I have a Honeywell HZ311 on my central a\c unit, the only thing

that works is when the...
I have a Honeywell HZ311 on my central a\c unit, the only thing that works is when the thermostat is in the fan only position the fan runs. In cool mode nothing happens.
Thanks ken
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
7/10/2013
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Brian HVAC Guy :

Hi, I'm Brian. I'm here to answer your HVAC question to your complete satisfaction! I have worked on a great deal of Honeywell zoning systems but never the hz311 but I have looked up the documentation and thought I might be able to help.

Brian HVAC Guy :

What is the brand and model heating/cooling thermostat connected to the HZ311 controller?

Customer:

Hi BrianI am not sure but I will find out, this unit just stopped working last week. When the thermostat is set to cool the damper for that zone opens but the air handler or compressor wont start. hope that helps.

Brian HVAC Guy :

Yes but you say that if you put that same thermostat on "fan on" the fan comes on so that is a bit strange. If I understand the 311 correctly if any zone calls for cool that zone damper should open and the system should call for fan and cooling. Because the fan comes on that tells me the air handler is fine and the control circuit should be fine for the cooling. If you have a voltmeter that can read 24-28 volts ac and a couple of jumper wires we can probably narrow down the problem to the suspect component.

Customer:

Yes I have a voltmeter what should I jump?

Brian HVAC Guy :

Ok great. Is your heating/cooling system an air handler with heat, a furnace with a coil or a heat pump?

Brian HVAC Guy :

Well regardless of system type, with all your thermostats turned off you should check that you have 24-28 volts ac between terminals Rh/Rc and Y, W and G respectively on the terminal strip marked 'equipment'. That will tell us that the control circuit for your heating/cooling system is all intact. You can then jumper Rc/Rh to G and your air handler fan should come on. Jumping Rc/Rh to Y should bring on your compressor outside. If that all works then your equipment is fine and the problem either lay in the thermostat(s) connected to the zone terminal strips or the Zone controller itself. Let me know what you find with these tests and we can go from there.

Brian HVAC Guy :

It almost seems you may be having trouble reading my posts or having trouble with the chat format here. I think it would be best if I switch to the Q/A format where we exchange messages back and forth with a lot more reliability. It is a little slower that is all.

Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Brian HVAC Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ok we will continue our conversation here, exchanging messages one at a time. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 4 years ago
Hi Brian I'm getting the text but I am on the road right now .this unit is only a/c no heat I will jump the wires when I get home I will sent you the results probably in a couple of hours Thanks for now Ken
Ok Ken that's great. We will figure it out after a while. I'm sure we can get to the root of things. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 4 years ago
Hi Brian I'm back When I jumper the compressor nothing happened when I jumped the air handler the fan turned on
Customer reply replied 4 years ago
At the compressor I opened the cover inside it looks like the the fan speed control has a burnt spot on it. Can that be by passed? To seeks the compressor is working?
It's hard to visualise what you are talking about but it sounds like there is an issue with your condensing unit for sure. If there is a burnt spot you may not have power there and the control system may be still calling for it to run. What is the make and model of your condensing unit and I will try to get on the same page as you.
Ask Your Own HVAC Question
Ken, I have to step out for a bit but will check back later. Please let me know what the make and model of your condensing unit it and also it might be helpful later in the process if I knew what the make and model of your zone thermostats are in case there is also an issue on that side of the system. Thanks, -Brian
Ask Your Own HVAC Question
Customer reply replied 4 years ago
The compressor is a soft sound 1400T model# XXXXX
Customer reply replied 4 years ago
The thermostat is a LUX heat & cool there is no model #. Inside there is TX9000LC
Hi Ken sorry it took so long. I am not seeing anything for the make and model of the outdoor unit. Since you see a burnt spot it is certainly likely that there is a problem out there but it's hard for me to help with that beyond basic steps such as making sure you fix any burnt wires, make sure you have 24-28 volts ac on the two low voltage wires that come into the outdoor unit, making sure the compressor contactor engages with that 24 volt signal, making sure you have 240 volts to the unit available. On the thermostat side the lux you stated is a simple enough thermostat and the 311 is just looking for contact closure from R to G and R to Y so you could jump those same terminals on the thermostat connection on the 311 terminal strip for that zone (probably zone 1) just like you did on the other side on the equipment terminal strip. It seems to me that the control system is working and there is just an issue with the outdoor unit.
Ask Your Own HVAC Question
Customer reply replied 4 years ago

Ok unable to work on it tonight I will touch base with you tomorrow about the outside unit

Very good I will be here until about 3:30 EST and checking messages after that.
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Brian HVAC Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
953 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier gas furnace won't ignite. Fault code 31. It will run
Carrier gas furnace won't ignite. Fault code 31 JA: Did you double-check the thermostat? And what about the pilot light? Customer: It will run blower after 5 minutes JA: Do you plan on doing the work … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A pOLOPA TANKLESS GAS WATER HEATER AND IT KEEPS GOING
i HAVE A pOLOPA TANKLESS GAS WATER HEATER AND IT KEEPS GOING OFF WHILE running hot water and thermstat reads C8 … read more
canuck the pro
canuck the pro
251 satisfied customers
All of a sudden my gas heater stopped working. It sounds
all of a sudden my gas heater stopped working. It sounds like the fan works. I don't smell gas … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm replacing the filters in a Rheem 80 plus. I got the
Hi, I'm replacing the filters in a Rheem 80 plus. I got the filters out but there is an instructional line drawing that I can't tell if there are supposed to be 2 filters in a V, or just one leaning o… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Just bought a house, gas furnace was working fine. gas
just bought a house, gas furnace was working fine. gas company shut off gas, then came back and turned it back on after the confusion was cleared up. Since the gas has been back on, can't get the furn… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Old stat has o g y w r rc. New stat has k y2 aux/e g o/ c y
Old stat has b o g y w r rc. New stat has k y2 aux/e g o/b c y r rc. I'm trying to figure out what wire goes where. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a bo code on my Haywood heater. The gas comes on and
I have a bo code on my Haywood heater. The gas comes on and heat and steam comes thru the vents. I can't check to see if th pool water is coming out warm as I an disabled. Is this safe?… read more
David Bowden
David Bowden
Owner
471 satisfied customers
I have a Lennox Elite installed in 2007. Some "furnace guy"
I have a Lennox Elite installed in 2007. Some "furnace guy" didn't tel me that he cracked the condensate box therefore the condensation leaked down into the furnace and over my IBM electronic filters … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 80uhg in heater mode that was only blowing cold
I have a 80uhg in heater mode that was only blowing cold air. I took the cover off and looked at the burners. They would turn on for about 20 seconds and then turn off. Then go through that cycle agai… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a honeywell comfortmaker, and the blower does not
I have a honeywell comfortmaker, and the blower does not start - just a high pitched electrical type hum coming from the circuit board. Bad transformer perhaps? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gas furnace question. Electric ignition, my problem is that
electric ignition, my problem is that the furnace will light only one burner, and then go out. then it will reset and light again, then most of the time it works … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 3 year old CruisAir 16,000 btu Marine AC that is
I have a 3 year old CruisAir 16,000 btu Marine AC that is making noise when the compressor runs - … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier furnace is not turning on. Thermidistat is blank.
My carrier furnace is not turning on. Thermidistat is blank. Error codes is 33. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our furnace does not turn on. I switched the power off than
Our furnace does not turn on. I switched the power off than on and I heard it click and than it went on. When it turned off it would not start up again. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Need to spake to someone about a burnham boiler. Since nov.
The boiler will not remain lit. The pilot lights will light but the burners won't fire up. Would a cracked hear exchanger be the cause of this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I disconnected my thermostat without labelling anything.
I disconnected my thermostat without labelling anything. Need help reconnecting to our new thermostat. Heat pump/AC system.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Wanting to replace th8320u1008 thermostat with th8320wf1029.
wanting to replace th8320u1008 thermostat with th8320wf1029. Have heat pump with gas furnace back-up. Current thermostat has a nine wire configuration and can't determine where all nine go in new ther… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Furnace is acting strange, it starts cycle and burner fires,
Furnace is acting strange, it starts cycle and burner fires, but then it turns off and cycle starts again. It works most of the time, but it will do this cycling thing on and off about 5 or 6 times a … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x