This answer was rated:

I have a York Diamond 80 HVAC system. I was trying to change out the t

I have a York Diamond...

I have a York Diamond 80 HVAC system. I was trying to change out the thermostat to the new WIFI Honeywell one. My old thermostat was ran off 4 wires and 2 AA batteries. Green wire to the G, Yellow Wire to the Y, White wire to the W, and Red wire to the RH with a little jumper wire going from the RH to the RC. When traced into my attic, it is hooked up with the Yellow to Y, Green to G, White to W. The red wire goes to the C (which i think is common). Then there is a separate 5 wire loom in the attic which i think runs outide to the condenser and the fan that makes the air cold. It only uses the red and yellow wire. The Yellow wire is hooked up to the Y, and the red wire is hooked up to a fat yellow wire that runs to a float which i think is a safety valve that will raise if i start overflowing. It goes from that float and connects to the R. So i have 2 yellow wires on Y, 1 White wire on W, 1 fat yellow wire on R, 1 green wire on G, and 1 red wire on C. The Honeywell thermostat needs to have a C -common. It gives a few ways to wire. I tried using the current 4 wire configuration and at the thermostat keeping a similar wiring pattern. Yellow wire to Y, White wire to W, Red wire to R (with a jumper from R to RC), and a GREEN wire to C - COMMON. Then in the attic I followed directions and kept the Yellow to Y, White to Y, Red to R, and Green to C. Then i ran a jumper line from Y to G. This would not click on my unit outside the house that creates the cold air. All i would get is my blower on with room temperature air. I tried a different option. I had a blue wire that wasn't being used in my bundle. I read that it should be used as the common. So i wired the Blue to the C, Green to G, Yellow to Y, White to W, and Red to R with a jumper between R and RH. Up in the attic I did the exact same thing. I left the yellow wire and the red (big yellow) hooked up to the red. I tried moving the Red wire to the R, and then alongside the Blue wire in the C. I can get the fan to blow but the outside unit will not click on. My thermostat will not trigger the outside unit like it should. I don't hear a click when i drop the AC temp below the room temp like i do on my old thermostat. I reinstalled my old thermostat just to make sure all my parts are working and I'm having no other issues. I am assuming that my wiring is wrong event though I've tried both ways that Honeywell says to wire it and even tried some trial and error ways of my own. I tried keeping the wiring that works with my old thermostat and then just added the Blue Wire to the C on both the attic and thermostat but it still would only engage the fan and the not allow the unit outside to kick on to get the air cold. I would appreciate any help you guys can give me. The thermostat is the Honeywell RTH6580WF

Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 hours by:
5/3/2013
Rick Mather
Rick Mather, HVAC Technician
Category: HVAC
Satisfied Customers: 3,634
Experience: 35 years experience, HVAC
Verified

Rick Mather :

This part is good "Green wire to the G, Yellow Wire to the Y, White wire to the W, and Red wire to the RH with a little jumper wire going from the RH to the RC." Now you need common wire from the transformer that is feeding power on R terminal.

Rick Mather :

Hope you did not put Red On terminal C if so check transformer secondary for blown fuse if so equipted

Rick Mather :

Please advise if you need more assistance

Ask Your Own HVAC Question
Brian
Brian, HVAC Technician
Category: HVAC
Satisfied Customers: 859
Experience: OFTEC registered oil heating engineer and plumber.
Verified
Hi my name is XXXXX XXXXX your in the capable hands of Rick and i must agree with his answer. unfortunately you have come back on our question board. I wonder if there is anything else you require. If yes please do not hesitate in replying back. If you would like to rate Rick for the quality of service he has provided then he will get renumeration for his efforts.

Of course if you are unhappy just ask and we can cancel this question for you.

Best regards

Brian
Ask Your Own HVAC Question
Customer reply replied 4 years ago

http://www.youtube.com/watch?feature=player_embedded&v=g5UXw6QhcCQ This is the video that i followed. However, because my previous thermostat had a red wire on the C terminal, i moved it to the R terminal and then put the unused blue wire on the C terminal


 


You said, "Now you need common wire from the transformer that is feeding power on R terminal." Im not sure where that is at or what exactly that means. I made the extra Blue Wire my common wire. It is current at the C terminal on my thermostat and the C terminal in my attic. Should i connect it to the R terminal instead of the C terminal in my attic? Is this what you mean? Or do i need to find an extra wire somewhere and connect it to the C terminal in the attic along with the blue wire coming from my thermostat.

As Rick has assisted you up to now i will let him finish the question. but i will say that the connections in your attic are not always what you have in your system. The common in your attic may not be connected to the HVAC system at all which will mean you have to run a cable from the attic to the common in your system.
Ask Your Own HVAC Question
as i stated you need common from transformer which will be in air handler and or furnace which should have terminal C or if it does not you will have to make connection to transformer itself
Rick Mather
Rick Mather, HVAC Technician
Category: HVAC
Satisfied Customers: 3,634
Experience: 35 years experience, HVAC
Verified
Rick Mather and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Rick Mather Your Own Question
Rick Mather
Rick Mather
Rick Mather, HVAC Technician
Category: HVAC
Satisfied Customers: 3,634
3,634 Satisfied Customers
Experience: 35 years experience, HVAC

Rick Mather is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,634 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat pump condenser coil are freezing up during this
my heat pump condenser coil are freezing up during this latest cold spell, can I thall them by using my aux mode … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My rhino e75CN/e110cn high efficiency condensing gas boiler
my rhino e75CN/e110cn high efficiency condensing gas boiler will not heat the house above 64 degrees. have set the thermostats to 78 and still will not het the house above 64. the LED display on the u… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have aTrane XE 1200 AC and as of yesterday the condenser
I have aTrane XE 1200 AC and as of yesterday the condenser fan and compressor won't shut off. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gianni tankless water heater error 25-condensed trap full. 1
Gianni tankless water heater error 25-condensed trap full … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL #702H02997 THAT THE COMPRESSOR WAS RECENTLY REPLACED BUT i STILL HAVE A ISSUE WITH IT IT CRANKS BUT IT STOPS AFTER 45 SECONDS NEED HELPWITH THIS IS… read more
R G
R G
44 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,410 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x