I have a Goodman AC and gas heater unit and it keeps blowing

the 3 amp fuse on...
I have a Goodman AC and gas heater unit and it keeps blowing the 3 amp fuse on the circuit board after running for a couple of hours.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
6/13/2013
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Welcome to Just Answer!.


There is an electrical short circuit in one of the heating controls or the wiring... these shorts can be very hard to locate..but it can be done if we take one step at a time.

My first guess is that as the printed circuit board with the fuse in it warms up during its operation.... it is shorting two circuits together inside the card.... and blowing the fuse.

Thats an educated guess. We can test that by using a hair drier to warm the card up very slowly and gently so that it is warm to the touch (120F or so, but not hot).

If that causes the fuse to blow sooner than it usually does, then the problem is in the card and the solution is to replace it.

If warming up the control card does not make the fuse blow faster, then the short is in another component, such as the gas valve, or a thermostat or control wire rubbing on the sheet metal and sorting out.

I will keep this question open for you as long as you keep rating my assistance positively.

Thanks!

Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

Thank you. I will give the hair dryer a shot and let you know.

Customer reply replied 4 years ago

Ok, so here is where we are a little over a week later. We have replaced the circuit board, the capacitor, and thermostat in the upstairs attic portion of the unit. When none of that worked my husband focused on the outside portion of the unit. He first replaced the contactor because it had what looked like a burned spot on it and then, when that didn't work he replaced the capacitor on that portion of the unit. When that did not work he investigated the wiring further and found the thermostat wires to be fine, but the whip that ran from the side of the house to the outside portion for power was filled with water and the wires inside had some cuts in them so he thought that perhaps that was causing the short so he replaced the whip finally last night. The unit ran fine all night last night, cooled the whole upstairs to 75 degrees, it ran this morning and then we went out this afternoon and came back around three and the 3 amp fuse was blown again and as a result the unit wasn't working. He replaced the fuse again and it ran for about 15 minutes before blowing the fuse and shutting down again. Since it is in the attic and it is extremely hot up there we waited several hours and tried to replace the fuse again and now it blows instantly. So that's where we are. Any ideas?

Hello again, before I forget let me say that each time a part is replaced there is the chance of an error... its best not to replace parts before testing and finding them bad.

None of those parts would cause an actual high voltage condition... the problem is in the voltage sensor the company uses most likely 98% chance thats the case.

The 3 amp fuse is related to the 24 volt control circuit... and would normally not cause a 'high voltage' read on the hi/low voltage sensor read out.... those are two different things.

the whip that runs from the side of the house to the unit could have been the problem judging by the water in the protective sheath.. and cuts in the wire insulation would cause the 3 amp fuse to blow... the cure for that is to buy another length of thermostat wire with the same colors of conductors and replace the thermostat wire you have...BE VERY CAREFUL TO MAKE A GOOD SKETCH OF THE WIRE CONNECTIONS...turn the power off to the unit and the furnace/ air handler inside when you replace the wire.

__________

I need more data on the other issue, the unit going off on 'high voltage'... or by that do you mean just this blow 3 amp fuse.

We can go from there. I will be in for another hour or two tonight, then back in the morning. There are no time limits here.

Thank you for the positive rating!

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago

He did replace the whip outside, and like I said it ran find after that for a good 12-13 hours straight last night and this morning. Now it is just blowing the 3 amp fuse again.

.

Ask Your Own HVAC Question

Hello again, at this point we have what is called an 'intermittent problem'.. that means it works great for hours or days... then fails..

Those can be quite difficult to trouble shoot because the system works when you test it most of the time.

 

You have replaced all of the suspect parts and wiring except the wire that runs to the thermostat on the wall.

That wire is generally stapled to the wall studs on its way to the thermostat, over time the staple can cut the wire insulation and cause a short... and blow the fuse.

Replacing that wire inside the walls is a difficult proposition..but thats what we need to look at next.

 

Tell me how far the thermostat is from the furnace... if its not too far, we may be able to pull new wire.

If its a long run inside the walls, we will have to use a megohm meter to check the resistance wire to wire after disconnecting it from the thermostat and the furnace/air handler.

any damage to the wire insulation will show up as a failed megohm test.
Most electrical appliance parts stores carry megohm meters in the $90 to $100 range.

let me know how all that goes,

Phil

Ask Your Own HVAC Question
Customer reply replied 4 years ago


Good Morning Phil,


The thermostat is approximately 15 feet from the furnace. When my husband gets home this evening he will pull the new wire for the thermostat because he said its not that big of a deal. Its just a couple of feet up the wall and then a straight shot through the attic. He is wondering if he should replace the wire that then runs to the outside portion of the unit as well. What are your thoughts on that? Do you think he should just do the thermostat to furnace wires first?


Thank you so much for all of your help so far.


Jennifer

Hello again Jennifer,

Thats one hard working husband you have there!

We need to be more specific about the wire that runs to the outside unit. Earlier you said the thermostat wire (whip) had been replaced. So now I am confused.

(There is also high voltage power wiring to the outside unit... that should not be a problem or any concern relative to blowing the 3 amp fuse)

If there is an intermittent short in the *low voltage thermostat wiring* running from the thermostat to the furnace/ air handler... that will blow the 3 amp fuse, if there is a short in the *low voltage thermostat wiring* going from the furnace/air handler to the outside unit, that will blow the 3 amp fuse.

If there is a short in any of the devices that wire directly to the PCB, printed circuit board with the 3 amp fuse in it, that will blow the 3 amp fuse.

Let me know I am the same page with you on this or not, we can go from there.

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago


Yes he is! And I apologize for the mixed up information. I am trying to be the go between because he works in the field and can't really stopping drilling to post. :-) The whip that was replaced outside was the high voltage whip that powers the outside portion of the unit. The protective casing was worn through and those wires were sitting in water. Even though the wires were within the rubber tube portion of the whip they had splits in their covering so he replaced it all together just to be on the safe side. Didn't really want wires with bare spots sitting in water. So, he has NOT replaced the thermostat wire leading to the outside portion of the unit. So do you think that would be his next step? He is very adept at this type of thing and usually can figure it all out on his own. Last year he replaced the motor and such in the downstairs unit when it went out and it has been fine ever since. This one, the actual making the repairs he is good to go, its figuring out the 'what needs to be repaired' that has him stumped.


Thank you so much again and I will give more and more feedback as we go through this. You have been very patient and helpful.


Jennifer

Hello again !

If the 3 amp fuse only blows when the system is in cooling mode, replace the *thermostat wire going from the air handler to the outside unit first....or... inspect it closely where it passes the sharp edges of the sheet metal... that is a common location for shorts.

Less likely is the thermostat wire shorted in the wall on its way to the thermostat...

Let me know how that goes,

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago


I will let you know. Thanks!

Finding intermittent shorts can take a while.

Phil
Ask Your Own HVAC Question
Customer reply replied 4 years ago


Good morning Phil,


My husband replaced the thermostat wire running to the outside unit last night and so far so good. There was one place that he found on the wire where the protective coating had been stripped (about a half inch long) that had the copper of the wiring exposed. Hoping that this is the issue. Its been running for about 8 hours now so I guess we will see what happens when it gets really hot this afternoon. Will let you know and thank you again so much for your assistance with this.


Jennifer

Good work! Stay in touch as necessary.

Phil
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I purchased a 60 x 100 insulated metal building. It had 3
I purchased a 60 x 100 insulated metal building. It had 3 1991 7.5 ton gas packs in it using lp tanks. The tanks are gone and they stole the guts out of the 1991 units. I'm building living quarters on… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Instaling fie insulation. Which way does the metal piece go
which way does the metal piece go to hold the baffles … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Dose the ac unit outsde need a foan insulation, yhermostat
yhermostat turns unit on the unit outside blow cold air … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I have a 120 year old two story Victorian, poorly insulated
I have a 120 year old two story Victorian, poorly insulated home. Recently installed a four ton system with the thermostat set at 68 degrees. Yesterday the outside temperature was 69 degrees, and my s… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I live in Bellevue WA and have a 1961 fully insulated 1550
Hello I live in Bellevue WA and have a 1961 fully insulated 1550 sq ft rambler how large a gas furnace do I need at 80% efficiency … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My question is: is it necessary to remove ALL old insulation
Hi,My question is: is it necessary to remove ALL old insulation before blowing in new insulation?What I'd like to accomplish is: 1. Improve the air quality in the house by getting rid of that dusty la… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have three rooms, all r13 insulated walls, r30 insulated
I have three rooms, all r13 insulated walls, r30 insulated ceiling with 1/2 inch drywall used across the whole room. The four rooms are 16 ft x 11 ft with a 9 ft ceiling, 15 ft x 21 ft with a 9 ft cei… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,078 satisfied customers
Even though my suction line on my split system is insulated
Even though my suction line on my split system is insulated I having a lot of condensation dripping from the seams of the insulation. My unit is 17 years old … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am looking for a low voltage thermostat for a gas furnace
I am looking for a low voltage thermostat for a gas furnace that is non-programmable, heat only, requires only two low voltage wires, and has at least a two degree temperature differential, Any sugges… read more
Webb-Guy
Webb-Guy
tech.
72 satisfied customers
Air handler insulation in my classroom. Condensation line
Air handler insulation in my classroom. Condensation line plugs and over flows into drain pan and the insulation under the drain pan gets soaked. Do you think this is mold? CO2 levels average 1600 ppm… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Phil, I have mold on my ceiling registers, in the insulation
Hi Phil, I have mold on my ceiling registers, in the insulation above the register, on the duct fin, and within the first foot of the ducting... how do I get rid of it? Spray some household mold clean… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Replacement insulation pad door of unit---can I order part
replacement insulation pad for top door of unit---can I order part for this 20 x 28 pad- insulation one side attached to gray fiber-type backing… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
We have a 1100 sq.ft. cabin that is well insulated, but it
We have a 1100 sq.ft. cabin that is well insulated, but it does get hot enough where we are in the mountains of NM that it would be nice to have a portable 110v AC unit. Please recommend one or more t… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
What is the proper insulation procedure faced insulation
What is the proper insulation procedure for foil faced insulation under radiant heat pipes like Pex. foil face up or down and touching or not touching heat pipes?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x