First Ill start off by giving you all of the model and part

First I'll start off by...
First I'll start off by giving you all of the model and part numbers that I could find on my unit. I have a Carrier Weathermaker 8000 Variable Speed 58UHV030-16 serial # XXXXX the control board is HK42FZ010, the Airflow Selector is CESO130028-00, the outdoor unit is a Carrier 38TXA048300.
The problem is a couple days ago the blower stopped working. I had a local Carrier repair tech come look at it and he replaced the ECM on the blower motor (the thermistor had burned off). Now the blower runs, but there is almost no airflow. Now when I say that "there is almost no airflow" I mean at either the return or the ceiling vents. (The return vent is one large vent directly below the platform that the unit sets on; all of the air vents are in the ceiling.) The problem persists even if I take the air filter out of the equation (out of the unit). I have also taken the cover off of the box on top that houses the air conditioner coils and they look clean and are free of ice. (The tech that came out seemed to think the lack of airflow was a blockage here; I disagree, if the blockage was here, that would explain the lack of airflow at the ceiling vents, but not at the return.) If I turn it on the larger pipe on the outside unit will get covered in ice; the tech thought that maybe I was low on refrigerant, but that checked out OK. Also, we tried the heat and that starts its cycle then kicks off due to a thermal protect (code 33). Although I didn't check at the time, I think the coils inside were probably freezing up (when the pipe outside was freezing). My thoughts are both the problem with the AC and the heat are attributed to a lack of airflow and my conclusion is that the blower is not spinning fast enough.
For me, this narrows it down to : a bad Control Board, a bad Airflow Selector, or a bad blower motor. Personally I think it's one of the two circuit boards, although I've examined both and don't see any burn marks on them.
I am pretty handy with electronics; I have a multimeter that I could do some tests with if I knew what (or where) to test. Also, I probably could have replaced the thermistor (I can do soldering) and saved about $400.
I guess the answer that I'm looking for is "where does the problem really lie?"
I don't want to waste a lot of money randomly switching out parts or doing unnecessary work (I'm sure my bill with the Tech is already over $500).
If the problem is with any of the above mentioned parts, I can replace any of those myself.
Any help you can provide would be great.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
7/7/2013
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,893
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,

On the motor is a 16 wire plug and then a smaller plug.

If you unplug the 16 wire plug what does the motor do when powered on?

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

OK, I unplugged the 16 wire and left the smaller one plugged in; Thermidistat set to "cool" with fan "on" and the blower does nothing. (I thought I heard a relay on the board click, though.)

Thank you,

please give me the number off the ecm module.

Billy

Ask Your Own HVAC Question
And before I forget

ECM Testing Manual

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

There is a sticker that says GE 04/18/98 BF06 3TCV.

thank you,

call the tech back as it appears the module is the incorrect one. The modules must be exact to the make and model furnace, circuit board and motor. The module you have has a diffent program in it.

Have the contractor verify and show you that new module is indeed a match as far as programming

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,893
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
The correct module will be a RMOD44AE120

Shown here 58UHV module

The one you have is listed as 230v fan coil unit shown here.

Please see list of furnace units (115volt) shown as using the module HERE

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Thanks for all your help. Tim (airheatman) seemed to think that the module was correct, however I did a search (after looking at the links you provided) and I agree with you that the module is probably not the correct one.


I did numerous searches and I can't find the "BF06 3TCV" module; all I can find is "BF06 2ZVU" and "BF06 39VM" which are both 230v modules so this would lead me to believe that (even though I couldn't find it) the module the Tech installed is probably for a 230v motor as well. The 5 pin plug on my motor has the jumper from 1 to 2, which according to the ECM manual that you sent me means that my motor is 120v (page 11/12).


Again thanks for all your help, I hope I can get this all resolved tomorrow.

Please let me know if you need any follow up at all.

I apologize for delays today.

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

No problem with any delays; I've been busy doing other things as well.

Just wish I would have known about the part numbers a little sooner; I had the blower out and the module off. No big deal, they come out easy enough.

Thanks again.

 

7/10/2013

Monday I called the Tech and asked for my old ECM back. He asked if there was a problem and I said "yes, you installed the wrong ECM on my motor and it doesn't work properly." He wasn't real happy and told me that he had pulled that one off of a motor at the shop and thought it would work. I explained that these are programed specifically for certain models and this one was obviously wrong. I told him that I intended to fix it myself and his services were no longer needed.

I ordered a new thermistor (the part that burn off) from Mouser Electronics (EPCOS Inrush Current Limiter part # XXXXX; about $5.50 for the part and about $8.00 for shipping). I got the part today, got it soldered in and everything put back together. It was about 90 in here when I got the AC running and about a half hour later it's down to 85; slowly but surely cooling off. At least the blower is moving plenty of air now.

Thanks again for all your help. And for anyone else who has the ECM on their variable speed blower "go bad" : check for a burned off thermistor. If your (or someone you know) soldering skills are OK, then I'd recommend doing this (for about $15.00) before you replace the entire ECM (for about $400.00 plus a service call and/or repair charges). It's not hard to do, and so far, so good.

Thanks again.

Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,893
22,893 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Our carrier infinity says "system malfunction". The fan is
our carrier infinity says "system malfunction". The fan is working but it is not cool. I went to the attic and changed the filter but code is still there. What does this mean? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The supplemntal heat is not working in my carrier air
The supplemntal heat is not working in my carrier air handler … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace unit is blowing cold air. I tuned off the unit
My furnace unit is blowing cold air. I tuned off the unit and checked all connections and restarted unit. The pilot light turned on and the unit ignited, it only stayed on for a few minutes and then t… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,893 satisfied customers
Phil, we have a Carrier Infinity Weathermaer natgas
Phil, we have a Carrier Infinity Weathermaer natgas furnacethis week the limit switch had to reset at lest 4 ties. We replaced the limit switch,ever since then the furnace runs but the top of the plen… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a Carrier Weather Maker 8000 ts and the light on the
Have a Carrier Weather Maker 8000 ts and the light on the front panel is blinking … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,893 satisfied customers
We have a Carrier Infinity System Thermostat Model #
We have a Carrier Infinity System Thermostat Model # SYSTXCCUIZ01-A and the plastic "heat" and "zone" buttons are broken. We are looking for a new unit with this model number to replace our current un… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im changing my thermostat from a carrier to honeywell
Im changing my thermostat from a carrier to honeywell rth6580wf. The orange wire, not sure where to connect it on the honeywell … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Airheatman, Trying to source a control board for a Carrier
Hi airheatman, Trying to source a control board for a Carrier forced air furnace that a technician said was no longer available. The number is ***** obscured, looks like 3057?5 702 working with a 3012… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,893 satisfied customers
I have a Heil furnace unit. Furnace running fine but blower
I have a Heil furnace unit. Furnace running fine but blower not working. Motor makes noise but doesn't spin blades. Blades move freely when no power to unit but stiff when motor is making noise. Tried… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a carrier split system model no. 38ydb024310 &
I have a carrier split system model no. 38ydb024310 & fe4anf002. Just replaced the thermostat with the infinity touch control. Getting error message 'outdoor unit has wrong size for indoor unit. 16kbt… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on flame failure. Igniter glows,main flame comes on,goes into failure. When reset it will run for days and again have same problem. Could ther… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,893 satisfied customers
I have a fan coil blower motor that rattles something
I have a fan coil blower motor that rattles something fierce, the motor seems okay but I think the bearings are going. Where do you even get replacement ball bearings. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Ruud furnace unit shut off while I was unscrewing the
My Ruud furnace unit shut off while I was unscrewing the cover for the blower. I did not shut the system off before I started unscrewing the cover. I did hit the shut off switch after the unit shut do… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Phil, I have one of these: - Firstco Ceiling Fan Coil for a
Hi Phil, I have one of these: https://www.firstco.com/Products/Multi-Family-Residential-Products/Ceiling-Fan-Coils/HX - Firstco Ceiling Fan Coil for a Bryant Heat Pump. We live in a condo. It has only… read more
Michael Ferryman
Michael Ferryman
88 satisfied customers
I have a Carrier furnace unit and I want to know what size
I have a Carrier furnace unit and I want to know what size filter to use in it. I have been using the wrong size. … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,893 satisfied customers
I have a fan coil with a 4 wire thermostat, I am trying to
I am trying to replace with 5 wire stat blue wire is not connected on either end trying to figure our where to land the wire in the fan coil … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x