HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC
This answer was rated:

Im having trouble with a brand new system . Installed new

I'm having trouble with a...
I'm having trouble with a brand new system . Installed new coil and new condenser (2 ton HEIL 410-A) last year. The line set was not replaced. This year the coil froze up with a big icicle. The filter was dirty but not extremely and that was replaced. I had a service call and they diagnosed low on freon (missing a little over a pound of freon) and that the joints were not braised and are soft soldered. I sprayed the joints and could not find a leak at the joints. The system was still working at this time but I decided to have it filled to eliminate further problems. I had someone fill it with 3/4 pd but it looked like he was having trouble with the gauges and he did not use a scale but told me he filled it with 3/4pd of freon. About 24 hours later the system is now blowing hot air. The same guy came out to check and the gauges are not making sense...reading 28 degrees...and he thinks it is freezing somewhere but last time it froze I still had cold air. Why the sudden change air temperature output. i dont know if I have a leak, moisture or if I'm talking to the wrong people. The guy that installed the condenser and coil did not evacuate the line with the tank but just let what freon was left out. We initially changed the condenser and coil (30 years old) thinking that was leaking since I had to fill it 2 times. Please help.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
8/16/2013
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,894
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

The system was never prepared correctly. You could have a leak, or you could have blockage in the freon system due to contaminates.

R410A is VERY picky about how it is set up. The system must be vacuumed 3 times...but that is after the existing lineset is flushed and cleaned thoroughly to remove traces of old oil and refrigerant. They do not mix well at all.

R410a must be vacuumed and the system totally free of air, moisture oil before releasing the refrigerant. The oil in R410a will absorb moisture instantly and be ruined.

Whether you have leaks or not...you will never be able to proceed in a corredt fashion until the unit is reclaimed, vacuumed and purged with nitrogen.

At the time it is pressurized with nitrogen is the time to leak test.

After all is confirmed tight with no leaks you can then charge with NEW R410a.

I apologize if this is not what you were planning on....but it is the right way to proceed.

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

a the time of install the guy said he checked the line with putting nitrogen in. does that still mean that its still not clean???

and why the sudden change with putting more freon in??

i really appreciate this there is just too many bad tech out there


If you reused the old lines, just pressure testing with nitrogen is insufficient.

I am at a disadvantage since I do not know what process was or was not used...but I can tell you that it is absolutely critical with R410a that the system be totally free of air, moisture, previous oil and/or refrigerant.

I have seen many techs chase their tail for years on a ac call when thet should have just reclaimed, cleaned, leak checked and recharged.

With your description you have either:

A serious leak, which should be evident with an electronic leak detector.

OR...you have blockage of the system resulting in a low suction pressure.

You see I recommend starting at the beginning to make sure no preexisting issues come back to haunt you.

You can clean, leak check and balnce charge all in one service thus eliminating all those options as supect.

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

could the new coil or condenser jeopardized already from that


Yes.

That is why compressor failures were so prevalent in R410A equipment.

They were prone to failure when the proper procedure was not followed at install. Everyone who installed R22 systems thought they could use the same protocol on installs. But the failure rate of new R410 systems was directly tied to incorrect installation procedures.

The oil used in R410 is 100 times more hygroscopic than R22 oil.

This means if exposed to air/moisture it absorbs 100 times what R22 would.

This is turn gells the oil...affects the compressor...and leads to burnout

Ask Your Own HVAC Question
Customer reply replied 4 years ago

i'll tip you @the end.


if this procedure gets done right (start from beginning evacuate etc and clean) should I I still worry about the soft soldered joints and leaking? I just found out that it is now shooting cold air again. When you say burnt out compressor does that mean complete failure or will it work again.

I mean complete failure.

I do not like soft solder joints ESPECIALLY with R410a.

The pressure of 410a is twice that of R22. An R22 unit could run 265psi on a hot day...and 410a over 500 psi. Now I am not saying you need to replace....it is just my opinion that they should not have been reused..especially with sof solder and 410 a...it is just begging for leaks.

Plus I never approved of soft solder because of flux in the system...vibration leaks etc..

My company only uses braze rod. Braze melts at 1400 degrees F compared to 400 f for solder. IF.....the system had a blockage..or was overcharged...you could be tripping off on high pressure or low pressure safety. Once recovered, it will start up again.

I recommend a new pair of eyes with proper equipment that works.
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,894
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

Since, we had the line leak tested for 24 hours with no leaks. Once reconnected with now braised joints it was again leak tested as a whole. Result--no leaks. Then system was vacuumed for 4 hours, recharged with new freon. The gauge continues to read too low on the low side. The system is working right now with cool air showing 55 degrees or less out of the vents but what is causing the low pressure readings.

Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,894
22,894 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Condenser contractor chattering is it bad? Just notice
We had very cold weather down to 10 degrees, fan not been running until today thouzght was running's. On heat strips. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat pump condenser coil are freezing up during this
my heat pump condenser coil are freezing up during this latest cold spell, can I thall them by using my aux mode … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,894 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,417 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,894 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.