I had R22 central air system which worked adequatly. The evaporator produced temperature in the range 35-40 degrees.

The compressor got flooded during Sandy, and was replaced with the new R407C based unit. No changes were made to evaporator. The low side pressure is around 60 psi, the high side pressure is around 180 psi. The evaporator is barely cold - 50 degrees or slightly higher. I tried evacuating refrigerant to reduce low side pressure in hopes to achieve lower temperatures in evaporator. I was gradually dropping the pressure to 55-50-45-40. The reduction of evaporator temperature was very small, and eventually it started freezing a little bit, at which point I had to stop.

Please advise what is wrong and what needs to be done.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 50 minutes by:
6/29/2013
Drcool
Drcool, HVAC Technician
Category: HVAC
Satisfied Customers: 2,086
Experience: i have been an A/C tech for the past 12 Years. working on window types, split type, and package
Verified

Drcool :

Hello, Is the metering device an expansion valve or an orifice type fixed capillary? If it is an expansion valve, have you tried adjusting the superheat?

Customer:

I am not sure. How do I check? I've heard the contractor mentioning the term orifice.

Customer:

I am pretty handy, so whatever I can do I don't mind doing...

Drcool :

Hello, If the metering device is a fixed orifice, then it is not adjustable. You can not do anything to adjust the super heat of the unit.

Drcool :

Can you enlighten me please. You mention of a contractor, I am thinking you are the contractor. SO, if you are the customer, and you are not satisfied, can you not contact your contractor and tell him you still have issues with the conversion?

Drcool :

If you are the customer, then adjusting the super heat would be expensive since you would need hvac tools to do that. It should be done by an HVAC engineer.

Customer:

Hello, I opened up the cover of the evaporator, it's definitely an orifice and a bunch of small tubes leading to the main evaporator. I am a customer, not a contractor. Why would you think I am a contractor?

Drcool :

Because of the many questions that you have placed here on the site. Some contractors are doing it here. Anyway, So, it is an orifice so we can not adjust the super heat.

Customer:

Anyway, I was adding more refrigerant little by little while observing the temperature and freezing of the evaporator. As I reached 48 psi (190 psi on high side), the evaporator stopped freezing, and most of it maintained pretty cool temperature around 40 degrees. So, based on my experience with this unit, the optimal temparature is 48 degrees. Above that, the avaporator produces little cold, while below that it starts freezing. Based on this information, would replacing an orifice with larger or smaller flow orifice be beneficial?

Drcool :

I would say, stop on the 48 psi where the temp of the inlet tubes are coldest. Would you know the temperature of the outlet tubes of the evaporator coil?

Customer:

Yes, I measured all of them, and the range is 35-45 degrees. The further from the capillars, the higher the temperature, and vice versa. I have another small practical question. While I am disconnecting the high pressure hose, a lot of the refrigerant escapes by the time I completely unscrew the cap and the valve closes. What is the right technique?

Drcool :

Was there a valve on the high pressure side? Or it is just a shreader valve like the one on tires?

Customer:

Just like on tires, and just like on the low pressure side.

Drcool :

Ok. What I can suggest is to turn the unit off , let the pressure stabilize, then hold the hose downward towards the pipe while loosening the round fitting of the hose. If you know that the whole fitting is unscrewed, let go of the hose and remove it. A small amount of liquid would come out but not sticking the valve open and letting a lot of liquid refrigerant flow out. I suggest use gloves to prevent frost bite.

Drcool :

By the way, did the contractor flush the system from its old oil?

Drcool :

When I say the outlet tubes of the evaporator, I mean the tubes that comes out of the evaporator going to the compressor. That would be the big pipe as all of the other pipes connects together and comes out as one. That would be the pipe to measure the temperature. Then we can compute the super heat.

Drcool :

Also, when you are adding refrigerant, use the liquid from the tank to add the refrigerant. R-407 gas has different blends form its liquid form and liquid is needed to charge a system.

Drcool :

Hello....are you still here?....

Drcool :

Hello, I am sorry but I have to leave. I will check again later and see if you have responded. With your question if you need a bigger orifice or a smaller, we need to find out what is the temperature of the outlet pipe first in order to find out what is the super heat so we can decide if we need a bigger orifice. Thanks

Customer:

Hello again, sorry I didn't realize you responded...

Customer:

Thank you for the recommendation on disconnecting the high pressure hose. That's what I was thinking. And yes, at least I figured to use gloves. They were all frozen.

Customer:

When I was charging, I was moving the can around to make sure the content is mixing. But I kept it vertical, so I am pretty sure it was gas and not liquid entering the system. Now I recal the contractor putting the can on its side, and now I understand why.

Customer:

I think the contractor flusshed the system. He was using some sort of compressor connected to it. I wasn't watching all the time.

Customer:

The temperature of the retrun tube at the compressor was around 50-55 degrees, but I am not sure. Would need to measure later on...

Ask Your Own HVAC Question
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,288
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
Russ here.. Trane Service Manager. Let me jump in herere. accept will go to other tech. If you google R 407a you will see it is not recomended for air conditioning applications only refrigeration. You loose efficiency. 421A is the one I recomend . You it on numerous occasions with no problems and no lose of efficiency. Russ
Ask Your Own HVAC Question
Customer reply replied 4 years ago


Russ, thank you. Type of refrigerant was not my choice.

Your welcome. Just sounds like a bad installation. Russ
Ask Your Own HVAC Question
Hello ,

I agree with Russ, if R407 was used, you would loose efficiency since it would need a bigger evaporator to equal the cooling efficiency of R-22.

But, if you have R-407 now on the system, then you can just try to adjust what you can so that at least you can make it work as cold as the R-22 before.

So we start from the beginning. If you can recover the refrigerant, evacuate the system, replace the orifice with the next bigger opening, and slowly charge it with liquid refrigerant until the frost on the outlet of the orifice melts.

Then measure the outlet temperature of the evaporator and we would see what would be the super heat.

Or, if you can still change refrigerant, then might as well use R-421A as Russ suggested.

-
Ask Your Own HVAC Question
Customer reply replied 4 years ago


Thanks for your suggestions. Over the weekend, I found the sweet spot which corresponds to 48 psi. I followed the same logic you mentioned - gradually adding refrigerant to the point the orifice and capillars stop freezing. It's been cooling for two days now, and with good results. In order to replace orifice, I would neet to call the contractor who will charge me for all the work and for an additional refrigerant to recharge the system. I will see if I can get away with how it performs now. Thanks again.

Hello,

That is nice to hear.

I just hope it would already work that way so you would no longer spend some more on the repair.

Thank you for using this service.

-
Drcool
Drcool, HVAC Technician
Category: HVAC
Satisfied Customers: 2,086
Experience: i have been an A/C tech for the past 12 Years. working on window types, split type, and package
Verified
Drcool and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Drcool Your Own Question
Drcool
Drcool
Drcool, HVAC Technician
Category: HVAC
Satisfied Customers: 2,086
2,086 Satisfied Customers
Experience: i have been an A/C tech for the past 12 Years. working on window types, split type, and package

Drcool is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I need an evaporator motor for a mini split unit. Sn
I need an evaporator motor for a mini split unit. Sn 50120031-7056 What is the best way to get this? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
383 satisfied customers
I have a Gladiator Freezerator and the evaporator fan won
I have a Gladiator Freezerator and the evaporator fan won sorry won't turn off could it be the control board … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator has 3/4 suction and the condenser has a 7/8 I'm going about 20 foot which size do I use for the copper tube… read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
41 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit,
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit, Model MS-A12WA). That recently started leaking a pretty significant amount of water. The water must be building up inside the unit and then at s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Fault code 26 and 59 at same time. Evaporator frozen
Fault code 26 and 59 at same time. Evaporator frozen condensation drain was blocked now open .blower mother will not run when set to fan only… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Evaporator water flow too low alarm keeps happening.
Evaporator water flow too low alarm keeps happening. Recently cleaned coils now this. The pumps are running fine. The pressures are good on the approach. The water strainer is clean. What is this a ca… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Our evaporative cooler has started leaking apparently so our
Hi there; Our evaporative cooler has started leaking apparently so our A/C is not working. They did a leak test and said that it had to be replaced because that's where the freon was leaking. We have … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,288 satisfied customers
I have a gibson C5BA-T42C- evaporator coil. Had a new
I have a gibson C5BA-T42C- B evaporator coil. Had a new condenser put in. they didn't change the coil. Said it would be ok. They used r410a freon. Case on this coil say r22. Is this coil going to work… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Sanyo CH1822 KEEPS ICING UP AND THE EVAPORATOR UNIT SHUTS
My Sanyo CH1822 KEEPS ICING UP AND THE EVAPORATOR UNIT SHUTS OFF BUT COMPRESSOR KEEPS RUNNING … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have questions about evaporative coolers. Just purchased
i would like to know about putting more air thru my Aerocool cooler by .putting a larger motor. … read more
Michael Ferryman
Michael Ferryman
87 satisfied customers
I have a furnace with an evaporator pump that i had to
I have a furnace with an evaporator pump that i had to repace all the relays and also the thermostat. After all is done it worked great for the winter except in order for it to work i had to put the t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x