Trying to replace my LR1620 to the RTH7600. I have a heat…

Trying to replace my LR1620...
Trying to replace my LR1620 to the RTH7600. I have a heat pump and a furnace installed. There is 4 wires coming out of wall (R,W,Y,G) which were hooked up to the corresponding letters on the LR1620. I also have a jumper wire that goes from Y to "1" on the LR1620. The new unit does not have have the option of "1", which I'm guessing is some sort of Aux wire connecting to Y. When I just connect the 4 wires to the corresponding connections on the new unit, power up at panel, I don't get any power to the new unit at all. Need help if you are familiar. I can upload images if needed.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 hours by:
6/19/2013
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,344
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

gotoman for ac : Russ here.. Please upload images , I will be herer for one more hour. Russ
Customer:

New Unit w/ wires
Full Size Image


 

Customer:

Old Unit with Jumper still in
Full Size Image

Customer:

Front of old unit
Full Size Image

Customer:

There are the images, let me know if you need any more images of anything. This is with the new unit currently hooked up, but I still have power disabled to the A/C and Furnace until I have it hooked up correctly.

Ask Your Own HVAC Question
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,019
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi, I'm Brian. I'm here to answer your HVAC question to your complete satisfaction!

I see that your question is back on the open list and it appears Russ had to leave. If you could take a picture of the front of your old thermostat with the cover off making sure to show the numbers on it that would be helpful. It would also be helpful if you can give brand and model number(s) of the equipment you are trying to control. I will do my best to find a solution for you.

Ask Your Own HVAC Question
Customer reply replied 5 years ago

Central Air Conditioner: Goodman CKL130-1L

Furnace Model: Goodman Janitrol GPD050-3 REV B

Image of old thermostat:

 

Old unit

Thanks for the picture. I may be able to use those numbers to figure out what's going on. I'm sorry it took so long to get back to you but I was just now alerted that you responded. I will try to get back to you within a couple hours or less. Thanks, -Brian
Ask Your Own HVAC Question
Ok I have looked up your new and old thermostats and your furnace and a/c unit literature. The number you provided for the Goodman condensing unit is a cooling only unit and therefore not a heat pump which explains why you only have 4 wires at the thermostat. The way you have it connected is correct. There is either a problem with the new thermostat or possibly an issue with your system itself. With the thermostat base on the wall and the thermostat not attached you should read 24-27 volts ac from the red wire to all 3 other wires. If you don't then there is a problem with the low voltage transformer or fuse in the furnace. If you do then there may be a problem with your new thermostat. If you have voltage at the thermostat you can short the red wire to G and you should get the furnace blower to run, R to Y should turn on the a/c unit outside and R to W should start up your furnace. If those tests work, the thermostat is indeed at fault. Please message back if you have any further questions.
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,019
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Brian HVAC Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 5 years ago

It was the new unit. There was 27ish volts going to all 3 wires. I took it back and exchanged for a new unit. Pretty obvious when the new unit powered up with AA batteries. Thanks for all the help, it helped to know I was on the right track with the wiring before assuming it was the unit.

That's great I'm glad we figured it out together! Honeywell thermostats are high quality thermostats but every once in a while a bad one out of the box does happen. Good luck and thanks!
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,019
1,019 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My goodman furnace blower wont start running when the a/c
My goodman furnace blower wont start running when the a/c unit starts running outside. The blower fan runs slowly then shuts off. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,876 satisfied customers
My air furnace blower motor wont come on i replaced the
My air furnace blower motor wont come on i replaced the transformer as it was bad still nothing … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My furnace blower will not turn off. I removed the
My furnace blower will not turn off. I removed the thermostat but it continued to run. I had to run it off st the unit, is this a fan switch issue? Or could it be resolved with a new thermostat? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace blower will kick on for a minute or two then stop.
Furnace blower will kick on for a minute or two then stop. … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,344 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
HVAC, 30 year old natural gas furnace, blower starts and
HVAC, 30 year old natural gas furnace, blower starts and heater relay on circuit board immediately clicks off. Does not trip circuit breaker. Thinking bad relay or over amp load condition, maybe dead … read more
Bill
Bill
Service Mgr
105 satisfied customers
Rheem furnace blower runs on low but will not run on high
rheem furnace blower runs on low but will not run on high furnace goes off on high heat limit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,876 satisfied customers
My Rudd furnace blower vibrates the entire house. Research
My Rudd furnace blower vibrates the entire house. Research indicates a motor/fan set screw may need tightening, but I can't see one. Where is it found? Can it be adjusted without removing the motor?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My 59SC2b furnace blower running time and blow cold air
My 59SC2b furnace blower running long time and blow cold air after heating cycle. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace blower stopped suddenly. I live in about 2,000sq
My furnace blower stopped suddenly. I live in about 2,000sq feet single family home. I called an HVAC technician. They arrived and installed a new motor. However, after they left I run the furnace and… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have an older luxaire commerical furnace blower motor runs
have an older luxaire commerical furnace blower motor runs all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My furnace blower wiil not start. Hopefully. Furnace tries
my furnace blower wiil not start JA: Did you check the furnace's filters? Customer: no JA: Do you plan on doing the work yourself? Customer: hopefully JA: Anything else we should know to help you best… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My evcon furnace blower fan cycles every day at 8:20 with no
My coleman evcon furnace blower fan cycles every day at 8:20 with no demand and no exhaust fan operation. It just co es on runs for 2 minutes then shuts down, and there was no previous heat dema d … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We have a question about a furnace blower that is not
We have a question about a Bryant furnace blower that is not working. The model number is ***** We have noticed a blinking light error that has two short and four long blinks. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x