Frigidaire furnace keeps blowing but no heat. 1 red blink.

Panel says limit circuit open...
Frigidaire furnace keeps blowing but no heat. 1 red blink. Panel says limit circuit open or external load on W. the filter is clean. Tried the re-set button. Anything else I can try?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
2/16/2013
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,998
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,

Are you familiar with a rectangle flat plate behind the gas valve that looks like this?

Ask Your Own HVAC Question
Customer reply replied 5 years ago
Found it. What's next.
Turn power off...tap the center of the switch 4-5 times. Turn power back on and tell me code

Ask Your Own HVAC Question
Customer reply replied 5 years ago
Still 1red blink

Turn power off
Remove the 2 wires.
Hook 2 wires direct together...a small nail or paperclip work well
Do not let the metal touch the furnace cabinet.

turn power on tell me code
Ask Your Own HVAC Question
Customer reply replied 5 years ago
Fan comes on. Still 1 red blink
Thank you,

Put wires back on. follow the wires to the next switch , They will be in series and the wires will go from one switch to another. Some may even have a small reset in center.

See page 22 HERE

You will see the limits in series at the top of the schematic.

Ask Your Own HVAC Question
Customer reply replied 5 years ago
There was 2 push button resets. Tried that. Still 1 red blink.

Ok, and are your switches connected with blue wires?

Ask Your Own HVAC Question
Customer reply replied 5 years ago
Yes
Last test.

The blue wire leaves the plug at circuit board...runs through limit and aux limits and returns on other blue to the plug.

Use a sewing needle and a couple inches from the board pierce the the center of the 2 wires. This bypasses the entire safety circuit for testing and will tell us if we have a bad circuit board or something wrong in the circuit.

Can you do this now?

Ask Your Own HVAC Question
Customer reply replied 5 years ago
Tried this. Still have 1 red blink
Thank you.

This verifies a bad circuit board.

There is one very rare condition but we might as well do it to be 100%.

Remove the wires from the R and W on the circuit board where thermostat wires attach.

Use a short jumper or wire and connect R direct to W. Start unit.

Tell me if code remains

Ask Your Own HVAC Question
Customer reply replied 5 years ago
The code remains

Thank you for the assistance,

unfortunately we completly bypassed the limit circuit and the code remains which means the circuit board is not reading the return 24v.

This requires replacing the circuit board.

Part is 624631A

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,998
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,998
22,998 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a frigidaire furnace FG6RC 060C-12A that blows air,
i have a frigidaire furnace FG6RC 060C-12A that blows air, but no heat. the burners come on, but then shut off after a couple of minutes. Thermostat is good and a new filter was just installed within … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Frigidaire furnace that won't stay lit. Tubes are
I have a Frigidaire furnace that won't stay lit. Tubes are clear. It lights up and then turns off. Connected to a new net thermostat. I even tried disconnecting the thermostat and jumping it but I got… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
My Frigidaire furnace is cycling on and off, One filter,
if I can i seated the cables to the circuit board and it came on for a few seconds then turned off … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I cannot find the model Frigidaire furnace that I have
I cannot find the model Frigidaire furnace that I have online. It may be an older model .the model number is ***** I am trying to find out if it has a filter that needs to be changed. I bought this ho… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My blower motor is staying on but I got no heat, Trying to
Trying to find a reset button. It's a frigidaire furnace FG61C 080C-V8 … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
We think last nights storm causr rain to blow onto the vent
We think last nights storm causr rain to blow onto the vent for our frigidaire furnace model FG6RC 080c and blew out the pilot light. How do we reset it? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Frigidaire furnace model g6ra096-16 and the blower
I have a Frigidaire furnace model g6ra096-16 and the blower fan motor won t stop running evenwhen thermastac is off and no heat coming on whats the problem?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Frigidaire Furnace - Blower starts running when heat is
Frigidaire Furnace - Blower starts running when heat is called, but there is no flame - Green LED flashing when heat called - Green and Red solid when no heat called… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Frigidaire Furnace FG6RA. It won't run and the red
Hi, I have a Frigidaire Furnace FG6RA. It won't run and the red light is blinking 5 times. Can you tell me what is wrong? Thanks. Ed… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
I hope so. I have a frigidaire furnace and the pilot won't
I hope so. I have a frigidaire furnace and the pilot won't light. It blows air out of the exhaust and when I go outside I can smell gas but it isn't blowing any air inside the house, just out the exha… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Frigidaire furnace Nordyne pt# ***** circuit board - red
Frigidaire furnace Nordyne pt# ***** circuit board - red status light is continuously lit indicating "shorted gas valve relay" do I need to replace the board?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Frigidaire furnace keeps blowing but no heat. 1 red blink.
Frigidaire furnace keeps blowing but no heat. 1 red blink. Panel says limit circuit open or external load on W. the filter is clean. Tried the re-set button. Anything else I can try?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
I am having the same problem as described in this fg6ra 096c
I am having the same problem as described in this fg6ra 096c 12b fRIGIDAIRE FURNACE SHORT CYCLES question. Burners turn off as soon as blower starts. Ignitor heats up and burners flame back up for a f… read more
tinman
tinman
n/a
Vocational, Technical or Trade Scho
171 satisfied customers
the frigidaire furnace flashes once every 4-5 seconds. What
the frigidaire furnace flashes once every 4-5 seconds. What does this mean, how can it be fixed?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
what is a universal replacement for the high limit on a Frigidaire
what is a universal replacement for the high limit on a Frigidaire furnace model#FG6RA 060C-12A serial#FGA020401672?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
Why burners wont light on frigidaire furnace model FG6
Why burners won't light on frigidaire furnace model FG6RA-096C-12B THIS WAS AN EMERGENCY. CANCEL QUESTION AND ORDER… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a two year old Frigidaire furnace and I believe Im
I have a two year old Frigidaire furnace and I believe I'm getting a limit circuit open fault (red light blinks once). The thermostat fan is set to auto but it does seem to be always running. Could th… read more
Jason Martin
Jason Martin
Maintenance Supervisor
Vocational, Technical or Trade Scho
88 satisfied customers
My frigidaire furnace fg6ra 096c-12b works sometimes when it
My frigidaire furnace fg6ra 096c-12b works sometimes when it doesn't it goes through the steps fires but then flame turns off while the blower keeps running, there is a diffrent error code each time ?… read more
appliance Doc
appliance Doc
Appliance Technician
Bachelor's Degree
41,941 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x