I have a Waterford free standing heater that looks like a wood stove. Every spring I turn off the gas and relight the pilot in fall. In 2012 the pilot would not stay lit when releasing the pilot button. Replaced the thermocouple and thermopile and it worked. Now fall of 2013 and pilot will not stay lit again on fall start up. What gives?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
9/2/2013
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,155
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to Just Answer!

Try cleaning off the tip of the thermocouple with plumbers sand cloth, and then tightening the nut were there the thermocouple screws into the gas valve (its a LEFT hand thread, turn it 1/8 to 1/4 of a turn)

If that fails then it is likely a bad gas valve... for some reason, about one in 10 times when you replace the thermocouple, the gas valve fails a little bit later.

It is most likely that you had not tightened the nut where the thermocouple screws in enough though, that is usually due to the small wrench size that tends to slop on the nut...I use vice grips if necessary to get that extra faction of a turn on the nut.

If you choose to rate my advice so far *positively, I hold the question open for any follow up you might need.

Thanks!

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago

I've checked the thermocouple and it was tight. It's not a left hand thread by the way. Is the tightening necessary to get electrical contact? What I don't get is this happens 2 years in a row and I remember now that only the thermopile was replaced 2nd time. It seems that the gas valve is not the problem. How do thermopile and thermocouple differ in operation?

Customer reply replied 4 years ago
Relist: Incomplete answer.
Jerry
Jerry, Service Technician
Category: HVAC
Satisfied Customers: 3,365
Experience: HVAC Technician. Hearth Products Specialty
Verified
Hello,
The thermocouple is the smaller of the two, and controls only the coil in the valve that holds open the pilot flame. The thermopile is a much larger thermocouple, and actually produces enough voltage to open and close the main burner port inside the valve, this is the one that operates the main flame. In your case, with the pilot flame not holding, it is going to be a thermocouple problem, (or gas valve issue). I would replace the thermocouple. There are different qualities of thermocouples available, and sometimes the tips of the cheaper ones burn completely off.
Ask Your Own HVAC Question
The above reply should have been posted as an answer, not an info request. Also, to answer your other question about how tight the thermocouple should be..... you are correct, it is a simple electrical connection there and does not need to be tighter than finger tight plus about a quarter turn.
Ask Your Own HVAC Question
Customer reply replied 4 years ago

OK, that helps. I'm assuming then the thermocouple generates millivolts but I don't understand how because there are no wires like the t-pile has only a copper line from it to the valve. Also, if the valve itself is bad is it repairable or junk?

The thermocouple does generate about 15 to 20 millivolts (when the pilot flame is strong, and touching the top 1/3 of the thermocouple). Make sure you check your pilot flame also.
The outside copper sheath is used as one of the conductors, and the inner part the other conductor. So to test mv on a thermocouple, you would put one lead on the outside and the other lead of your meter on the very end that would screw into the valve.
IF the valve is bad (not likely) then it is not repairable.
Jerry
Jerry, Service Technician
Category: HVAC
Satisfied Customers: 3,365
Experience: HVAC Technician. Hearth Products Specialty
Verified
Jerry and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Jerry Your Own Question
Jerry
Jerry
Jerry, Service Technician
Category: HVAC
Satisfied Customers: 3,365
3,365 Satisfied Customers
Experience: HVAC Technician. Hearth Products Specialty

Jerry is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,155 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My boiler is running low on water every day or so. I see a
My boiler is running low on water every day or so. I see a good deal of steam escaping around the water-level indicator (a vertical glass tube), and I wonder if I have the valves adjusted wrong. … read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
I have a Lennox lf24-150 that is giving me a 4 flash. It
Hi I have a Lennox lf24-150 that is giving me a 4 flash. It runs perfectly for 2-3 cycles then starts fires but the fan doesn't turn on. Then I get the 4 flash since it is overheating without the fan … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Sure. I need to reset my Trane Xe90 Furnace. It's on
Sure. I need to reset my Trane Xe90 Furnace. It's on external lockout after failing to light. Happened after I tried switching to a new thermostat. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have a Ac/Heater unit Model RGPS-10EBRJR made 03/2010, the
Have a Ac/Heater unit Model RGPS-10EBRJR made 03/2010, the heater will come on & light, as soon as the blower comes on the flame will go out. it will do this over & over, I can turn the heater off & l… read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
It doesn't seem like my newly installed Aprilaire humidifier
It doesn't seem like my newly installed Aprilaire humidifier is working. Shouldn't I hear water draining out the condensation drain? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My spa heater isn't working properly and I don't know how to
Hi my spa heater isn't working properly and I don't know how to interpret the codes … read more
David Bowden
David Bowden
Owner
466 satisfied customers
We use Flanders brand Pre Pleated 40 LPD filters for our
We use Flanders brand Pre Pleated 40 LPD filters for our AC/CH unit. It is 16x25x2 in size. We cannot find the MERV rating of this particular filter. Can you tell us? My wife's allergist urges a filte… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an Armstrong Air gas furnace which is about 7 years
I have an Armstrong Air gas furnace which is about 7 years old. Recently it hasn't been working right. The LED on the control board has been flashing 3 times showing the pressure switch is open with t… read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
I just finished installing a new ruud heater in my home and
I just finished installing a new ruud heater in my home and I'm getting a code 59 that means its sensing water and the heater won't run. Art … read more
Certified HVAC Service Technician
Certified HVAC Service Technician
Welder
Vocational, Technical or Trade School
2 satisfied customers
Having issues wiring a new Honeywell rth9585 with old
Having issues wiring a new Honeywell rth9585 with old wiring. Old thermostat is trance xt302a which used ZY1, R, G, W1, W2 and B wires. … read more
Michael Ferryman
Michael Ferryman
86 satisfied customers
Thermostat called for heat, igniter was no for about 5
Thermostat called for heat, igniter was no for about 5 seconds, then the blower kicked in and at the same time, it turned off the igniter. … read more
HvacmanSean
HvacmanSean
Owner
HVAC
228 satisfied customers
I have a Rodgers 50A55-288-05. Furnace has been working but
I have a white Rodgers 50A55-288-05. Furnace has been working but no on the control board I am getting 3 flashing lights and ignition switch does not heat up. Exhaust fan tuns on but burners and ignit… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We have a comfort star plus a/c unit and received an error
we have a comfort star plus a/c unit and received an error code of H1 on the … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our furnace fan seems to be running continuously in spite of
our furnace fan seems to be running continuously in spite of the fact that the inside temperature is as shown on the thermostat setting … read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
I have a outdoor boiler. I use the honeywell TRIAC line volt
I have a outdoor wood boiler. I use the honeywell TRIAC line volt thermostat. The one I had worked well on manual mode. If went bad today and I replaced with a new one, same as the old. The fan will t… read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
I have a 30 year old Plus 90 furnace. Recently I noticed a
I have a 30 year old Bryant Plus 90 furnace. Recently I noticed a humming noise when the blower starts up, and is gone when at full speed. In other forums (and this one), the capacitor has been identi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Will running my fan constant help heat a tri level home with
will running my fan constant help heat a tri level home with a arcoaire N8MXL furnace installed in 2015. … read more
Michael Ferryman
Michael Ferryman
86 satisfied customers
I turned my furnace off at the electrical box to replace my
I turned my furnace off at the electrical box to replace my thermostat. Ever since I turned the breaker back on I have no power to my thermostat and the furnace is blinking 6 times. Can you help? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x