control board of lennox furnace

3A fuse in control board...

3A fuse in control board of lennox 80uhg3-75a-2 keeps blowing when I connect t stat wires or jumper 'r' and 'w'...lv wires are ccurrently disconnected in control box  and no action in the furnace

Show More
Show Less
Ask Your Own HVAC Question
Answered in 16 minutes by:
11/4/2012
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
Hi, I'm Douglas and I am here to help you resolve problems with your heating and cooling equipment.

I see someone else jumped in at some point there.

Did the fuse blow as soon as you connected it, or did it have a period of time before it blew?
Ask Your Own HVAC Question
Customer reply replied 5 years ago

I was talking to you yesterday. if turn off power, then connect lv wires and turn on power, its almost instantly popping. also, as soon as jumper it pops

Ok... this is somewhat difficult to tackle. If you look on the control board there should be a large molex connector with maybe 9-12 wires on it. With the jumper you have from R-W in place, power off, new fuse and that harness unplugged from the board, when you power it up, will it blow the fuse again? (this may help us determine if the short is in the board itself or in one of the external circuits leading to the limits etc).
Ask Your Own HVAC Question
Customer reply replied 5 years ago

fuse did noot blow

Ok you said you have an old meter, does it have an ohms setting (omega sign) and if so, put it there and touch the leads of the meter together, the needle shoud swing to the other side. ( we need to know the meter works).
Ask Your Own HVAC Question
Customer reply replied 5 years ago

yes it works

great, with the furnace power OFF, do you know where the main limit is? Its usually a 1.5" x 2" fiber card with two wires going to it, mounted on the fire wall.

With your meter set to ohms, place one lead on one of the terminals of the main limit and the other to ground. no need to remove wires. It shouldnt have any continuity to ground, in other words the meter shouldnt register anything. If it does, we are closing in on the short. You can leave the molex disconnected for this test.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

definate continuity to ground on that limit

Ok, now pull the wires off the limit and check it again.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

wired off and still grouunded at that limit

Both wires off?

Ok... now, there are probably two screws that hold that in, pull the limit out and first check the hole to see if ther is any foil back insulation that may be touching the limit rods or something.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

it looks to be cut neatly and out of the way

any chance the limit was in crooked or touching the back to the metal cut out? With the wires off, touching one terminal and ground, you had continuity?
Ask Your Own HVAC Question
Customer reply replied 5 years ago

it was upside down...I turned it around and now it isn't grounded anymore

Argghhh.. go ahead and put it all back, leave the jumper in place and try it now.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

harness in or out?

in, lets try the furnace with the jumper first and if all is good, pull the jumper out and reconnect the thermostat wires
Ask Your Own HVAC Question
Customer reply replied 5 years ago

ok didn't pop the fuse...combustion blower started but then shut off and got the fast alternating led's

Ok... I have to find that manual again...
Ask Your Own HVAC Question
Customer reply replied 5 years ago

it says its either main ground improper, under voltage, or broken ignitor/ open ignitor circuit

Whats the resistance of the ignitor? Unplug it and check with your ohm meter, it cant be over like 19 ohms.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

stupid analog...looks to be sitting right around 20

Ok switch it to Volts AC and measure from the Neutral line (white wire on power line) to ground and see if it registers any voltage.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

no voltage from neutral to ground...when check this ignitor again, the needle doesn't even seem to move. maybe its pooched

could be, but its odd it read before.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

not used to aanalog...it rests at about the 20 ohm mark...don't think it actually read before

I like analog, but digital is easier. I like the ability to pick up something quick, the digitals buffer and one can miss a blip.

Anyway. Can you pick up an ignitor tomorrow?

IF nothing else, I think we took care of the fuse blowing problem. it took a while
Ask Your Own HVAC Question
Customer reply replied 5 years ago

should be able to...I think a new ignitor might be the answer...thanks so much douglas!h

Ok let me know if I can be of any additional help
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
Douglas and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Douglas Your Own Question
Douglas
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
3,089 Satisfied Customers
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE

Douglas is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I purchased a 60 x 100 insulated metal building. It had 3
I purchased a 60 x 100 insulated metal building. It had 3 1991 7.5 ton gas packs in it using lp tanks. The tanks are gone and they stole the guts out of the 1991 units. I'm building living quarters on… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Instaling fie insulation. Which way does the metal piece go
which way does the metal piece go to hold the baffles … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Dose the ac unit outsde need a foan insulation, yhermostat
yhermostat turns unit on the unit outside blow cold air … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a 120 year old two story Victorian, poorly insulated
I have a 120 year old two story Victorian, poorly insulated home. Recently installed a four ton system with the thermostat set at 68 degrees. Yesterday the outside temperature was 69 degrees, and my s… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I live in Bellevue WA and have a 1961 fully insulated 1550
Hello I live in Bellevue WA and have a 1961 fully insulated 1550 sq ft rambler how large a gas furnace do I need at 80% efficiency … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My question is: is it necessary to remove ALL old insulation
Hi,My question is: is it necessary to remove ALL old insulation before blowing in new insulation?What I'd like to accomplish is: 1. Improve the air quality in the house by getting rid of that dusty la… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have three rooms, all r13 insulated walls, r30 insulated
I have three rooms, all r13 insulated walls, r30 insulated ceiling with 1/2 inch drywall used across the whole room. The four rooms are 16 ft x 11 ft with a 9 ft ceiling, 15 ft x 21 ft with a 9 ft cei… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,078 satisfied customers
Even though my suction line on my split system is insulated
Even though my suction line on my split system is insulated I having a lot of condensation dripping from the seams of the insulation. My unit is 17 years old … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Air handler insulation in my classroom. Condensation line
Air handler insulation in my classroom. Condensation line plugs and over flows into drain pan and the insulation under the drain pan gets soaked. Do you think this is mold? CO2 levels average 1600 ppm… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Phil, I have mold on my ceiling registers, in the insulation
Hi Phil, I have mold on my ceiling registers, in the insulation above the register, on the duct fin, and within the first foot of the ducting... how do I get rid of it? Spray some household mold clean… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Replacement insulation pad door of unit---can I order part
replacement insulation pad for top door of unit---can I order part for this 20 x 28 pad- insulation one side attached to gray fiber-type backing… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
We have a 1100 sq.ft. cabin that is well insulated, but it
We have a 1100 sq.ft. cabin that is well insulated, but it does get hot enough where we are in the mountains of NM that it would be nice to have a portable 110v AC unit. Please recommend one or more t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a 32x48x14 ceiling insulated pole barn that I need to
I have a 32x48x14 ceiling insulated pole barn that I need to cool only intermittently while I'm working. Typically weekends and some evenings. I was thinking about a 24,000 btu window unit but it won'… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,078 satisfied customers
What is the proper insulation procedure faced insulation
What is the proper insulation procedure for foil faced insulation under radiant heat pipes like Pex. foil face up or down and touching or not touching heat pipes?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x