I an Hvac system with low performance. Suction pressure is…

I an Hvac system with...

I an Hvac system with low performance. Suction pressure is 10 psi and 125 on the hi side. the suction line is iced over from the unit to the a-coil and the a-coil itself. please advise

Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
7/20/2013
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,122
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,
You need to thaw the coil and then check pressures, but it sounds as though you are very undercharged.

Do you have refrigerant?

Ask Your Own HVAC Question
Customer reply replied 5 years ago


Thawing as we speak and I can get refrigerant on Monday. I have no idea how to measure a proper charge or how much oil to add if any. had a service out here two days ago and they said they added some and didn't want to add more because the pressures were to high, when I checked they seemed low.

Keep in mind there formulas for exact charging by superheat and/or subcooling but this is a tough venue to teach that.

The basic pressures for R22 on a 90 degree day...265 head and 75-80 suction depending on indoor temp.

The problem is a cold/frozen coil gives low reading because of ice, but with only 125 head pressure you are very low. There must be a significant leak needing repair.

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,122
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,122
23,122 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a three ton comfee Air Conditioner and the compressor
I have a three ton comfee Air Conditioner and the compressor and suction line is iced up the outdoor temperature is about 90 degrees Fahrenheit the evaporator seems to be ok good fan speed and clean c… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have an antique True double glass door cooler made in
Hello, I have an antique True double glass door cooler made in 1995. The spec sticker inside has been damaged so I can't read the high and low pressures. I had a local HVAC guy come over and put his g… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I JUST INSTALLED A NEW CR32K6E-PFV-875 COMPRESSOR, A NEW SUCTION
I JUST INSTALLED A NEW CR32K6E-PFV-875 COMPRESSOR, A NEW SUCTION DRYER, AND HI SIDE DRYER. I EVACUATED THE SYSTEM FOR 90 MINUTES.CHARGED THE SYSTEM, WITH FRESH R22, SUCTION LINE FROM EVAPORATOR TO CON… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Lastnight our a-coil, suction line and compressor were iced
Hello, Lastnight our a-coil, suction line and compressor were iced up. System was running but was restricted by ice. Fortunately it was cool last night so I shut system down and let it thaw. Today whe… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a walkin freezer, the box stayed at 25degree, but it
I have a walkin freezer, the box stayed at 25degree, but it need to go at least 0degree. So i checked the coils, they looked fine no dirt. Fan and compressor are fine, capacitor is in range. So i foun… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
After recovery, evac., and 14 lb R410a recharge of a heat pump
After recovery, evac., and 14 lb R410a recharge of a heat pump I need to wait several hours before turning on the system to yield normal pressure readings. Otherwise, If I start the system immediately… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Hello, I have an HVAC system that isnt cooling very well
Hello, I have an HVAC system that isn't cooling very well and I need some advice on what to do. It is a 14 year old Rheem R22 split system, scroll compressor, 10 SEER. The symptoms are: On a 90+ day t… read more
Appliance Guru
Appliance Guru
18,166 satisfied customers
why the compressor has a constant hissing sound? when i turn
why the compressor has a constant hissing sound? when i turn off the unit the hissing sound gone. this is a new install condensing unit two months ago… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Carrier model 50 gl-36 321 410a freon Low side pressure 125
Carrier model 50 gl-36 321 410a freon Low side pressure 125 psi High side pressure. 490psi Replaced the filter dryer and the piston flush with nitrogen vacumm the system Reacharge again With new freon… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Aircon unit is Trane X13 - 4 years old. 410A refrigerant.
Aircon unit is Trane X13 - 4 years old. 410A refrigerant. After frozen evap coil, changed the clogged filter, and cold air returned, but High side starts 300 psi when operating and climbs to 400 psi a… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I just installed a new compressor in a 10 ton package unit.
I just installed a new compressor in a 10 ton package unit. I charged it to specs. I am getting frost on the suction line out of the compressor. System is 410a. Suction press. at 90psi head at 350. I'… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Okay this is the problem this year it is a heat pump by Hamilton
Okay this is the problem this year it is a heat pump by Hamilton the coils are clean, suction is running 325 psi with 94 degree at the condenser and 76 degree at the evaporator, liquid is at 65 psi an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My home ac system is not cooling effectively. It is an r-22
My home ac system is not cooling effectively. It is an r-22 system and I am certified in auto ac. I installed a set of manifold gauges and my low side pressure is 50 psi but high side is only 80 to 85… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,122 satisfied customers
im having a recurrent problem with a trane xl13 ac (22 mos.
i'm having a recurrent problem with a trane xl13 ac (22 mos. old# the inside coil continues to freeze up installer pulled pressure #410a) at the compressor of 90 installer replaced run condenser in fa… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, I have a residential split system air conditioner and
Hello, I have a residential split system air conditioner and the outsie air temp is 90 degress and my indoor wet bulb is 58 degrees, i hooked up my gauges to the unit and my high side pressure is abou… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am a general contractor with hvac/electrical/furnace experience.My
I am a general contractor with hvac/electrical/furnace experience.My moms 1.5 ton Bryan split system a/c seems to overheat and shutdown.Yestarday it had 70 suction and 235 head on a 97 degree day.Thos… read more
freon
freon
Owner
High School or GED
214 satisfied customers
Installed a 13 seer compressor in a 10 seer coil and condensing
Installed a 13 seer compressor in a 10 seer coil and condensing unit, I have a 7/8 pipping low side and 3/8 on the high side. The unit is cooling but not a full force, runs for 2 to 3 hours at the tim… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,122 satisfied customers
I have a Lennox C23-41-1 HVAC and the evaporator coil keeps
I have a Lennox C23-41-1 HVAC and the evaporator coil keeps icing up. The condensate drain is un-obstructed, I can thaw the coils and the unit works until it ices up again. I am expecting to find a th… read more
The Home Smithy
The Home Smithy
Home Improvement Repair Consultant
1,890 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x