I an Hvac system with low performance. Suction pressure is…

I an Hvac system with...

I an Hvac system with low performance. Suction pressure is 10 psi and 125 on the hi side. the suction line is iced over from the unit to the a-coil and the a-coil itself. please advise

Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
7/20/2013
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,994
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,
You need to thaw the coil and then check pressures, but it sounds as though you are very undercharged.

Do you have refrigerant?

Ask Your Own HVAC Question
Customer reply replied 4 years ago


Thawing as we speak and I can get refrigerant on Monday. I have no idea how to measure a proper charge or how much oil to add if any. had a service out here two days ago and they said they added some and didn't want to add more because the pressures were to high, when I checked they seemed low.

Keep in mind there formulas for exact charging by superheat and/or subcooling but this is a tough venue to teach that.

The basic pressures for R22 on a 90 degree day...265 head and 75-80 suction depending on indoor temp.

The problem is a cold/frozen coil gives low reading because of ice, but with only 125 head pressure you are very low. There must be a significant leak needing repair.

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,994
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,994
22,994 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a new installation of a heil heat pump heat pump
I have a new installation of a heil heat pump heat pump model # NXH536000A air handler model # FEM4X3600A aux. heater model # EHK15AKB thermostat Honeywell RTH 2300/RTH221 SERIES when attempting to st… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
This question is for Phil only please *** It's getting ready
This question is for Phil only please ***It's getting ready to warm up here in Virginia. It is supposed to be hitting 80 degrees today. You said previously you wanted the temperature in the house to b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I installed a walk in cooler,compressor wont kick off on low
I installed a walk in cooler,compressor wont kick off on low pressure cut out,pulls down to 0 set to cut out at 10psi? … read more
ApplianceTech
ApplianceTech
President
Associate Degree
1,734 satisfied customers
Subject: heat pump system subcooling requirements for a
subject: heat pump system subcooling requirements for a downflow air handler.I have Rheem 6 ton variable speed split heat pump system. My air handler is installed in downflow position. Air handler is … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have 78 low side 231 high side r22 is this due to over
i have 78 low side 231 high side r22 is this due to over charge? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Billy, I have had the Fedders (remember them) 15K Split HP
Hi Billy, I have had the Fedders (remember them) 15K Split HP for a few years. Last year I had only an 8F inside temp spred so I put a little R410a in to match the gauge outside temp. Inside temperatu… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Nor norlake walk-in cooler / freezer and the
Hello! I have a Nor norlake walk-in cooler / freezer and the freezer is currently reading 22 deg. And doesn't seem to be kicking on to cool down It's usually at or below zero … read more
ApplianceTech
ApplianceTech
President
Associate Degree
1,734 satisfied customers
I am an HVAC contractor in Southern DE. I have a performance
I am an HVAC contractor in Southern DE. I have a performance issue with a York system that another contractor installed and after going through a few things I believe they mismatched the outside and i… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a rheem unit. Cannot get supply duct temp below 62
I have a rheem unit. Cannot get supply duct temp below 62 degrees 410-ref? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have 50HJ066 acutrol metering device changed refrigerant to
Have 50HJ066 acutrol metering device changed refrigerant to 407c unit takes 10 lbs on label but had to charge 16 lbs but metering device freezing … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having trouble getting more that 10 degrees of cooling between the return and the vent. I've adjusted the charge to the spec in the manual for a pi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
If the reversing valve has a internal short like you said is
if the reversing valve has a internal short like you said is that why my suction psi is ;low… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Three ton goodman spiit pressures are great everything
three ton goodman spiit pressures are great everything runing but not cooling unit is 7 yrs old … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Is the head pressure & discharge pressure same thing? And
Is the head pressure & discharge pressure same thing ? And what about back pressure & suction pressure !… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a reem 2.5 ton unit. The head pressure is 300 PSI. It
I have a reem 2.5 ton unit. The head pressure is 300 PSI. It is now cooling fine but the head pressure seems too high… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm an HVAC Tech in Tennessee and was replacing a scroll
I'm an HVAC Tech in Tennessee and was replacing a scroll compressor in a 1.5 Ton Rheem Heat Pump.After brazing up my compressor and filter dryer, I performed a leak check.After which I pulled a vacuum… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.