I just had a ac...

I just had a ac installed recently. The unit is a 3.5 ton air handler with a 4 ton condenser. The air handler has 22x24 return opening and my return air grill is 20x24. My contractor agreed that my return is slightly undersized but due to the tight area (no room to expand it between the trusses) he said it was not a problem because the return was drawing air silently and the static pressures were fine. He said it does hurts my efficiency slightly but not enough to actually be concerned about. I've done a Manual D calculation and I have 480 sq ins but I calculate I need 576 if I want 350 fps air velocity and that's not even adjusted for grill free area. My question is....Is he right that I shouldn't worry about it if my return is quiet (which it is) or is there something else I should be worrying about?

Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
7/19/2013
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,155
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to Just Answer!

The contractor is most likely correct, but it depends on how long the return air duct is, and what size the return air duct is, and if it has any 90 degree turns or bends in it.

Let me know about that, we can go from there. As things stand so far, you are indeed smaller than the ideal but not by enough to make a significant difference... particularly if you are in a humid climate, such as the gulf coast of the US.

by the way the return air grill and return duct velocity is figured in feet per *minute you have an apparently typographical error ... FPS (feet per *second)*s.

I am going to bed in a few minutes, if I miss your tonight, I will pick this question up again first thing in the morning.



Phil


.
Ask Your Own HVAC Question
Customer reply replied 4 years ago


Oh yeah, def a typo. fps is for bullets not air velocity lol. The return air duct is only about 8 ft long. Could you give me some insight as to why the recommended return size is so large? Is sound the only reason?

Customer reply replied 4 years ago


Sorry didn't read fully, 18" duct with no 90 turns just a long sweep and I live in South East Florida

Hello again, the 18" round duct, 8 feet long is 15% small for return air requirements of 350 CFM per ton of cooling capacity. 350 x 4 = 1400 CFM

Thats 792 feet per minute CLICK HERE FOR THE CALCULATOR

Thats 15% above the recommend maximum velocity, but with no 90 degree bends and only 8 feet long it will be passable in most cases depending on the size of the supply air ducts and the *total external static pressure of the duct system.

If the supply air ducts are all 15 to 20% undersized then the system will be restricted for net air flow..and that would make a significant difference in the systems over all performance.


But if the supply air ducts are not undersized as well, then the 18" return duct, only 8 feet long and with no 90 degree bends will be passable... not ideal at all, but passable. This is a common problem with two story houses where getting large enough spaces to run duct work is a problem.

Do your schedule D calcs on the entire system, with pressure drops figured at the registers per the specs on the particular registers used, and the supply air duct sizes and lengths, and the get the total static pressure drop... compare that to the total external static pressure capabilities of the air handler or furnace used.

If you do not exceed the total external static pressure of the air handler or furnace there will generally be no problem at all... however if you do exceed the total static pressure capabilities of the air handler or furnace by even 10%, you can suffer a loss of air flow in the 20%* range and that will definitely affect performance and leave the system more prone to icing the coil when the house is warm inside and the outside temperature is below 75F... an iced coil stops all air flow.

The issue here is the practical issue of how to fit large enough duct work into the structure given the limited space available as the contractor stated. It would be good if you find a way to run an additional return air duct at least 12 inches in diameter.

If you rate my response *positively I can hold the question open for follow up.


Phil











( It is 350 CFM per ton in Florida, very low air flow per ton, because of the very high humidity there... the humidity (steam essentially) carries tremendous heat with it, allowing for less air flow, so we can run very easily at 350 CFM per ton, as compared to 400 to 500 CFM per ton in dryer climates)
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,155
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,155
9,155 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,155 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat pump condenser coil are freezing up during this
my heat pump condenser coil are freezing up during this latest cold spell, can I thall them by using my aux mode … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My rhino e75CN/e110cn high efficiency condensing gas boiler
my rhino e75CN/e110cn high efficiency condensing gas boiler will not heat the house above 64 degrees. have set the thermostats to 78 and still will not het the house above 64. the LED display on the u… read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
I have aTrane XE 1200 AC and as of yesterday the condenser
I have aTrane XE 1200 AC and as of yesterday the condenser fan and compressor won't shut off. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gianni tankless water heater error 25-condensed trap full. 1
Gianni tankless water heater error 25-condensed trap full … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL #702H02997 THAT THE COMPRESSOR WAS RECENTLY REPLACED BUT i STILL HAVE A ISSUE WITH IT IT CRANKS BUT IT STOPS AFTER 45 SECONDS NEED HELPWITH THIS IS… read more
R G
R G
44 satisfied customers
Water is leaking from my condensation humidier (i think).
HI. water is leaking from my condensation humidier (i think). When I touch under the box it is wet. What can I do myself … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,408 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x