I have a Carrier HVAC system. Tech2000 SS. Last night it quit

cooling, I checked some obvious...
I have a Carrier HVAC system. Tech2000 SS. Last night it quit cooling, I checked some obvious things. The condenser fan and compressor dot seem to turn on. 1 of the 2 30 amp fuses going to the condenser unit was blown. I replaced both. It still does not run. I went out to check a thing or 2 after about 1/2 hour with the new fuses and the condenser fan motor is HOT. I am an Auto Tech, knowledgeable with mobile A/C systems and know how to use a voltmeter.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
6/12/2013
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,765
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,

Is the capacitor top flat and recessed or domed upward?

Billy

Ask Your Own HVAC Question
Customer reply replied 4 years ago

I cannot see a capacitor in the unit. Could it be hidden? What is the approximate size anad would it be close to or mounted on the motor? I have done no disassembly on the unit uo to this point.


 


Thanks, Russ

Remove the corner panel where wiring from house enters. 5/16s nut driver.

Look for the capacitor behind that panel

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Looks like a can of red bull with a FLAT top. And I wish the guy installing the fence had talked to the guy that installed the condenser unit.<g>

Thanks Russ.

Now you will see a contactor.


the power from house (230v) comes in one end. When tstat calls for cool this contactor closes (springloaded up and down) and 230v goes out other end.

1- see if 230v at the front end from house.
2- see if the spring loaded center is up or down when thermostat set to cool.
3- see if 230v going out the other end.

Ask Your Own HVAC Question
Customer reply replied 4 years ago

242 in and 242 out cannot feel any spring loading either way? it did hum/buzz for about 2-3 seconds when the fuses were inserted for the voltage check

Ok,

and neither the fan motor or compressor started?

we have it narrowed down now...

Ask Your Own HVAC Question
Customer reply replied 4 years ago

Nope, just a hum and no other action

Ok,

good news = power is in correct to contactor and out which proves all main power and low voltage are working.

Since neither motor or compressor starts the only common denominator is the capacitor. The capacitor is responsible for starting the fan and compressor.

Replace the capacitor with a same rated capacitor and you should be back in business.

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,765
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,765
22,765 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
77 satisfied customers
I have a Carrier 58SX gas fired condensing furnace that will
I have a Carrier 58SX gas fired condensing furnace that will not start. The pilot flame comes up upon the thermostat calling for heat but the flame is a bit lazy and it goes out after about 5-7 second… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Question for you regarding wiring a carrier infinity with a
Question for you regarding wiring a carrier infinity with a Honeywell lyric. I have a gas furnace and an AC condenser. Today the terminal with the abcd wires connected in the furnace has 2 sets of wir… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to identify thermostat wires from an old Carrier
Trying to identify thermostat wires from an old Carrier Comfort Zone to review options for upgrading the thermostat. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have carrier c48175d. changed thermostat to honeywell.
i have carrier c48175d. changed thermostat to honeywell. carrier shows green to A yellow to B white to C and red to D. … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,765 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Just bought a Nest, but it's incompatible with my Carrier
Hi Hi. Just bought a Nest, but it's incompatible with my Carrier Infinity system. what to do? Rewire? Or find a different thermostat? If so, which one? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,765 satisfied customers
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH NEEDS TO BE REPLACED. DO YOU RECOMMEMD A ONLINE PART. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Is there a battery on my carrier infinity thermostat? The
Is there a battery on my carrier infinity thermostat? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Carrier is 4 years old. My problem is the condensate
Hi my name is Dave. My Carrier is 4 years old. My problem is the condensate drain is stopped up. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Carrier condenser Model#: 38HDC060321. Relay opens after
Carrier condenser Model#: 38HDC060321. Relay opens after about 1 minute of running. I've replaced the capacitor (usually burns out about every two years) and the main fuses (1 blew, replaced both). Go… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a carrier furnace (1990') with a Heil Condenser. The
I have a carrier furnace (1990') with a Heil Condenser. The furnace blower doesn't shut off and the thermostat appears to be inoperative meaning the controls don't seem to have any effect on the syste… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Carrier Condenser Model 38CK036320 I need to know
I have a Carrier Condenser Model 38CK036320 I need to know how to connect the new type S1-DP130024 Contasctopr… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x