Hi, have a question about York Diamond 80 HVAC system

Hi, have a question about York Diamond 80 HVAC system
Ask Your Own HVAC Question
Answered in 20 minutes by:
6/22/2013
R.G.
R.G., HVAC Technician
Category: HVAC
Satisfied Customers: 319
Experience: 20 yrs. experience as HVAC technician, state certified contractor.
Verified

R G : Hi, I am R. G., sorry you're having trouble today, I will do my best to assist you in resolving you're issue.
R G : At this
R G : At this point you have original stat back in place?
Customer:

yes

R G : Okay and nothing will work?
Customer:

no

R G : Can you access your furnace?
Customer:

we have tried resetting the on-off switch to reset the circuit board on the HVAC unit

Customer:

yes, we can access it

R G : Okay at the control board where thermostat wires connect there should be a small 3 or 5 amp automotive type fuse
R G : Can you locate it and check to see if it is blown?
Customer:

ok we are lookin

R G : Okay I am looking for a manual Tory and before specific also
R G : To try
Customer:

we found it. it is blue. looks like there are 2 wires inside at the middle that aren't connected

R G : Is the fuse blown?
Customer:

yes

Customer:

is it possible to send you a picture

R G : Okay replacing fuse should get you back going
R G : Yes you can use paper clip icon to attach it here
Customer:

Full Size Image

R G : Yes it's definitely blown just replace it with same rated fuse, looks like a 3 amp
Customer:

is this something that can be bought at home depot, lowe's, or ace hardware?

Customer:

yes it is a 3 amp fuse

R G : It is an ordinary automotive fuse can get at wal mart or any parts store or could rob one from your vehicle
Customer:

the bigger question is why the fuse blew in the first place

R G : You must of had A wire shorted out somewhere when you had changed wiring causing fuse to blow
R G : Was unit working before with old stat?
Customer:

although our honeywell thermostat didn't have a C wire, the HVAC circuit board did. We followed the instructions for venstar add-a-wire, using a diode connection between the Y and G. on the circuit board, the Y blue wire was intertwined the a red power wire from the A/C unit. Both wires were coupled with the diode wire, and a single wire from the diode was screwed onto the Y terminal of the circuit board. this was the only time we got power during this new thermostat installation attempt. when we tried to turn on Heat, the unit briefly ran, and then blew a fuse

Customer:

yes, unit worked with old stat just fine, but our bedroom is on terminal vent, and it gets hot. so, we wanted a remote unit to control temp using ambient temp in bedroom. this is where all our problems have started, trying to follow so-called easy DIY installation.

Customer:

here is the video we followed:https://www.youtube.com/watch?v=R3pea5qtygo

R G : Okay replace fuse and make sure unit works with old stat if not let me know and we will troubleshoot further if so you can get a batteryowered stat that doesn't require the C wire or you can remove green from G at stat And furnace and connect to C then connect G to Y at furnace. Air and heat will work but Continous fan will not if wired like this
R G : Not familiar with the venstar add a wire system but I can look it up if you want to use it
Customer:

but, our wiring at the control board looked different. there was a single white wire from the AC line to the C terminal, and the red wire from that line was coupled with the blue wire at the Y terminal. there was a green G wire, a white W wire, and a red R wire.

R G : Yes that is correct wiring , you can unhook the green from G at stat and furnace and connect it to C at stat and to C at furnace with the white from a/c. Then take a small piece of wire and at furnace connect G to Y leaving the red and blue on Y also
R G : This will let heat and cool work but Continous fan will not
Customer:

yes. we tried that, but it was after the fuse was already blown, only we didn't know fuse was blown

Customer:

huge pain in the ass

Customer:

and we live in the South!

R G : Yes it can be frustrating
R G : Im in alabama
R G : Get fuse replaced and let me know if you need anything further.
Customer:

so, in your opinion, the fuse is the problem, and that new stat that requires C wire can be installed using the G to C method you described. we never use a continuous fan. it would obviated the need for extra wires.

Customer:

ok thanks

R G : Yes nothing will run with that fuse blown and method above is the easiest if your ok with not having the Continous fan option
Customer:

all we have is 10 amp fuses. can we use one of those for tonight?

R G : I wouldn't recommend that if you cross something up it will burn out transformer before it blows that fuse causing even bigger
R G : Problems
Customer:

ok

R G : Just by chance look inside furnace on side to see if there is a small envelope taped or glued to side some units have this with a spare fuse and literature on unit in it
Customer:

no such luck

Customer:

we will go to auto zone in the morning and get some new fuses

R G : Okay i will be here till the morning and back on to or row evening late. Just reply back if need any further assistance and I will answer as soon as I am available
R G : Thanks for your patience
Customer:

Ok, will let you know what happens

R G : If you rate answer now you can still come back to it for further information at no extra charge or you can wait until completed to rate
R G : Okay thanks, XXXXX XXXXX
R.G.
R.G., HVAC Technician
Category: HVAC
Satisfied Customers: 319
Experience: 20 yrs. experience as HVAC technician, state certified contractor.
Verified
R.G. and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

Replaced old fuse, wired thermostat and HVAC terminals to use G wire as common (instead of using the Venstar Add-A-Wire system), and voila, system works! Thanks for all your help.

Thank you. Let me know if need anything else. Good work
Ask Your Own HVAC Question
Ask R.G. Your Own Question
R.G.
R.G.
R.G., HVAC Technician
Category: HVAC
Satisfied Customers: 319
319 Satisfied Customers
Experience: 20 yrs. experience as HVAC technician, state certified contractor.

R.G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier gas furnace won't ignite. Fault code 31. It will run
Carrier gas furnace won't ignite. Fault code 31 JA: Did you double-check the thermostat? And what about the pilot light? Customer: It will run blower after 5 minutes JA: Do you plan on doing the work … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A pOLOPA TANKLESS GAS WATER HEATER AND IT KEEPS GOING
i HAVE A pOLOPA TANKLESS GAS WATER HEATER AND IT KEEPS GOING OFF WHILE running hot water and thermstat reads C8 … read more
canuck the pro
canuck the pro
251 satisfied customers
I'm replacing the filters in a Rheem 80 plus. I got the
Hi, I'm replacing the filters in a Rheem 80 plus. I got the filters out but there is an instructional line drawing that I can't tell if there are supposed to be 2 filters in a V, or just one leaning o… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
All of a sudden my gas heater stopped working. It sounds
all of a sudden my gas heater stopped working. It sounds like the fan works. I don't smell gas … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Just bought a house, gas furnace was working fine. gas
just bought a house, gas furnace was working fine. gas company shut off gas, then came back and turned it back on after the confusion was cleared up. Since the gas has been back on, can't get the furn… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Old stat has o g y w r rc. New stat has k y2 aux/e g o/ c y
Old stat has b o g y w r rc. New stat has k y2 aux/e g o/b c y r rc. I'm trying to figure out what wire goes where. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My & thermostat doesn't seem to be controlling our furnace.
My White &Rogers thermostat doesn't seem to be controlling our furnace. It's set to 70°and it's currently 79°. I have arrowed down and pressed run and it keeps getting hotter. I just turned the system… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a Carrier Infinity 96 gas furnace blowing cold air
I have a Carrier Infinity 96 gas furnace blowing cold air with yellow blinking light … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a bo code on my Haywood heater. The gas comes on and
I have a bo code on my Haywood heater. The gas comes on and heat and steam comes thru the vents. I can't check to see if th pool water is coming out warm as I an disabled. Is this safe?… read more
David Bowden
David Bowden
Owner
471 satisfied customers
I have a Lennox Elite installed in 2007. Some "furnace guy"
I have a Lennox Elite installed in 2007. Some "furnace guy" didn't tel me that he cracked the condensate box therefore the condensation leaked down into the furnace and over my IBM electronic filters … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 80uhg in heater mode that was only blowing cold
I have a 80uhg in heater mode that was only blowing cold air. I took the cover off and looked at the burners. They would turn on for about 20 seconds and then turn off. Then go through that cycle agai… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a honeywell comfortmaker, and the blower does not
I have a honeywell comfortmaker, and the blower does not start - just a high pitched electrical type hum coming from the circuit board. Bad transformer perhaps? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gas furnace question. Electric ignition, my problem is that
electric ignition, my problem is that the furnace will light only one burner, and then go out. then it will reset and light again, then most of the time it works … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 3 year old CruisAir 16,000 btu Marine AC that is
I have a 3 year old CruisAir 16,000 btu Marine AC that is making noise when the compressor runs - … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier furnace is not turning on. Thermidistat is blank.
My carrier furnace is not turning on. Thermidistat is blank. Error codes is 33. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our furnace does not turn on. I switched the power off than
Our furnace does not turn on. I switched the power off than on and I heard it click and than it went on. When it turned off it would not start up again. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Need to spake to someone about a burnham boiler. Since nov.
The boiler will not remain lit. The pilot lights will light but the burners won't fire up. Would a cracked hear exchanger be the cause of this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I disconnected my thermostat without labelling anything.
I disconnected my thermostat without labelling anything. Need help reconnecting to our new thermostat. Heat pump/AC system.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x