I have a trane xv80 hvac, heater works geat but the ac only…

I have a trane xv80...
I have a trane xv80 hvac, heater works geat but the ac only blows warm air, any ideas there is not outside unit to this one
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
6/27/2013
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 973
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Brian HVAC Guy :

Hi, I'm Brian. I'm here to answer your HVAC question to your complete satisfaction! Are you receiving my chat message today?

Customer:

yes

Brian HVAC Guy :

I am a bit confused by your statement that "there is no outside unit to this one" Does your furnace have an air conditioning coil attached to it?

Customer:

not sure, its sealed up tight, cant find an outside unit, but our thermostat has cool and heat settings,

Brian HVAC Guy :

In addition to your XV80 furnace there would have to be an ac evaporator coil accessory attached to the furnace and an interconnecting outdoor ac condensing unit in order for you to have air conditioning. A thermostat can be used for heating only even if it has setting for air conditioning.

Customer:

it has two thermostasts one up stairs and one down, the one down stairs blows a little cold air, the upper just warm air,

Brian HVAC Guy :

So you only have one outside unit (ac condenser)?

Customer:

no i cant find one outside,

Brian HVAC Guy :

I am assuming this is a new residence for you, is that correct?

Brian HVAC Guy :

a/c condensers can also be located on the roof as well. Is this a single family home or a condo or townhouse?

Customer:

yea, we are renting its a single family home,

Customer:

so it can be on the roof?

Brian HVAC Guy :

Ok, well if you can locate your furnaces you can determine if you have a/c on them by seeing if the furnace(s) have a separate sheet metal casing with copper and pvc lines attached to it. That would indicate that the systems should have a matching unit outside somewhere for air conditioning. You could also look in the breaker panel for breakers labeled a/c unit or such. If the roof on the home is a flat roof it is possible the a/c units are up there if they exist otherwise they should be on the ground somewhere on the side of the home.

Customer:

well its not on the roof, could it be a heater and ac in one unit? or does it need a seperate condenser to have ac, im begining to think we dont have ac on this one,

Brian HVAC Guy :

With that model of furnace it would need a separate condenser. There is no type of package unit (all in one a/c) that would also attach to the furnace. In order to have a/c there must be an outside unit of some sort to get rid of the heat removed from the home. It does appear that your furnaces may indeed be heating only even though the thermostats are heating/cooling thermostats.

Customer:

ok, that solves that problem, they told us it had ac when we moved in, and being winter time you dont really want to turn it on, lol thanks for your help.

Brian HVAC Guy :

You are welcome. I think I would call the homeowner back and see if they can give more info as to what they are referring to as a/c. Good luck!

Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 973
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Brian HVAC Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 973
973 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

973 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I need the BTU rating for a Heatcraft Evaporator Model
I need the BTU rating for a Heatcraft Evaporator Model ADT56AWGJ … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE ERROR CODE I AM GETTING SAYS "EE" =compressor relay contacts welded … read more
Bill
Bill
Service Mgr
79 satisfied customers
The condensate pump on my xe90 is cycling on and off. 1st
the condensate pump on my xe90 is cycling on and off … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a old frigiking tappan air conditioning Condenser
I have a old frigiking tappan air conditioning Condenser unit but no model number, I have a compressor number Aw108ft-014-a4. What is the tonnage?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Today, evaporator coil froze over and i heard the outside
Today, evaporator coil froze over and i heard the outside condensor area making a louder noise. i shut the ac off when noticing this and the coil melted and the fan blows air now. i looked at the evap… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,676 satisfied customers
Condenser fan going counterclockwise. Just notice it. put a
just notice it. put a new motor in it , but has differ color wiring … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HVAC question I have a Carrier condenser unit that was
HVAC question I have a Carrier condenser unit that was running this morning when the heat was on in the house. The thermostat was set for heat? Model number 38TGO30300. I through the outside breaker b… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Looking to buy replac ement condenser to model nac036akc3
Looking to buy replac ement condenser to model nac036akc3 serial e040516483 … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
How much does an evaporator coil cost for Ruud Model
how much does an evaporator coil cost for Ruud Model UBHA-17J11SFGA cost? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I replaced a jazz bored today along with evaporator fan
I replaced a jazz bored today along with evaporator fan motor and I can only get the motor running if I use the ground wire to one terminal on the motor and one of the wires that has 120 V I replaced … read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
Condenser contractor chattering is it bad? Just notice
We had very cold weather down to 10 degrees, fan not been running until today thouzght was running's. On heat strips. … read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I need an evaporator motor for a mini split unit. Sn
I need an evaporator motor for a mini split unit. Sn 50120031-7056 What is the best way to get this? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
I have a Gladiator Freezerator and the evaporator fan won
I have a Gladiator Freezerator and the evaporator fan won sorry won't turn off could it be the control board … read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator has 3/4 suction and the condenser has a 7/8 I'm going about 20 foot which size do I use for the copper tube… read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
49 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
767 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x