Bought a 2.5 ton R22 Dry A/C Unit, I was told but can't confrim that that all New Condensors are built for R 410 or some other R factor but the way they get around the R22
sales is by sneding them dry this way it can still be used for R22.

MY Question is can someone confrim this for me or better yet give me the right information.
And last but not lest do they put oil in the system already in a dry unit other than Nitrgen.

And if they don't how would I add, put oil into the compressor? and do I evacuate the system first then add oil? Or do I do it before or after?
Thanks
Tom
Show More
Show Less
Ask Your Own HVAC Question
Answered in 43 minutes by:
8/16/2013
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,788
Experience: Furnace, A/C and heat pump specialist.
Verified

Hello.My name is XXXXX XXXXX I will do my best to help.Troubleshooting often requires meters and test equipment.Let's get started and see what we can do! The unit is a dry unit. It has a small amount of nitrogen which you will release before pulling into a vacuum and charging. The compressor is already charged with oil.You will lose none of the oil in process of releasing the small amount of nitrogen. You will weld the unit in, release the nitrogen , pull a vacuum and then weigh in virgin R22 as per chart in unit.

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Thanks I was not sure if the unit had a oil in it since they said dry charge.


I understand what you said about brazing first then releasing the charge and pulling a vaccum.


 


But their is two things I'm not to sure about. one Don't I have to take out the sharder valve seats from the compressor first before I braze or I can damage them? Second since I need to put in a new orfice size in my evaporator .71 because I have a 2.5 ton unit and a 3 ton A- Coil, is there going to be a problem once I release the nitrogen out of the system? I have to open up the old system to put in the new ofrice and install a new liquid line dryer. I'm concerned about damage to the high side and low side valves on the condensor. Or do I just leave the nitrogen in the compressor braze everything and then release and vacuum.


If you know of any other way to do this with the right tools and equipment please let me know.


Such as a core removal tool etc, etc.


 


Another question if I didn't have to add these extra componets, do hvac techs add nitrogen to the system then braze to prevent flaking inside and possible damage to the system.


 


Please answer my question in the order I presented them to you so that I may understand.


I have a very strong electrical back ground but


only a limted certification in hvac up to 2 ton units that I worked on and only when the need arises.


Thank You


Tom


 

1. You will first recover any refrigerant in old system if it still has freon in it.
2.You will connect gauges to new unit,open valves on new unit, release nitrogen to the atmosphere.
3. Disconnect gauges and remove valve stems with a core remover.
4.Go ahead and replace orifice in coil at this time while system is open.
5.Weld in new unit and filter drier.
6.Re install the valve stems.
7.Pull system into vacuum
8.Add refrigerant.
As for the flaking. most manufactures recommend running nitrogen through system while welding (About 3 to 5 psig. Personally I usually just weld, then before replacing valves, purge good with nitrogen .
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,788
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

Thanks I forgot to mention that I did recover the


R22 in a recovery unit and pulled a vaccum to about 10 Hg,.. since I did that I will follow the above procedure you gave me.


You have answered all my questions and I feel confident I can continue with what I started and finnish.


Thank You


Tom


Ps. Once I add xtra $$ to my account I will add it to yours as I know you only get a portion of this fee for your services..


 

Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,788
8,788 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I need an evaporator motor for a mini split unit. Sn
I need an evaporator motor for a mini split unit. Sn 50120031-7056 What is the best way to get this? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
385 satisfied customers
I have a Gladiator Freezerator and the evaporator fan won
I have a Gladiator Freezerator and the evaporator fan won sorry won't turn off could it be the control board … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator has 3/4 suction and the condenser has a 7/8 I'm going about 20 foot which size do I use for the copper tube… read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
41 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
airheatman
airheatman
HVAC Technician
8,788 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit,
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit, Model MS-A12WA). That recently started leaking a pretty significant amount of water. The water must be building up inside the unit and then at s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Fault code 26 and 59 at same time. Evaporator frozen
Fault code 26 and 59 at same time. Evaporator frozen condensation drain was blocked now open .blower mother will not run when set to fan only… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Evaporator water flow too low alarm keeps happening.
Evaporator water flow too low alarm keeps happening. Recently cleaned coils now this. The pumps are running fine. The pressures are good on the approach. The water strainer is clean. What is this a ca… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Our evaporative cooler has started leaking apparently so our
Hi there; Our evaporative cooler has started leaking apparently so our A/C is not working. They did a leak test and said that it had to be replaced because that's where the freon was leaking. We have … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a gibson C5BA-T42C- evaporator coil. Had a new
I have a gibson C5BA-T42C- B evaporator coil. Had a new condenser put in. they didn't change the coil. Said it would be ok. They used r410a freon. Case on this coil say r22. Is this coil going to work… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Sanyo CH1822 KEEPS ICING UP AND THE EVAPORATOR UNIT SHUTS
My Sanyo CH1822 KEEPS ICING UP AND THE EVAPORATOR UNIT SHUTS OFF BUT COMPRESSOR KEEPS RUNNING … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have questions about evaporative coolers. Just purchased
i would like to know about putting more air thru my Aerocool cooler by .putting a larger motor. … read more
Michael Ferryman
Michael Ferryman
87 satisfied customers
I have a furnace with an evaporator pump that i had to
I have a furnace with an evaporator pump that i had to repace all the relays and also the thermostat. After all is done it worked great for the winter except in order for it to work i had to put the t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x