Hello, I have a Lennox 13ACC-0240230-01 used for our upstairs.

In Sept. '12 the capacitor...
Hello, I have a Lennox 13ACC-0240230-01 used for our upstairs. In Sept. '12 the capacitor went

out. I never needed AC repairs before so I called a local company. They came out later that day

and replaced it with a Turbo 200 for $340. In March of this year, the 1st time we need it after

the winter, the system started to seem like it wasn't cooling as well, but nothing was said by

me. I had the same company come out mid April to start a maintenance agreement. They check the

units out, cleaned, etc. They also told me on my 13ACC-047-230-01 unit that the capacitor was

the incorrect size and suggested I replace it, which I had them do.
Two days ago I noticed at the breaker box a buzzing every 10 - 15 seconds. I traced it to one of

the AC breakers and then started investigating and found that the upstairs unit was blowing hot

but after about 5 or 10 minutes of the buzzing it would finally kick on and start blowing cold

air. I had the repair company come out, they said the capacitor was fine and that the Compressor

was going bad. They showed me that the LRA should be 56 amps but when it was trying to start it was going to 59 amps. He mentioned a Hard Start kit could work but it doesn't always work and I would be out the $400 for the Hard Start kit even if it didn't work.

They are recommending the following:
Replace Comp (Dry charged) - $3000
New Trane 1-2 Ton XR13 - $4415
New Trane 1-2 Ton XR15 - $4847


Also, on the 13ACC-0240230-01 unit, I noticed that the Turbo 200 is set to 45/5 and the actual size for that unit should be 40/5. If it has been running a capacitor at 45/5 since Sept '12 could that cause premature wear on the compressor?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 36 minutes by:
7/3/2013
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,792
Experience: Furnace, A/C and heat pump specialist.
Verified

Hello.Sorry you are having problems. My name is XXXXX XXXXX I will do my best to help.Please wait to leave rating until we are finished.The capacitor setting could have an effect. These are supposed to always be within 5% + or -. As for prices, they seem a bit high. I would get another opionion and estimate before spending that much money. As for the hard start kit, they should be willing to attempt this first and if it does not work, not charge you. This is a part that can be re used. I once had a lady call me and told me her AC guy had installed a hard start and it did not work. He removed the hard start and through it in back of his truck, still charging her for it. I am sure after he left her house he put the hard start back in his truck inventory as like I stated, these are re usable.Hope this helps. My suggestion is to get another opinion and estimate

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Hi Tim,
What do you mean by "The capacitor setting could have an effect."? That the 45/5 vs 40/5 could cause a premature wear?

Also, a buddy of mine works in HVAC a ways away from me and suggested I try a Hard Start. I just got the Supco MPR5 in today. Should I try adding it on (to the R and H)? if so, should I keep the Turbo 200 at 45/5 or change it to 40/5 first?


 


 


 


Thank you.

Yes if unit called foe 40uf on the compressor side. that must always be within 5%. So it can be as low as 38 or as high as 42.(Never lower or higher)
Place one wire from hard start on the center terminal and the other to one of the compressor terminals making up the 40uf
Ask Your Own HVAC Question
Customer reply replied 4 years ago

Thank you for your help and confirmation. With the Turbo jumped at 25 + 20 its reading 42.64uf.


I assume that's ok?


 


I kept the Turbo at that current setting and added the hard start. The compressor kicked right off!

Yes that will be close enough. Did you install the hard start?I see you did. This should hopefully fix you up/.

 

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Yes, I kept the Turbo at that current setting and added the hard start. The compressor kicked right off!


 


Thank you again Tim!

Thank You and let me know if I can assist further.
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,792
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,792
8,792 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier gas furnace won't ignite. Fault code 31. It will run
Carrier gas furnace won't ignite. Fault code 31 JA: Did you double-check the thermostat? And what about the pilot light? Customer: It will run blower after 5 minutes JA: Do you plan on doing the work … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A pOLOPA TANKLESS GAS WATER HEATER AND IT KEEPS GOING
i HAVE A pOLOPA TANKLESS GAS WATER HEATER AND IT KEEPS GOING OFF WHILE running hot water and thermstat reads C8 … read more
canuck the pro
canuck the pro
251 satisfied customers
I'm replacing the filters in a Rheem 80 plus. I got the
Hi, I'm replacing the filters in a Rheem 80 plus. I got the filters out but there is an instructional line drawing that I can't tell if there are supposed to be 2 filters in a V, or just one leaning o… read more
airheatman
airheatman
HVAC Technician
8,792 satisfied customers
All of a sudden my gas heater stopped working. It sounds
all of a sudden my gas heater stopped working. It sounds like the fan works. I don't smell gas … read more
airheatman
airheatman
HVAC Technician
8,792 satisfied customers
Just bought a house, gas furnace was working fine. gas
just bought a house, gas furnace was working fine. gas company shut off gas, then came back and turned it back on after the confusion was cleared up. Since the gas has been back on, can't get the furn… read more
airheatman
airheatman
HVAC Technician
8,792 satisfied customers
Old stat has o g y w r rc. New stat has k y2 aux/e g o/ c y
Old stat has b o g y w r rc. New stat has k y2 aux/e g o/b c y r rc. I'm trying to figure out what wire goes where. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My & thermostat doesn't seem to be controlling our furnace.
My White &Rogers thermostat doesn't seem to be controlling our furnace. It's set to 70°and it's currently 79°. I have arrowed down and pressed run and it keeps getting hotter. I just turned the system… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a Carrier Infinity 96 gas furnace blowing cold air
I have a Carrier Infinity 96 gas furnace blowing cold air with yellow blinking light … read more
airheatman
airheatman
HVAC Technician
8,792 satisfied customers
I have a bo code on my Haywood heater. The gas comes on and
I have a bo code on my Haywood heater. The gas comes on and heat and steam comes thru the vents. I can't check to see if th pool water is coming out warm as I an disabled. Is this safe?… read more
David Bowden
David Bowden
Owner
471 satisfied customers
I have a Lennox Elite installed in 2007. Some "furnace guy"
I have a Lennox Elite installed in 2007. Some "furnace guy" didn't tel me that he cracked the condensate box therefore the condensation leaked down into the furnace and over my IBM electronic filters … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 80uhg in heater mode that was only blowing cold
I have a 80uhg in heater mode that was only blowing cold air. I took the cover off and looked at the burners. They would turn on for about 20 seconds and then turn off. Then go through that cycle agai… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a honeywell comfortmaker, and the blower does not
I have a honeywell comfortmaker, and the blower does not start - just a high pitched electrical type hum coming from the circuit board. Bad transformer perhaps? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gas furnace question. Electric ignition, my problem is that
electric ignition, my problem is that the furnace will light only one burner, and then go out. then it will reset and light again, then most of the time it works … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 3 year old CruisAir 16,000 btu Marine AC that is
I have a 3 year old CruisAir 16,000 btu Marine AC that is making noise when the compressor runs - … read more
airheatman
airheatman
HVAC Technician
8,792 satisfied customers
My carrier furnace is not turning on. Thermidistat is blank.
My carrier furnace is not turning on. Thermidistat is blank. Error codes is 33. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our furnace does not turn on. I switched the power off than
Our furnace does not turn on. I switched the power off than on and I heard it click and than it went on. When it turned off it would not start up again. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Need to spake to someone about a burnham boiler. Since nov.
The boiler will not remain lit. The pilot lights will light but the burners won't fire up. Would a cracked hear exchanger be the cause of this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I disconnected my thermostat without labelling anything.
I disconnected my thermostat without labelling anything. Need help reconnecting to our new thermostat. Heat pump/AC system.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x