:

that said

Customer:

the thermostat is set to 74

Customer:

with the ambient temp at 76

Customer:

and the thermostat says "wait"

Tim H. :

So it sounds like your furnace has power and 24 volts. But the thermostat is "dead"?

Customer:

I was able to start the fan though

Customer:

not sure

Customer:

the thermostat is an LCD readout

Tim H. :

OK and it says "wait"?

Customer:

yes

Customer:

it's lit up

Tim H. :

That is the delay when in a/c mode

Customer:

and I can make alterations to the desired temp, etc

Customer:

and start the fan

Customer:

OK

Customer:

so what does that mean?

Tim H. :

give it 3-5 minutes

Customer:

OK

Customer:

will do

Tim H. :

Then it should work

Customer:

I put a wire nut on the two exposed switch leads

Tim H. :

OK, I just wanted to make sure it wasn't the new switch

Customer:

no

Customer:

I think the switch they sold me at the electronics shop isn't the same type as the switch I removed

Customer:

I think this one BREAKS the current when depressed, rather than the other way around

Tim H. :

Yeah, better to get an OEM replacement

Customer:

like a fridge light

Tim H. :

There are many sites that sell Trane parts

Customer:

Ebay, my man

Customer:

eBay

Customer:

rather

Customer:

so it seems like I was basically on the right track, just didn't have the right switch

Tim H. :

Yes

Tim H. :

Go to an HVAC site that sells Trane parts

Customer:

still waiting to see if it comes back on

Tim H. :

It takes a good 3-5 minutes

Customer:

K

Customer:

Ok, seems to be running now

Tim H. :

Great!

Customer:

so I should be OK with it jumped like that, but will want to put in an oem switch, right?

Tim H. :

Yes, OK to leave jumped for now

Customer:

Gotcha

Customer:

thanks, Tim

Tim H. :

Yes, good luck! Thanks you for using Just Answer and please don't forget to rate my service. (Bonuses are always appreciated). Feel free to post back with any additional questions.

Customer:

I appreciate it.

Tim H. :

Have a great day

Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified
Tim H. and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
3,971 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a LUXAIRE furnace and it is not working properly. The
hello I have a LUXAIRE furnace and it is not working properly … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I changed the ignite on my heil NDGK. It's still not
I changed the ignite on my heil NDGK. It's still not heating … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Fan stops motor just hums tech touched the test o. Touching
touching the test point got the fan turning again but after a few days it stopped again … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The compressor on my mini split is working but the interior
The compressor on my mini split is working but the interior fan is not Also the high pressure refrigeration line stays hot … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I'm having an issue with my furnace. Furnace was shutting
Furnace was shutting down after running for couple of minutes. I called an HVAC service and they change filter/open limit switch and pressure valve/switch … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My light keeps blinking on my oil heater. What's a few
Hi my light keeps blinking on my oil heater. What's a few problems that makes the light blink? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a lennox zoned heat pump and it is not heating down
I have a lennox zoned heat pump and it is not heating down stairs. … read more
HvacmanSean
HvacmanSean
Owner
HVAC
229 satisfied customers
My siemans RWB30E centeral heating box is not lighting up I
Hi My siemans RWB30E centeral heating box is not lighting up I have no heating, It is set to come on twice a day but not turning on or lighting up I have tried the over ride switch with no success … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
The heater is not responding. Inside temp is 65 and heat is
the heater is not responding. Inside temp is 65 and heat is set at 71. The hold button is not on. I don't know how to get the heat to come on. I canned a photo of the panel if possible. I don't have a… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Gm from la.i have a luxaire gas furnace it has been giving
gm from la.i have a luxaire gas furnace it has been giving me problems...mod#g8t06012uha11a,new flame sensor,new ignitor,new limit switch,and new thermostat...it comes on when it wants to...temp is 69… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a new Beckett Genisys 7505 oil furnace that stopped
I have a new Beckett Genisys 7505 oil furnace that stopped working last night. I completely filled the oil tank and have reset the furnace a few times, but when I try to turn on the heat I get cold ai… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Aprilaire 700. Water is getting to the switch at the bottom
Aprilaire 700. Water is getting to the switch at the bottom of the unit but not proceeding up into the unit to the filter element. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
We have a new HVAC gas pack. It is a Daikin DP16GM3008041,
We have a new HVAC gas pack. It is a Daikin DP16GM3008041, 2.5T PKG Gas, 16 SEER. The filter I am using is a Honeywell Elite Allergen 10 FPR. It makes a whistling sound when the unit runs and seems re… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I am showing the e24 on my thermostat and our temp here is
I am showing the e24 on my thermostat and our temp here is going to be in single digits later tonight. I am a widow and have not idea about taking off panels on the furnace. Help … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Used stove one day and it will not light tonight. HELP. 5
Used stove one day and it will not light tonight. HELP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We have a Trane 4YCC3024B1064B packaged unit, 3 years old.
We have a Trane 4YCC3024B1064B packaged unit, 3 years old. In winter, especially coldest days, it will start, provide heat, but then shut off well before thermostat temp is reached. House is often 5-6… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a rheem manufacturing company model # rkma-a060jl10e
I have a rheem manufacturing company model # rkma-a060jl10e it does not want to work. We found that the gas had been turned off to it so I turned it back on. Is there a pilot light or something that n… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I turned on my built in fireplace for the first time
i turned on my built in fireplace for the first time yesterday. I came on for 1 minute and turn back off. I could here a click every time it would turn on and off. I was leaving the house after it tur… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x